Summary of your model:
- single zone (6m x 8m x 2.7m)
- no windows, no doors
- 4x walls & 1x roof : 200mm concrete + 50mm EPS ... ~R10
- 1x slab-on-grade : 200mm + finish - no insulation
- no cooling, no ventilation, no infiltration
I can pretty much reproduce your results (max 34°C ... not 36°C) - I suspect I'm not using the same Damascus weather file. Yet overall, there's very little wrong with your model.
What is likely happening is that the (uninsulated) slab+ground combo is continuously acting as a heat sink, lowering zone air (and wall+roof interior surface) temperatures. Peruse through hourly surface temperatures in the eplusout.eso file: the floor interior surface temperatures are 3 to 4°C cooler than the other surface temperatures in summer.
I altered your model by adding the same 50mm EPS insulation in the floor construction (cancelling the slab+ground heat sink effect). The floor interior surface temperatures are now only slightly below the other temperatures (e.g. -0.5°C). Yet ALL temperatures are now 7 to 8°C warmer (in summer) than the original uninsulated scenario. This can also be accomplished by setting the floor outside boundary conditions to "adiabatic". Adding day ventilation + infiltration will make things worse. Adding a west-facing window will raise temperatures well into the 40°C, I suspect.
Side note: Check the eplusout.err file warnings for both the "people" and "equipment" definitions/schedules (see here), which I changed:
People,
ZONE ONE People, !- Name
GF, !- Zone or ZoneList or Space or SpaceList Name
ALWAYS 1, !- Number of People Schedule Name
People, !- Number of People Calculation Method
4, !- Number of People
, !- People per Floor Area {person/m2}
, !- Floor Area per Person {m2/person}
0.3, !- Fraction Radiant
0.3, !- Sensible Heat Fraction
ActivitySchedule; !- Activity Level Schedule Name
ElectricEquipment,
ZONE ONE Equipment, !- Name
GF, !- Zone or ZoneList or Space or SpaceList Name
ALWAYS 1, !- Schedule Name
EquipmentLevel, !- Design Level Calculation Method
400, !- Design Level {W}
, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/person}
0.3, !- Fraction Latent
0.6, !- Fraction Radiant
0.1; !- Fraction Lost
Schedule:Compact,
ALWAYS 1, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
1; !- Field 4
Schedule:Compact,
ActivitySchedule, !- Name
ActivityLevelX, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
100; !- Field 4
ScheduleTypeLimits,
ActivityLevelX, !- Name
70, !- Lower Limit Value
200, !- Upper Limit Value
continuous, !- Numeric Type
activitylevel; !- Unit Type
Note the activity levels (e.g. min 70 W/person) ...
@Sama can you upload your model to Google Drive, Dropbox, etc. and then share a URL for others to download? That would help others provide better solutions.