This isn't a bug in Year — the EMS variable is stable. The spikes come from how
your EnergyManagementSystem:OutputVariable blocks are configured.
You set Type of Data in Variable = Summed and Update Frequency = SystemTimestep.
With that combination, EnergyPlus adds up the value once per HVAC system
sub-iteration inside each zone timestep. When cooling peaks, the HVAC solver
subdivides the zone timestep into more sub-iterations to converge — say N of
them — and the reported value becomes Year × N (and YearBaseline × N),
which is why both variables spike in sync. It's the OutputProcessor doing
exactly what Summed asks for, but Year isn't something you want summed.
## The fix
Change all three of your WIP_Year / WIP_YearDiff / WIP_YearBaseline output variables to:
EnergyManagementSystem:OutputVariable,
WIP_Year, Year, Averaged, ZoneTimestep, , ;
i.e. Summed → Averaged and SystemTimestep → ZoneTimestep. These are state
values, not rates, so Averaged is the right choice.
## Verifying it's the sub-iteration mechanism
If you divide your reported WIP_Year by 2030 you get an integer — literally
the number of HVAC sub-iterations that zone timestep used. Running your IDF on
current develop (26.2.0), the distribution across all 26,352 timesteps of your
RunPeriod:
N count %run WIP_Year
1 25,429 96.50% 2030
2 369 1.40% 4060
3 206 0.78% 6090
4 147 0.56% 8120
5 60 0.23% 10150
6 28 0.11% 12180
7 26 0.10% 14210
8 20 0.08% 16240
9 20 0.08% 18270
10 47 0.18% 20300
Every spike is exactly 2030 × N. 96.5% of timesteps are N=1 (no subdivision,
correct value), which is why the spikes look sporadic. You can also request
Output:Variable,*,HVAC System Solver Iteration Count,Timestep;
and you'll see it track the spikes too (it reports 3 × N on your model).
## One surprise: Year = 2030, not 2025
EnergyPlus reads the calendar year from the EPW file each step
(ESP_Sevilla.083910_SWEC_2030.epw → year 2030), so Year is 2030 in your
run even though RunPeriod Begin Year = 2025. If you want the RunPeriod year
instead, the built-in CalendarYear is the one to use — it tracks the
RunPeriod, not the weather file. Your YearDiff will then be 10 as expected.
So:
- Use Averaged, ZoneTimestep to stop the spikes
- Use CalendarYear instead of Year if you want 2025 - 2015 = 10
I also posted a detailed write-up with the full proof on GitHub issue https://github.com/NatLabRockies/EnergyPlus/issues/7569 for reference.