The information above shows the zone and system sizing information. There is also "Component Sizing Information" information on coil sizing below this section in the eio file. Also look at the Capacity as a Function of Temperature performance curve for your coil. If the operating conditions (e.g., outdoor temperature and indoor wet-bulb temperature) are different than when the coil sized the capacity multiplier (the curve result) might be different. You can report all of this information using Output:Variable reports listed in the rdd file.
From eio file:
Component Sizing Information, COIL:COOLING:WATERTOAIRHEATPUMP:EQUATIONFIT, MAIN FLOOR WAHP COOLING COIL, Design Size Rated Total Cooling Capacity [W], 5725.81490
From rdd file:
Output:Variable,"your coil name",Cooling Coil Total Cooling Rate,hourly; !- HVAC Average [W]
Output:Variable,"your coil CAPFT curve name",Performance Curve Output Value,hourly; !- HVAC Average []
Output:Variable,"your coil INLET NODE name",System Node Temperature,hourly; !- HVAC Average [C]
Output:Variable,"your coil INLET NODE name",System Node Wetbulb Temperature,hourly; !- HVAC Average [C]