I am setting up a heat recovery chiller and want to connect the recovered heat to a campus hot water loop. Is this arrangement possible. Or is there a work around that I could use to determine the total heat rejected by the heat recovery chiller.

edit retag flag offensive close merge delete

Comments

On similar count it is possible to have a chiller heater follow the heating load and transfer the excess chilled water to the campus chilled water loop.

kbk78's avatar kbk78  ( 2015-12-17 09:58:31 -0600 )edit

2 Answers

Sort by ยป oldest newest most voted
2

answered 2015-12-17 09:30:14 -0600

Someone has asked a similar question HERE. You would need to connect chiller heat recovery stream to storage tank, then have the storage tank serve as HW supply to campus hot water loop. You will likely need to use a Fluid to Fluid HX object to have the chiller heat recovery water provide heat to the campus hot water loop. Reference the schematic below.

image description

edit flag offensive delete link more
1

answered 2015-12-17 09:21:49 -0600

Chandan Sharma's avatar

Yes, this arrangement is possible. Please take a look at HeatRecoveryElectricChiller.idf example file.