First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Why is it that when I set the output variable as "Zone Thermal Comfort Fanger Model PPD" in the EnergyPlus output variable section, there are no related CSV results appearing after parameterized simulation through Jeplus?

asked Nov 2

TIMO TIMO E+'s avatar

updated Nov 4

I'm sorry, but I can't provide images because the website requires at least 10 points to upload files. How can this issue be resolved?

image descriptionimage description!image descriptionimage description(http://)image description

Preview: (hide)

Comments

1

@TIMO TIMO E+ you should have enough karma points now to upload an image.

Aaron Boranian's avatar Aaron Boranian  ( Nov 3 )

1 Answer

Sort by » oldest newest most voted
0

answered Nov 4

PmP's avatar

The reporting frequency is set as annual, but your image shows timestep frequency results. Try changing the frequency to timestep.

Preview: (hide)
link

Comments

ok,let me try,thx

TIMO TIMO E+'s avatar TIMO TIMO E+  ( Nov 4 )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: Nov 2

Seen: 95 times

Last updated: Nov 04 '24