Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Which software can model a low temp VAV with PFP boxes.

asked 2016-04-19 15:25:56 -0500

edixon16's avatar

updated 2016-04-19 21:59:24 -0500

Can a low temperature VAV system be modeled explicitly in any of the energy modeling softwares? The system I am trying to model tempers the SA down to 46F at the AHU cooling coil, then a parallel fan power box (variable speed ECM running continuously when the AHU is on) mixes RA with the low temp SA to about 55F before it is delivered to the space to avoid occupant comfort problems associated with dumping cold air. During cooler months the cooling coil leaving air temp would be reset to 55F in order to reduce the amount of reheat required.

I have spoke with a Trane product support and Trace cannot model the 46F LAT from the coil with 55F SA temp to the space unless I were to add 9F of duct loss, which would negate the benefit of using a low temp VAV system. Is it possible to model this in any of the other programs such as eQuest, EnergyPlus or IES?

edit retag flag offensive close merge delete

Comments

2

I've recently modeled a VAV with PFP boxes using OpenStudio with more standard supply air temperatures. While I can't think of any issue with lowering the supply air temperature, I believe the fan on parallel PIUs need to be constant volume and not variable speed as your design suggests.

pflaumingo's avatar pflaumingo  ( 2016-04-19 17:59:19 -0500 )edit
1

That's an answer, not a comment.

__AmirRoth__'s avatar __AmirRoth__  ( 2016-04-19 20:02:18 -0500 )edit

I second @pflaumingo. If you decide to take EnergyPlus route, AirTerminal:SingleDuct:ParallelPIU:Reheat is what you'll need. But the limitation is that PIU fan should be constant speed and not variable speed.

Chandan Sharma's avatar Chandan Sharma  ( 2016-04-19 21:14:32 -0500 )edit

2 Answers

Sort by ยป oldest newest most voted
1

answered 2016-04-19 18:17:14 -0500

crduggin's avatar

That would be easy to model in the VE. The pfpb is setup as CV by default, but making them variable is a simple control change.

edit flag offensive delete link more

Comments

Why is it "the VE" rather than just "VE"? More importantly, why is it "the Ohio State University"? I can sort of see using "the VE" to disambiguate from other the-less uses of "VE" like "Value Engineering". But "The Ohio State University" is "Ohio State University"...

__AmirRoth__'s avatar __AmirRoth__  ( 2016-04-19 20:01:41 -0500 )edit

Lol, don't forget THE University of the South. I suppose it sounds better when you say what it stands for. Model in the Virtual Environment rather than model in Virtual Environment.

crduggin's avatar crduggin  ( 2016-04-19 20:23:23 -0500 )edit

Do you mean IES VE ?

BL's avatar BL  ( 2016-04-20 08:03:13 -0500 )edit

Yes, I mean IESVE. Prototype system 6 and 8 are PFPB, depending on whether you want DX or CHW. Simply change the cooling coil LAT to the required 46F and adjust the PFPB airflow control to be variable. You will have to make some adjustments to the PFPB volume to ensure you get the SAT desired though.

crduggin's avatar crduggin  ( 2016-04-20 08:30:23 -0500 )edit
1

I know I'm over a year late to this party, but - can't comment on the universities syntax, but it's THE VE, because it wouldn't be grammatically correct without the article once you spell out the acronym (...to model in THE Virtual Environment...)

bbrannon4's avatar bbrannon4  ( 2017-12-12 20:45:46 -0500 )edit
0

answered 2017-12-12 20:46:10 -0500

bbrannon4's avatar

It's also definitely possible to model in EnergyPlus.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2016-04-19 15:25:56 -0500

Seen: 566 times

Last updated: Dec 12 '17