Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How do I set up a multi-zone DOAS and a zone level FCU for a high rise residential building?

asked 9 years ago

VictoriaEagen's avatar

updated 7 years ago

How do I set up a multi-zone DOAS and a zone level FCU for a high rise residential building?

Preview: (hide)

2 Answers

Sort by » oldest newest most voted
4

answered 9 years ago

There's a BCL measure that creates a central DOAS system (1 per floor) and applies zone level 4 pipe fan coils to zones with a selected space type. The measure includes many user inputs to help construct the DOAS as needed (energy recovery? chilled water? dx? etc...).

I would suggest applying the measure to a copy of your model to see how the DOAS system and zone level FCUs are constructed. You can get an idea of the necessary components and setup, and choose to either proceed with the BCL measure version, or re-build the system to best suit your specific design or application.

The measure can be found in the OS app through the 'Components & Measures' menu > 'Apply Measures Now' > 'Find Measures on BCL' > 'HVAC' > 'Whole System > 'Four Pipe Fan Coil More Design Parameters'

Preview: (hide)
link

Comments

Thank you, I have done this already. I am just having a hard time changing from chiller/boiler to district cooling/heating. I am also having a hard time with where I put thermostat temperatures and sizing temperatures. I don't think the DOAS and FCU's are working together, I am getting way to much energy use, 0 degree setpoint temperatures and and thousands of unmet hours in cooling.

VictoriaEagen's avatar VictoriaEagen  ( 9 years ago )
2

answered 9 years ago

Adam Hilton's avatar

Use a four pipe fan coil unit as zone level equipment and then assign as many thermal zones as you want to an air loop for your outside air. There are other approaches, but I believe that is the most common for a typical DOAS system.

Preview: (hide)
link

Comments

Yeah but how do I make sure Energy Plus knows to have the DOAS be first priority and then use the FCU to heat and cool for thermostat temperature? My errors file is showing temperature setpoint is zero, it is not zero, so something is going wrong

VictoriaEagen's avatar VictoriaEagen  ( 9 years ago )

I am having the same problem. Baseboard hot water heaters work just fine, but fan coils show high fan energy consumption and thermostats are at 0. Did you ever get an answer to this?

RBallard's avatar RBallard  ( 8 years ago )

In the OS interface cooling/heating priority is set by the order they appear/are dropped in. Not quite sure what you're trying to say with 'thermostats are at 0'.

Adam Hilton's avatar Adam Hilton  ( 8 years ago )

Office building with several small spaces needing small amount of heat to avoid Unmet loads, plus outside ventilation air. I added air loop with heater to supply ventilation air at room air temperature. To meet heat load I added baseboard heater, which worked. But, to model actual design I changed heater to fan coil auto sized. Simulation gave thousands of cfm for the fan coil, with very small temperature difference from room air, and an error saying that this difference was too small, with note that at time of error thermostat set point is 0 degrees. Why the error with the FC?

RBallard's avatar RBallard  ( 8 years ago )

Because you're probably trying size the equipment to meet load with a neutral air temperature.

Adam Hilton's avatar Adam Hilton  ( 8 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 9 years ago

Seen: 865 times

Last updated: Feb 04 '16