Outdoor air loads
I'm using openstudio 1.10.0.
How can I model a room load regarding outdoor air infiltration? In my building I got something like 0,8 ach.
First time here? Check out the Help page!
I'm using openstudio 1.10.0.
How can I model a room load regarding outdoor air infiltration? In my building I got something like 0,8 ach.
Infiltration is typically defined from the Space Types Tab (5th from top). You'll see these on the Spaces Tab (7th from top) under the Loads subtab. These will typically be in green text to designate that the values were inherited from the Space Type definition. You can choose to redefine the values used in the Space Type Tabs.
There is no way to assign a particularly infiltration directly to a thermal zone?
Infiltration is treated as a load associated with a physical space. Thermal zones can have a 1-to-1 relationship with spaces, but that's not a requirement (e.g. a thermal zone can span multiple physical spaces).
So I should assign infiltration to a space and not to a thermal zone?
Yes. Specify the infiltration as a space type definition -> Assign the space type definition to a physical space -> Zone your building. It may seem like an extra step, but it gives you flexibility in evaluating different zoning options for your building - and there's a user script in the SketchUp Plug-In that will automatically create a 1-to-1 mapping between spaces and zones for you if you want to zone your building that way. (I don't recall if that's been converted into a standalone OpenStudio Measure or not.)