Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Impossible to autosize UnitHeater: Autosizing of heating coil UA failed for Coil:Heating:Water

asked 2016-01-21 06:45:17 -0600

updated 2016-01-21 09:37:57 -0600

I've got a large model with offices, corridors, and stairwells. The stairwells are only semi-heated to 50°F with Unit Heaters equipped with Hot Water Coils, connected to a boiler loop that serves the rest of the building.

I cannot get the sizing to happen properly. I've isolated one stairwell zone to make debugging easier and I've tried playing on all the setpoints but to no avail.

Here is the error log:

   ** Warning ** Calculated design cooling load for zone=1-STAIR-A ZN is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ************* Beginning Plant Sizing Calculations
   ** Warning ** The design coil load is zero for Coil:Heating:Water 1-STAIR-A ZN UNIT HEATER HEATING COIL
   **   ~~~   ** The autosize value for maximum water flow rate is zero
   **   ~~~   ** To change this, input a value for UA, change the heating design day, or lower
   **   ~~~   **   the system heating design supply air temperature
   ** Severe  ** Autosizing of heating coil UA failed for Coil:Heating:Water "1-STAIR-A ZN UNIT HEATER HEATING COIL"
   **   ~~~   **   Bad starting values for UA
   **   ~~~   **   Lower UA estimate = 2.288029 W/m2-K (0.1% of Design Coil Load)
   **   ~~~   **   Upper UA estimate = 2288.029488 W/m2-K (100% of Design Coil Load)
   **   ~~~   **   Zone "1-STAIR-A ZN" coil sizing conditions (may be different than Sizing inputs):
   **   ~~~   **   Coil inlet air temperature     = 6.617 C
   **   ~~~   **   Coil inlet air humidity ratio  = 4.434E-003 kgWater/kgDryAir
   **   ~~~   **   Coil inlet air mass flow rate  = 6.611502E-002 kg/s
   **   ~~~   **   Design Coil Capacity           = 0.000 W
   **   ~~~   **   Design Coil Load               = 2288.029 W
   **   ~~~   **   Coil outlet air temperature    = 40.555 C
   **   ~~~   **   Coil outlet air humidity ratio = 8.000E-003 kgWater/kgDryAir
   **   ~~~   **   Inadequate water side capacity: in Plant Sizing for this hot water loop
   **   ~~~   **   increase design loop exit temperature and/or decrease design loop delta T
   **   ~~~   **   Plant Sizing object = HOT WATER LOOP
   **   ~~~   **   Plant design loop exit temperature = 82.000 C
   **   ~~~   **   Plant design loop delta T          = 11.111 C
   **  Fatal  ** Preceding water coil sizing errors cause program termination
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=1
   ..... Last severe error=Autosizing of heating coil UA failed for Coil:Heating:Water "1-STAIR-A ZN UNIT HEATER HEATING COIL"

Here is my isolated model (one stairwell zone and an autosized boiler):

Can someone help please?

EDIT: even after I fix what Chandan said, I can get it to run in my small one-zone model but not in my full model. Note that my hot water plant loop is rated at 180°F with a 40°F deltaT, and that's dictated by the VAV boxes that will represent almost all of my heating anyways. So changing the $\Delta T$ isn't an option

ZoneHVAC:UnitHeater,
  1-Stair-A Zn Unit Heater,               !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Node 1235,                              !- Air Inlet Node Name
  Node 1236,                              !- Air Outlet Node Name
  Fan:ConstantVolume,                     !- Supply Air Fan Object Type
  1-Stair-A Zn Unit Heater Fan,           !- Supply Air Fan Name
  Autosize,                               !- Maximum Supply Air Flow Rate {m3/s}
  Coil:Heating:Water,                     !- Heating Coil Object Type
  1-Stair-A Zn Unit Heater Heating Coil,  !- Heating Coil ...
(more)
edit retag flag offensive close merge delete

Comments

@Eric Ringold pointed me to this issue

Julien Marrec's avatar Julien Marrec  ( 2016-01-21 08:42:52 -0600 )edit

1 Answer

Sort by » oldest newest most voted
3

answered 2016-01-21 08:50:23 -0600

Chandan Sharma's avatar

"Maximum Hot Water or Steam Flow Rate {m3/s}" input field in unit heater object should have "Autosize" instead of blank. That successfully completes the simulation.

ZoneHVAC:UnitHeater,
  1-Stair-A Zn Unit Heater,               !- Name
  Always On Discrete,                     !- Availability Schedule Name
  Node 1235,                              !- Air Inlet Node Name
  Node 1236,                              !- Air Outlet Node Name
  Fan:ConstantVolume,                     !- Supply Air Fan Object Type
  1-Stair-A Zn Unit Heater Fan,           !- Supply Air Fan Name
  Autosize,                               !- Maximum Supply Air Flow Rate {m3/s}
  Coil:Heating:Water,                     !- Heating Coil Object Type
  1-Stair-A Zn Unit Heater Heating Coil,  !- Heating Coil Name
  ,                                       !- Supply Air Fan Operating Mode Schedule Name
  No,                                     !- Supply Air Fan Operation During No Heating
  autosize,                               !- Maximum Hot Water or Steam Flow Rate {m3/s}
  0,                                      !- Minimum Hot Water or Steam Flow Rate {m3/s}
  0.001;                                  !- Heating Convergence Tolerance
edit flag offensive delete link more

Comments

Yes thank you Chandan, I just figured it out like 1 minute ago. I think this is my fault/OS's, I created all the unit heaters using OpenStudio API and I just assumed that by default it would have everything on autosize. might be something for @Kyle Benne to look at?

Julien Marrec's avatar Julien Marrec  ( 2016-01-21 09:06:51 -0600 )edit

Hum I may have spoken too fast. It works on my one-zone model, but still crashes for the actual one.

Julien Marrec's avatar Julien Marrec  ( 2016-01-21 09:23:13 -0600 )edit

I've unaccepted your answer because I still can't make it work, but I'll give you back the credit don't worry!

Julien Marrec's avatar Julien Marrec  ( 2016-01-21 09:38:38 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2016-01-21 06:45:17 -0600

Seen: 1,530 times

Last updated: Jan 21 '16