Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Modeling electric resistance heater in CBECC

asked 2024-09-21 18:08:32 -0600

Abdul1236's avatar

updated 2024-09-22 11:54:45 -0600

I am trying to model electric unit heater for a stairwell in CBECC Non-Res 2022 but for some reason when I use 'furnace' as my zone system and create a heating coil(electric resistance) with a fan, the output report spits out that there is a no cooling system for that stairwell and assigns it a random cooling coil capacity. It seems that the software is thinking that there should be a cooling happening although there is none. I have tried unchecking the box where it says 'add cooling system to meet the load' but no luck. Please guide if you have any idea.

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2024-09-23 10:03:31 -0600

LukeInCali's avatar

In general, all conditioned spaces are evaluated in both heating and cooling for compliance purposes. So yes, your stairwell will have a dummy cooling system added to it even though there's nothing installed in reality. I don't have this part of the ACM memorized, but it's going to be an autosized cooling system matching the Standard Design system type and ratings.

edit flag offensive delete link more

Comments

Thanks for the insights. I see. So it’s fine to leave it as auto sized as is right now? I was wondering if I needed to get rid of it but seems I cant. It’s not bothering in terms of overall compliance results or UMLH.

Abdul1236's avatar Abdul1236  ( 2024-09-23 13:32:01 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2024-09-21 17:02:46 -0600

Seen: 71 times

Last updated: Sep 23