I want to model a hybrid HVAC system of VAV and Active Chilled Beam (ACB). ACB has cooling capacity of 30W per outdoor air flow rate, wchich is insufficient to handle all the cooling load, and VAV handles the remaining cooling load.
I reproduced the "problems" in simple models for posting on this site. The base model is 5ZoneWarmest.idf (but I revised parameters such as schedule and internal loads a lot).
Then, I added ACB as follows. One AirLoop has two Airterminals in each zone. I have the following issues when I autosize.
Minimum Outdoor Air Flow Rate
ofController:OutdoorAir
is double counted.Design Size Maximum Flow Rate
ofFan:Variable
is oversized.PlantLoop (
Design Maximum Flow Rate
ofPump:VariableSpeed
,Reference Capacity
ofChiller:Electric:EIR
,Design Air Flow Rate
ofCoolingTower:SingleSpeed
, etc.) is oversized.
Is there any way to autosize them correctly? Or is this a bug and we have to wait for it to be fixed in the future?
On the other hand, I also modelled the following AirLoops i.e., the AirLoop for ACB and the AirLoop for VAV are separated. In this model, AirLoops and PlantLoops have smaller flow rates compared to the previous model (5ZoneWarmest_rev+ACB_Integrated.idf), but still larger than 5ZoneWarmest_rev.idf.
As the above models are not autosized well, I hardsized some parameters and finally managed to get what I wanted (5ZoneWarmest_rev+ACB_Integrated_Hardsized.idf).
All the files (V23-2-0) are here.