Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Heating and cooling loads for the southern hemisphere

asked 2016-03-01 03:43:39 -0500

updated 2020-01-20 13:39:28 -0500

Dear All,

I've simulated a building in EnergyPlus for the weather of Nairobi (Kenya) which is located in the southern hemisphere. Would you please tell me if north and south swap for the purposes of heating and cooling loads in EnergyPlus? Do the results for heating and cooling energies represent them correctly or I must switch them afterwards?

Thanks a lot in advance!

edit retag flag offensive close merge delete

Comments

I don't know the answer, but would be surprised if EP didn't correct for this situation. You could test this by simply choosing a northern hemisphere location that is approximately equidistant from the equator and compare the annual profiles.

MatthewSteen's avatar MatthewSteen  ( 2016-03-01 07:39:48 -0500 )edit

Thanks a lot! in fact I checked myself and was almost sure it's correct, but an expert asked me about that and I wanted to make sure, i double checked with the way you proposed! thanks again!

Pouya's avatar Pouya  ( 2016-03-01 13:48:01 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-03-01 08:15:59 -0500

There's absolutely no reason you would need to switch them afterwards. The heating and cooling loads are defined by how your building is defined in energyplus (envelope, gains, etc) and the weather file you used. If you used the correct weather file in conjunction with the correct Site:Location object you're good to go.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-03-01 03:43:39 -0500

Seen: 244 times

Last updated: Mar 01 '16