Supplementary Heating in AirLoopHVAC:UnitaryHeatPump:AirToAir

asked 2025-10-27 21:20:53 -0500

Abir Ahsan's avatar

updated 2025-10-28 09:59:38 -0500

When using autosizing for the supplemental heating coil in the AirLoopHVAC:UnitaryHeatPump:AirToAir

object, does EnergyPlus size the coil based only on the unmet heating load remaining after the heat pump’s capacity, or is it sized for the full design heating load?

If it is sized only to cover the unmet portion, is there a way to autosize the supplemental coil to the full design load instead?

My goal is to model a dual-fuel system, where the supplemental heating coil operates on gas, while varying the heat pump capacity for cost optimization.

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2025-10-29 10:22:59 -0500

Greg Estep's avatar

updated 2025-10-29 10:23:28 -0500

I believe it sizes for the entire load. You can check in the component sizing report. This would make sense because if temperatures fall below the heat pump minimum outdoor air temperature, you still need full capacity.