| 1 | initial version |
@Keigo, when I run 5ZoneNightVent3 in the latest V26.2 I see OA and system air flow. I didn't check all nodes in the air loop and zones but it does appear to me that the system activates for Night Ventilation.
| 2 | No.2 Revision |
UPDATE: I added zone nodes to the investigation. Sure enough the zone side of the system has 0 flow during NightVentilation. This is because the TU is using the fan schedule when it should be Always ON.
AirTerminal:SingleDuct:VAV:Reheat, SPACE1-1 VAV Reheat, !- Name FanAvailSched, !- Availability Schedule Name
| 3 | No.3 Revision |
FanAvailSched, !- Availability Schedule NameName
| 4 | No.4 Revision |
SPACE1-1 AirTerminal:SingleDuct:VAV:Reheat,
FanAvailSched, FanAvailSched, !- Availability Schedule Name