BEopt Room AC % Conditioned

asked 2026-03-06 14:42:06 -0500

jpierce's avatar

updated 2026-03-07 09:45:16 -0500

BEopt supports modelling the partial air conditioning of a home by selecting/setting an option with an "Energy Multiplier[frac]" less than one. The name of this parameter implies that it simply scales the energy use of the RAC(s) relative to 100% coverage, whereas the help file is a bit more nuanced.

Room air conditioners are modeled as conditioning the entire finished floor area. This multiplier can be used to adjust the cooling energy use to account for, e.g., when the system does not condition the entire living space.

How is the energy modelling for these partial load installations handled? I ask, because a quick check of the energy consumption of three RAC options with the same efficiency but different coverage produces some non-intuitive results. As can be seen below, they certainly aren't a simple percentage of the 100% coverage energy consumption, but they also do not show any moderating effects from partition walls potentially being at less extreme temperatures than ambient walls.

image description

edit retag flag offensive close merge delete

Comments

Can you share your BEopt file via Google Drive or Dropbox?

shorowit's avatar shorowit  ( 2026-03-08 12:41:00 -0500 )edit

Here you go https://drive.google.com/drive/folders/1WLscmB7XVvD-IYjiVtgU4TgLcXrsLqfY?usp=drive_link It's BEopt 2.8 because I still have problems with version 3 on Windows 11 (hangs on simulation)

jpierce's avatar jpierce  ( 2026-03-09 08:20:18 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2026-03-09 13:32:32 -0500

updated 2026-03-09 13:35:51 -0500

The intent of the Energy Multiplier is indeed to scale the energy use of the RAC(s) relative to 100% coverage. I created a simple new construction home in BEopt 2.8 that gives perfect results (for 100% vs 30% vs 20%):

image description

That said, I can confirm in your retrofit case that it is not coming out that way and looks to be a bug. I think the issue is that the room air conditioner in the 100% case is being undersized, so its consumption is lower than it should be. If you look at the 20% and 30% runs in your graph, it does look like the 30% run consumption is 1.5x the 20% run consumption. Since BEopt 2.8 is more than 8 years old, it doesn't make sense to investigate further as there are no more bugfixes for that version, but I will plan to see if BEopt v3 is similarly affected.

edit flag offensive delete link more

Comments

Thanks for investigating.

Re: v2.8 noted. Alas v3b is also a bit dated and does not seem work with Windows 11 :-/

jpierce's avatar jpierce  ( 2026-03-09 13:45:21 -0500 )edit
1

I am running v3b on Windows 11 without a problem and I know many others are as well. If you can provide any information about what you are seeing, that would help. Have you retried installing it? Does it give any errors? Does v2.8 work on the same machine? Feel free to email me.

shorowit's avatar shorowit  ( 2026-03-09 13:50:25 -0500 )edit