First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Setting zone ventilation design flow

asked 9 years ago

updated 9 years ago

How do we use the Zone Ventilation Design Flow object directly (not through the EnergyPlus IDF) in Open Studio?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 9 years ago

Under the Space Types tab in the OS App, you can access the OS:DesignSpecification:OutdoorAir object. This object allows you to edit the OA requirements for all the zones that are assigned to that Space Type. Essentially, this builds the ZoneVentilation:DesignFlowRate for each zone with that Space Type.

image description

Preview: (hide)
link

Comments

1

Is this answer correct?

AFAIK DesignSpecification:OutdoorAir and ZoneVentilation:DesignFlowRate are two different things, the first is only used by air loops to bring outdoor air via mechanical ventilation and the second models natural ventilation via window openings OR mechanical ventilation outside of an air loop (like a fan that is directly mounted in the wall?), depending of the "Ventilation Type" parameter (https://bigladdersoftware.com/epx/doc....

I'm not 100% sure though, can someone please confirm?

I am a bit perplex though because I read from different places that OS:DesignSpecific

Adrien's avatar Adrien  ( 4 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 9 years ago

Seen: 994 times

Last updated: Aug 31 '15