Chiller heater performance curve

asked 2016-03-10 19:00:14 -0600

kbk78's avatar

updated 2016-03-10 19:01:32 -0600

I am evaluating the chiller heater system and working with the example file CentralChillerHeaterSystem_Cooling_Heating.idf

Perticularly, I am trying the find out the temperature dependence of performance curves. To evaluate this I created temperature independent curve as below:

Curve:Biquadratic,
ChillerHeaterHtgEIRFT_Const,   !- Name
1,                       !- Coefficient1 Constant
0,                       !- Coefficient2 x
0,                       !- Coefficient3 x**2
0,                       !- Coefficient4 y
0,                       !- Coefficient5 y**2
0,                       !- Coefficient6 x*y
4.44,                    !- Minimum Value of x
15.56,                   !- Maximum Value of x
35.0,                    !- Minimum Value of y
57.22,                   !- Maximum Value of y
,                        !- Minimum Curve Output
,                        !- Maximum Curve Output
Temperature,             !- Input Unit Type for X
Temperature,             !- Input Unit Type for Y
Dimensionless;           !- Output Unit Type

I output the "Chiller Heater EIR Temperature Modifier Multiplier Unit 1" hourly variable and anticipated the output to be a 0 or a 1 at all times. However I am getting fractional values indicating that the output of the above curve is not always 1.

Is this anticipated? I have attached the file with the modified curve.

C:\fakepath\CentralChillerHeaterSystem_Cooling_Heating_CurveTest.idf.jpg

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-03-10 21:10:48 -0600

Chandan Sharma's avatar

updated 2016-03-11 02:04:24 -0600

ChillerHeaterClgEIRFT should also be set to constant 1. Also reporting frequency should be set to detailed as hourly frequency aggregates the output value for an hour.

edit flag offensive delete link more

Comments

It is set to one In the input file. All the capacity curves are also set to one. Reporting frequency is certainly hourly.

kbk78's avatar kbk78  ( 2016-03-10 22:21:36 -0600 )edit

That seems odd. I just pulled CentralChillerHeaterSystem_Cooling_Heating.idf and set ChillerHeaterClgEIRFT and ChillerHeaterHtgEIRFT to 1 as you did above. It is giving 1 as output for Chiller Heater EIR Temperature Modifier Multiplier Unit X (X =1,2,3,4) for detailed frequency. Once it is verified that output is 1 as expected, reporting frequency can be changed back to hourly.

Chandan Sharma's avatar Chandan Sharma  ( 2016-03-11 01:58:01 -0600 )edit

reporting frequency detailed does give the anticipated results.Thanks.

kbk78's avatar kbk78  ( 2016-03-11 09:03:06 -0600 )edit