Using the CEC Performance Database data for Solar PV in E+

asked 2015-10-27 11:41:33 -0600

updated 2015-10-27 12:16:43 -0600

It seems that the PhotovoltaicPerformance:EquivalentOne-Diode is very similar to the California Energy Commission Performance Model: they both are equivalent to a one-diode circuit, and 4 or 5-parameter models.

Can I use the California Energy Commission Performance Model with module Database numbers directly into E+?

edit retag flag offensive close merge delete

2 Answers

Sort by » oldest newest most voted
2

answered 2015-10-27 12:29:39 -0600

I'd like to stand corrected, but I'd tend to say you can't because the E+ is a 4P model whereas the CEC's one is a 5P model.

EnergyPlus PhotovoltaicPerformance:EquivalentOne-Diode

From the Engineering Reference Guide:

This model predicts the electrical performance of a photovoltaic (PV) array. This model is also known as the “TRNSYS PV” model.

[...]

The four-parameter equivalent circuit model was developed largely by Townsend [1989] and is detailed by Duffie and Beckman [1991]. The model was first incorporated into a component for the TRNSYS simulation package by Eckstein [1990]. The EnergyPlus module employs the Eckstein model for crystalline PV modules, using it whenever the short-circuit IV slope is set to zero or a positive value as modified by Ulleberg [2000].

Equivalent circuit in the four parameter model

Equivalent circuit in the four parameter model

CEC

The California Energy Commission (CEC) Performance Model uses the University of Wisconsin-Madison Solar Energy Laboratory's five-parameter model with a database of module parameters for modules from the database of eligible photovoltaic modules maintained by the California Energy Commission (CEC) for the California Solar Initiative.

The five-parameter model calculates a module's current and voltage under a range of solar resource conditions (represented by an I-V curve) using an equivalent electrical circuit whose electrical properties can be determined from a set of five reference parameters. These five parameters, in turn, are determined from standard reference condition data provided by either the module manufacturer or an independent testing laboratory, such as the Arizona State University Photovoltaic Testing Laboratory.

The five-parameter model is described in De Soto 2004, Improvement and Validation of a Model for Photovoltaic Array Performance, Master of Science Thesis, University of Wisconsin-Madison.

From De Soto (2004):

Equivalent circuit representing the 5-Parameter model

Equivalent circuit for the 5-Parameter model

edit flag offensive delete link more
2

answered 2015-10-27 13:26:38 -0600

Archmage's avatar

My understanding is that the implementation in EnergyPlus is actually the 5 parameter model and the engineering reference is not accurate. As I recall the original engineering reference content was just a copy of old TRNSYS type documentation which was out of date at the time.

The shunt resistence is an input. The series resistence is calculated from the other inputs here https://github.com/NREL/EnergyPlus/bl...

edit flag offensive delete link more

Comments

This is good news (and also should be a github issue for EnergyPlus...)

I guess I'll give it a shot, try to use CEC data and input that in E+ and see if it matches. I'll report back when I do

Julien Marrec's avatar Julien Marrec  ( 2015-10-27 17:16:19 -0600 )edit