You're correct, the EP object to do this is Sizing:Zone. However, as of OS 1.7.0 the Zone Cooling/Heating Design Supply Air Temperature Input Method field is not available in the App or the SDK and uses the default SupplyAirTemperature choice. These inputs are available in the OS App via Thermal Zones tab > Cooling Sizing Parameters and Heating Sizing Paramters buttons. I set these values to +/- 20F of the zone setpoint temperature to comply with 90.1.
These inputs are available in the OS App via Thermal Zones tab > Cooling Sizing Parameters and Heating Sizing Paramters buttons. I set these values to +/- 20F of the zone setpoint temperature to comply with 90.1.90.1 Appendix G.