Through the help of David Goldwasser with my GitHub Issue, I was able to figure out the issue. It appears that when I used the "Create Baseline Building" measure, it created System Type #4 PSZ HPs without a curve assigned for the Energy Input Ratio Function of Flow Fraction Curve Name field. Therefore, to fix the error I assigned a curve to all of those systems and now the model works fine. See below for an example of one of these systems that were created by the measure.
OS:Coil:Heating:DX:SingleSpeed,
{776f6865-1852-4676-bff0-84bf537884ed}, !- Handle
07-12_C_IT_Zn HP Htg Coil 426 Clg kBtu/hr 3.2COPH, !- Name
{6e8dbd76-5254-4c6f-a302-11a185759d64}, !- Availability Schedule Name
Autosize, !- Rated Total Heating Capacity {W}
3.60026690437399, !- Rated COP {W/W}
Autosize, !- Rated Air Flow Rate {m3/s}
773.3, !- Rated Supply Fan Power Per Volume Flow Rate {W/(m3/s)}
{d585d277-c98b-48a0-8bb4-28976a9a89d1}, !- Air Inlet Node Name
{25129ef6-83e4-46a2-9533-5fc6d1670159}, !- Air Outlet Node Name
{bc8f8221-eff4-4f73-8a4a-2bc3973fa606}, !- Total Heating Capacity Function of Temperature Curve Name
{cc195893-93ff-4d9b-babf-f147e959acbc}, !- Total Heating Capacity Function of Flow Fraction Curve Name
{e579bc22-6789-4e64-8d98-3e14056b26bd}, !- Energy Input Ratio Function of Temperature Curve Name
, !- Energy Input Ratio Function of Flow Fraction Curve Name
{c5cfd3ce-0677-4f0f-80df-6c8db152a06f}, !- Part Load Fraction Correlation Curve Name
{0604b260-f8f0-4a01-a837-cb7513e2a3e7}, !- Defrost Energy Input Ratio Function of Temperature Curve Name
-12.2, !- Minimum Outdoor Dry-Bulb Temperature for Compressor Operation {C}
1.67, !- Maximum Outdoor Dry-Bulb Temperature for Defrost Operation {C}
50, !- Crankcase Heater Capacity {W}
4.4, !- Maximum Outdoor Dry-Bulb Temperature for Crankcase Heater Operation {C}
ReverseCycle, !- Defrost Strategy
OnDemand, !- Defrost Control
0.166667, !- Defrost Time Period Fraction
2000; !- Resistive Defrost Heater Capacity {W}
