Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Setting zone ventilation design flow

asked 2015-08-31 02:12:50 -0600

updated 2015-08-31 12:02:29 -0600

How do we use the Zone Ventilation Design Flow object directly (not through the EnergyPlus IDF) in Open Studio?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2015-08-31 11:21:51 -0600

Under the Space Types tab in the OS App, you can access the OS:DesignSpecification:OutdoorAir object. This object allows you to edit the OA requirements for all the zones that are assigned to that Space Type. Essentially, this builds the ZoneVentilation:DesignFlowRate for each zone with that Space Type.

image description

edit flag offensive delete link more

Comments

1

Is this answer correct?

AFAIK DesignSpecification:OutdoorAir and ZoneVentilation:DesignFlowRate are two different things, the first is only used by air loops to bring outdoor air via mechanical ventilation and the second models natural ventilation via window openings OR mechanical ventilation outside of an air loop (like a fan that is directly mounted in the wall?), depending of the "Ventilation Type" parameter (https://bigladdersoftware.com/epx/doc....

I'm not 100% sure though, can someone please confirm?

I am a bit perplex though because I read from different places that OS:DesignSpecific

Adrien's avatar Adrien  ( 2020-11-21 02:53:55 -0600 )edit