VRF Control in EnergyPlus
All;
I have a model which used Sefaira to build/create the geometry and HVAC systems. I have downloaded the EnergyPlus file and imported it to E+ v8.4. I have gotten the model to run, but I have a ton of unmet hours which I cannot figure out. The system is set up as a DOAS with VRF; all of which are currently set to autosize. I have figured out the autosizing parameters and increased those, as well as modified the schedules to have the setpoints ramp back up rather than an abrupt change - but neither of these appear to have been the issue. The autosizing appears to be sizing the coils...but not operating the coils in numerous zones. Is there an additional thermostat control / control setpoint that needs to be assigned or verified? Thank you in advance for your assistance. DA
Did you check Zone Cooling/Heating schedule setpoint schedule and setpoint /Availability Manager for DOAS airloop?
Ok. It appears I do have a DOAS Availability Manager & Assigned DOAS schedule, and the values there make sense. I also have a Zone Heating & Cooling Schedules setup. Also, for ZoneControl:Thermostat I have a control schedule of 'HVACTemplate-Always 4 assigned. I am assuming this means that the zone system is always available, even if the DOAS is 'off'?
Additionally, my Zones have a ThermostateSEtpoint:DualSetpoint assigned, with this object referencing the correct [only] Heating & Cooling schedule objects....
'HVACTemplate-Always 4 means you have dual setpoint with deadband for thermo stats. did you add Output:timebin; and see summary of temperature in each hours and each month? i
I'd bet it's a sizing problem and that your question is exactly the same as this one.
Julien, Thanks for that link, but I'd found that thread. I had assigned those controls to the VRF units, but it appear to have no impact on the unmet hours situation. Though, at this point, I'm going to assign it to all of them to see. Im quite confused... I will also try the reporting method from ngkhanh above. It may be worth noting, I attempted to assign an AvailabilityManager to the VRF units, but the input boxes remain pink in the idf editor...I assume this means its an error. But running it both with them assigned and removing them also seemed to have no impact. I could post model..?