I'm working on an existing IES VE model that will be used for Title 24 compliance. IES lists the following general guidance for errors:
I am receiving errors with room names. Can you offer any general guidance for the 3D model?
As the Title 24 module in the VE runs the CBECC-Com Ruleset & EnergyPlus simulation engine for compliance, there are a few limitations with regards to naming the rooms. Please note that these issues do not exist elsewhere in the VE:
- The &, >, <, and $ symbols cannot be used.
- No more than 10 rooms allowed per thermal zone.
- Duplicate room names are not allowed. Each room and each zone must have a unique name.
- Rooms on different floors cannot be on the same thermal zone.
- The analysis will not be successful with any space or surface polygon (PolyLp in CBECC-Com) containing more than 120 vertices due to a limitation in the EnergyPlus simulation.
- Self-shading surfaces (from ModelIT) are not accounted for in the Title 24 calculation.
Another common issue we see coming through to our technical support team is a mismatch on ventilation information. Some entries include 15 cfm/person, for example, but then the ventilation source is set as cfm/ft2. The CBECC ruleset will then check for the cfm/ft2 value, which is 0, and gives an error about not enough ventilation.
So my question is whether other IES VE users have encountered additional issues with translating to CBECC-Com and whether the above guidance holds? I'm specifically interested in #3, which I think may have been fixed by appending the room ID to the room name.