Water Heater Efficiency per Table 7.8 of ASHRAE 90.1-2010

Hello,

I'm currently working with two (600,000 Btuh, 130 Gallons, 97 EF) boilers for a dormitory building. From my interpretation of Table 7.8 the equation I'm suppose to use is 80%Et(Q/800 +110sqrt(V)) SL, Btuh. From I've what I've read, I'm suppose to disregard the 80% Et and that leaves me for the remainder of the equation (600000/800 + 110sqrt(130)) to get 2004 Btuh as my stand by loss for my baseline water heaters. A few questions I had were:

  1. Should I leave this number in the service water heating section as what I calculated as for the SL or do I need to convert this to an EF ?

  2. Is there a way to convert to this to an efficiency (EF)?

In previous projects my co-worker worked on they always left as a % EF on the MEP calculator and used that along with the HW usage to calculate an energy usage in MBH/hr for each water heater. They then plugged that energy usage into Trace 700 for the base utilities for the water heaters.

Water Heater Efficiency per Table 7.8 of ASHRAE 90.1-2010

Hello,

I'm currently working with two (600,000 Btuh, 130 Gallons, 97 EF) boilers for a dormitory building. From my interpretation of Table 7.8 the equation I'm suppose to use is 80%Et(Q/800 +110sqrt(V)) SL, Btuh. From I've what I've read, I'm suppose to disregard the 80% Et and that leaves me for the remainder of the equation (600000/800 + 110sqrt(130)) to get 2004 Btuh as my stand by loss for my baseline water heaters. A few questions I had were:

  1. Should I leave this number in the service water heating section as what I calculated as for the SL or do I need to convert this to an EF ?

  2. Is there a way to convert to this to an efficiency (EF)?

In previous projects my co-worker worked on they always left as a % EF on the MEP calculator and used that along with the HW usage to calculate an energy usage in MBH/hr for each water heater. They then plugged that energy usage into Trace 700 for the base utilities for the water heaters.