Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
6

DesignSpecification:OutdoorAir not being set by OpenStudio

asked 2015-10-14 22:45:17 -0600

updated 2015-11-09 11:56:14 -0600

I have noticed in hourly reports and the HTML EnergyPlus Outdoor Air Summary Report that thermal zones were not receiving ventilation air volumes as defined in the OS:DesignSpecification:OutdoorAir objects. I exported the IDF file from my OpenStudio model and all of the 'Design Specification Outdoor Air Object Name' fields are blank when opened in the IDF editor.

It appears OpenStudio (1.9.0) does not set the 'Design Specification Outdoor Air Object Name' for the AirTerminal:SingleDuct:VAV:Reheat object. This excerpt from the E+ Input/Output reference suggests this field is required for the AirTerminal to deliver the proper amount of ventilation...

image description

I am not using demand controlled ventilation and the total airflow to zones is routinely under the volume of outdoor air defined.

How does OpenStudio implement the DesignSpec:OA to ensure the AirTerminal provides minimum ventilation at all times? Are there other approaches to consider or am I missing something here?

This question builds upon this previous question

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
12

answered 2015-10-15 12:29:44 -0600

updated 2015-10-15 13:06:40 -0600

You are correct that OpenStudio does not currently allow you to assign the zone's DesignSpecification:OutdoorAir object to the AirTerminal:SingleDuct:VAVReheat or AirTerminal:SingleDuct:VAVNoReheat terminals. Therefore, when simulations are run, the airflow for a given VAV terminal is governed by the load and bounded by the settings in the VAV terminal object itself. As you noted in the documentation, it will not control for minimum OA flow.

Traditionally, VAV systems have operated in this fashion (VAV terminals not knowing about OA). In order to ensure that each zone is properly ventilated at minimum flow, designers use the multi-zone ventilation rate procedure calculations from ASHRAE Standard 62.1 to determine the overall OA flow rate for the system. These calculations often result in a full-flow OA flow rate that is significantly higher than what you would get by simply summing the OA from all zones. You can enable this calculation method in OpenStudio by clicking on the AirLoop and changing the System Outdoor Air Method from ZoneSum to VentilationRateProcedure. Note that this calculation is sensitive to the minimum damper positions in the terminal. If you have a VAV system, you should use this method. When you do so, if you see that your system is now running at 100% OA, try to determine your critical zone and increase the minimum damper position in that zone. My rule of thumb is to start with a minimum position of 30% for zones with an OA requirement less than 0.2 cfm/ft2, and a minimum position of 70% for zones with higher OA requirements, then fine-tune damper positions as needed.

The ability for a each VAV terminal to monitor OA and adjust in real-time is called "Multiple-zone VAV System Ventilation Optimization Control," and this was not required until 90.1-2010. In order for systems to be able to do this type of control, they must have DDC control of terminals. The ability to assign a DesignSpecification:OutdoorAir to a terminal and have the terminal adjust accordingly was added to EnergyPlus enable this type of control. We are going to enable this feature in OpenStudio soon. However, depending on your particular scenario, your system may or may not actually have this type of control.

This ASHRAE article by Dennis Stanke of Trane gives a good overview of the multi-zone calculations for design conditions. This other ASHRAE article by Dennis Stanke of Trane gives a very good walkthrough of the 62.1 multizone calculations during operation (aka Multiple-zone VAV System Ventilation Optimization Control) if you want to dig into this deeper.

edit flag offensive delete link more

Comments

@Kyle Benne I think based on this question that we should set the design OA method to VentilationRateProcedure in the default VAV templates.

aparker's avatar aparker  ( 2015-10-15 13:04:47 -0600 )edit

Is there a best question and answer pair of the year award? If there is I think this post is a strong contender. Yeah I will make this happen.

Kyle Benne's avatar Kyle Benne  ( 2015-10-15 13:24:04 -0600 )edit
1

@Lyle K@jmcneill FYI starting with OS 1.9.3 you'll be able to attach a design spec OA to VAV terminals from both the GUI and the API.

aparker's avatar aparker  ( 2015-10-21 20:13:27 -0600 )edit

@aparker This is good news! Thanks!

jmcneill's avatar jmcneill  ( 2015-10-28 13:15:46 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2015-10-14 22:45:17 -0600

Seen: 1,280 times

Last updated: Oct 15 '15