reliability of Chillers.idf entries?

I was looking through various chillers around 425 ton in the EnergyPlus-8.7.0\DataSets\Chillers.idf file (Chiller:Electric:EIR):

Trane CVHE 422 ton VSD York YT 425 Ton VSD Carrier 19XR 443 ton VSD Carrier 19XR 465 ton Vanes McQuay WSC 432 ton Vanes

All of these have their Optimum Part Load Ratio set to 1.0. Even for the two Vanes chillers, I don't believe this is true, and certainly not for the VSD chillers. When plotting EIR = EIRFT*EIRPLR/PLR/COPref vs. PLR, the Vanes chillers have their optimum PLR (point of best COP according to EnergyPlus I/O reference) near 75% and the VSD chillers have their optimum PLR near 40%.

In addition, most of these have non-standard Entering Condenser Water Temperatures.

Just curious, how useful/trustworthy are these chiller curves, or is the optimum PLR usually the only major discrepancy in these?

reliability of Chillers.idf entries?

I was looking through various chillers around 425 ton in the EnergyPlus-8.7.0\DataSets\Chillers.idf file (Chiller:Electric:EIR):

Trane CVHE 422 ton VSD York YT 425 Ton VSD Carrier 19XR 443 ton VSD Carrier 19XR 465 ton Vanes McQuay WSC 432 ton Vanes

All of these have their Optimum Part Load Ratio set to 1.0. Even for the two Vanes chillers, I don't believe this is true, and certainly not for the VSD chillers. When plotting EIR = EIRFT*EIRPLR/PLR/COPref vs. PLR, the Vanes chillers have their optimum PLR (point of best COP according to EnergyPlus I/O reference) near 75% and the VSD chillers have their optimum PLR near 40%.

In addition, most of these have non-standard Entering Condenser Water Temperatures.

Just curious, how useful/trustworthy are these chiller curves, or is the optimum PLR usually the only major discrepancy in these?