Constant COP of Cooling Coil

asked 2025-09-24 17:55:59 -0500

mep_engineer's avatar

updated 2025-09-25 09:37:15 -0500

In EnergyPlus, if I want my cooling system to have a constant COP regardless of temperature or flow fraction, which performance curves should I modify — should I flatten the 'Energy Input Ratio Function of Temperature' and 'Energy Input Ratio Function of Flow Fraction' curves (e.g., set them equal to 1.0), or is there another recommended way to configure the curves for constant COP performance?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2025-09-25 10:17:26 -0500

updated 2025-09-25 12:04:23 -0500

Yes, you'd set the coefficients for the following curves so that they yield a value of 1 regardless of PLF/Temp/Flow (independent variables):

Energy Input Ratio Modifier Curve
Energy Input Ratio Modifier Curve
Part Load Fraction Correlation