1 | initial version |
(idf file was sent to the helpdesk, Ticket 13055).
If you report Fan Electric Power, or System Node Mass Flow Rate, you'll see that the air handler is not operating on the design days. That leads to the airloop AvailabilityManager
or the schedule in the supply fan object. The schedule referenced by the fan object is
Schedule:Constant,
Always On Discrete, !- Name
OnOff, !- Schedule Type Limits Name
1; !- Hourly Value
No problem there. The schedule reference by the AvailabilityManager:Scheduled
is
Schedule:Compact,
On24/7/Weekdays, !- Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 24:00, !- Field 3
1, !- Field 4
For: AllOtherDays, !- Field 5
Until: 24:00, !- Field 6
0; !- Field 7
The day types in the design days are WinterDesignDay and SummerDesignDay, so the above schedule is off on those days. Change "For: Weekdays" to "For: Weekdays WinterDesignDay SummerDesignDay," and the system will run.
