What should I use to calculate COP? EER or IEER?

asked 2015-09-17 16:55:55 -0500

updated 2015-11-10 14:48:08 -0500

I would like to input "Rated Cooling COP" of "AirConditioner:VariableRefrigerantFlow". The engineer provides both EER and IEER for the unit. Which one should I use to calculate COP? As I know, IEER shows the performance of part load. However, the EER of this unit only shows the unit performance when VRF is operating 99%-100% of its full-size. I think most of the time, the unit will operate less than 98% of its full-size. Does it mean that I should use IEER to calculate the COP but not EER? Thanks.

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
4

answered 2015-09-17 16:58:50 -0500

You need to use EER at the rating condition to get the Rated Cooling COP.

As part as capturing part load performance, that's what performance curves are all about!

edit flag offensive delete link more
0

answered 2015-09-18 05:44:31 -0500

obuchely's avatar

You have to take in account that EER most of the time refers to packet performance. It includes compressors plus fans. COP often refers to compressor performance only. The best way for my is to get the technical data from the manufactured. It will show you at full load consumptions for compressor and fans. So you can be sure that you are modeling correct. For the part load you have to use the part load curve.

edit flag offensive delete link more