Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

How to modulate air transfer to corridor from rooms

asked 2015-12-10 05:21:42 -0600

J Monteiro's avatar

updated 2015-12-14 10:09:48 -0600

image descriptionIn my project I got various thermal zones with only supply air with an AHU. This air is transfer by door grilles to a corridor and then is extracted by a fan. How can I model this situation?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2015-12-10 07:51:46 -0600

updated 2015-12-13 05:57:37 -0600

You can model the corridor as a return plenum or you can use zonemixing. This question can help you on your way.

edit flag offensive delete link more

Comments

In my case the air is supply to a zone (room) by an AHU then is transfer to another zone (corridor) and finally is extracted by a fan with no return flow to the AirLoop. The extracted air pass by an heat recovery (the energy is transfer to the supply air). So should I use zonemixing right?

J Monteiro's avatar J Monteiro  ( 2015-12-11 09:57:07 -0600 )edit

If you want to recover heat from the air, then I would go the return plenum route. This way you can add an Air-Air heat exchanger on your air loop. If you use ZoneMixing and a Fan:ZoneExhaust, you can't recover any of that heat easily. Note: the return plenum method won't work if your corridor is conditioned by other equipment. This video shows how to set up the plenum zones.

ericringold's avatar ericringold  ( 2015-12-11 11:11:35 -0600 )edit

Ok I understand. Another thing, part of the air in the corridor go to the heat recovery, and other part is transfer to toilets, and then is extracted directly to the exterior. How can I model this situation?

J Monteiro's avatar J Monteiro  ( 2015-12-14 08:22:24 -0600 )edit

Can you post a schematic drawing of your situation ? Maybe you can simplify the case. Is there 1 zone with an air supply or are multiple zones connected to a corridor. Do you have a supply fan and an extract fan + an exhaust fan for the toilets? ...

BBel's avatar BBel  ( 2015-12-14 09:54:03 -0600 )edit

I don't know if you can add an exhaust fan to a plenum, if you can't I would still go for the mixing and add dummy (fictional) exhaust fans to maintain the balance in the supplying zones. However you will have to do the balancing of the system yourself like you did in the schematic.

BBel's avatar BBel  ( 2015-12-15 03:36:04 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2015-12-10 05:21:42 -0600

Seen: 509 times

Last updated: Dec 14 '15