asked 2025-07-01 01:15:25 -0500

updated 2025-07-01 09:29:48 -0500

I'm looking for the clarification on space type of a heated underground parking garage area. In the space type definitions in 90.1 the code says "Crawlspaces, attics, and parking garages with natural or mechanical ventilation are not considered enclosed spaces." However, this clarification is specifically listed under the "unconditioned space" label. If a garage has a heating system that allows it to qualify as conditioned or semi heated space based on btu/h-f^2 would it be considered an enclosed space? Or are all garage spaces not considered enclosed spaces weather they are conditioned or not?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2025-07-14 21:55:25 -0500

Keigo's avatar

You can refer to PNNL 90.1 Performance Rating Method Reference Manual.

image description

A parking garage with a heating system is an unenclosed space. The geometry, lighting power and HVAC system shall be modelled.