How to set LoadProfile:Plant on DesignDay

(This post is slightly related to my previous post about SwimmingPool:Indoor.)

I want to use LoadProfile:Plant in conjection with many Coil:Heating:Water objects in a hot water plant loop as shown below.

image description

I already know 8760 hours of load profile for LoadProfile:Plant, but the entire load in the hot water loop is unknon. So, I want to simulate sizing run and autosize the boiler, pump and heating coils.

LoadProfile:Plant is used with ScheduleFile. I also know the load profile for LoadProfile:Plant on WinterDesignDay and SummerDesignDay. However, the load profile on DesignDays cannot be input to ScheduleFile. How can I set set load of LoadProfile:Plant on DesignDays?

According to Application Guide for EMS, it seems that "CurrentEnvironment == 1" represents WinterDesignDay when WinterDesignDay is Obj1 of SizingPeriod:DesignDay. I tried to override ScheduleFile during the sizing run with EMS, but my EMS input does not work for now. During the design days, EnergyPlus refers to loads on the same date as the sizing day in ScheduleFile i.e. load on January 21st for WinterSizingDay in my case.

I would appreciate it if anyone could correct my EMS input below or advise any other way to set LoadProfile:Plant on DesignDays.

! CHICAGO_IL_USA Annual Heating 99% Design Conditions DB, MaxDB= -17.3°C
SizingPeriod:DesignDay,
    CHICAGO_IL_USA Annual Heating 99% Design Conditions DB,  !- Name
    1,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    -17.3,                   !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    ,                        !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Day Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    -17.3,                   !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    99063.,                  !- Barometric Pressure {Pa}
    4.9,                     !- Wind Speed {m/s}
    270,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.0;                     !- Sky Clearness

Schedule:File,
    Swimming_Pool_Load_Schedule,  !- Name
    ,                        !- Schedule Type Limits Name
    C:\Project\Swimming_Pool_Load_Schedule\Swimming_Pool_Load_Schedule.csv,  !- File Name
    2,                       !- Column Number
    1,                       !- Rows to Skip at Top
    8760,                    !- Number of Hours of Data
    Comma,                   !- Column Separator
    No,                      !- Interpolate to Timestep
    60,                      !- Minutes per Item
    No;                      !- Adjust Schedule for Daylight Savings

LoadProfile:Plant,
    Swimming_Pool,  !- Name
    Swimming_Pool Inlet,  !- Inlet Node Name
    Swimming_Pool Outlet,  !- Outlet Node Name
    Swimming_Pool_Load_Schedule,  !- Load Schedule Name
    0.0398,                   !- Peak Flow Rate {m3/s}
    ASHRAE90.1_Schedule_H_Ventilation;  !- Flow Rate Fraction Schedule Name

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========

EnergyManagementSystem:Actuator,
    Swimming_Pool_Load_Schedule_Override,  !- Name
    Swimming_Pool_Load_Schedule,  !- Actuated Component Unique Name
    Schedule:File,           !- Actuated Component Type
    Schedule Value;          !- Actuated Component Control Type

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========

EnergyManagementSystem:ProgramCallingManager,
    EMS_PCM_Pool_Load_Schedule_Override,  !- Name
    AfterComponentInputReadIn,  !- EnergyPlus Model Calling Point
    EMS_Program_Pool_Load_Schedule_Override;  !- Program Name 1

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========

EnergyManagementSystem:Program,
    EMS_Program_Pool_Load_Schedule_Override,  !- Name
    IF (CurrentEnvironment == 1) && (CurrentTime == 1),  !- Program Line 1
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- Program Line 2
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 2),  !- A4
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A5
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 3),  !- A6
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A7
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 4),  !- A8
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A9
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 5),  !- A10
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A11
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 6),  !- A12
    SET Swimming_Pool_Load_Schedule_Override = 376992.2,  !- A13
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 7),  !- A14
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A15
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 8),  !- A16
    SET Swimming_Pool_Load_Schedule_Override = 658.6,  !- A17
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 9),  !- A18
    SET Swimming_Pool_Load_Schedule_Override = 170214.3,  !- A19
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 10),  !- A20
    SET Swimming_Pool_Load_Schedule_Override = 4427.3,  !- A21
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 11),  !- A22
    SET Swimming_Pool_Load_Schedule_Override = 83041.5,  !- A23
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 12),  !- A24
    SET Swimming_Pool_Load_Schedule_Override = 165126.8,  !- A25
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 13),  !- A26
    SET Swimming_Pool_Load_Schedule_Override = 5655.7,  !- A27
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 14),  !- A28
    SET Swimming_Pool_Load_Schedule_Override = 159247.5,  !- A29
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 15),  !- A30
    SET Swimming_Pool_Load_Schedule_Override = 8976.7,  !- A31
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 16),  !- A32
    SET Swimming_Pool_Load_Schedule_Override = 154043.9,  !- A33
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 17),  !- A34
    SET Swimming_Pool_Load_Schedule_Override = 12206.8,  !- A35
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 18),  !- A36
    SET Swimming_Pool_Load_Schedule_Override = 75720.2,  !- A37
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 19),  !- A38
    SET Swimming_Pool_Load_Schedule_Override = 159007.2,  !- A39
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 20),  !- A40
    SET Swimming_Pool_Load_Schedule_Override = 2813.3,  !- A41
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 21),  !- A42
    SET Swimming_Pool_Load_Schedule_Override = 159402.8,  !- A43
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 22),  !- A44
    SET Swimming_Pool_Load_Schedule_Override = 6384.2,  !- A45
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 23),  !- A46
    SET Swimming_Pool_Load_Schedule_Override = 150281.2,  !- A47
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 24),  !- A48
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A49
    ENDIF;                   !- A50

How to set LoadProfile:Plant on DesignDay

(This post is slightly related to my previous post about SwimmingPool:Indoor.)

I want to use LoadProfile:Plant in conjection with many Coil:Heating:Water objects in a hot water plant loop as shown below.

image description

I already know 8760 hours of load profile for LoadProfile:Plant, but the entire load in the hot water loop is unknon. So, I want to simulate sizing run and autosize the boiler, pump and heating coils.

LoadProfile:Plant is used with ScheduleFile. I also know the load profile for LoadProfile:Plant on WinterDesignDay and SummerDesignDay. However, the load profile on DesignDays cannot be input to ScheduleFile. How can I set set load of LoadProfile:Plant on DesignDays?

According to Application Guide for EMS, it seems that "CurrentEnvironment == 1" represents WinterDesignDay when WinterDesignDay is Obj1 of SizingPeriod:DesignDay. I tried to override ScheduleFile during the sizing run with EMS, but my EMS input does not work for now. During the design days, sizing run, EnergyPlus refers to loads on the same date as the sizing day in ScheduleFile i.e. load on January 21st for WinterSizingDay WinterDesignDay in my case.case, which is not what I expect.

I would appreciate it if anyone could correct my EMS input below or advise any other way to set LoadProfile:Plant on DesignDays.

! CHICAGO_IL_USA Annual Heating 99% Design Conditions DB, MaxDB= -17.3°C
SizingPeriod:DesignDay,
    CHICAGO_IL_USA Annual Heating 99% Design Conditions DB,  !- Name
    1,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    -17.3,                   !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    ,                        !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Day Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    -17.3,                   !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    99063.,                  !- Barometric Pressure {Pa}
    4.9,                     !- Wind Speed {m/s}
    270,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.0;                     !- Sky Clearness

Schedule:File,
    Swimming_Pool_Load_Schedule,  !- Name
    ,                        !- Schedule Type Limits Name
    C:\Project\Swimming_Pool_Load_Schedule\Swimming_Pool_Load_Schedule.csv,  !- File Name
    2,                       !- Column Number
    1,                       !- Rows to Skip at Top
    8760,                    !- Number of Hours of Data
    Comma,                   !- Column Separator
    No,                      !- Interpolate to Timestep
    60,                      !- Minutes per Item
    No;                      !- Adjust Schedule for Daylight Savings

LoadProfile:Plant,
    Swimming_Pool,  !- Name
    Swimming_Pool Inlet,  !- Inlet Node Name
    Swimming_Pool Outlet,  !- Outlet Node Name
    Swimming_Pool_Load_Schedule,  !- Load Schedule Name
    0.0398,                   !- Peak Flow Rate {m3/s}
    ASHRAE90.1_Schedule_H_Ventilation;  !- Flow Rate Fraction Schedule Name

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========

EnergyManagementSystem:Actuator,
    Swimming_Pool_Load_Schedule_Override,  !- Name
    Swimming_Pool_Load_Schedule,  !- Actuated Component Unique Name
    Schedule:File,           !- Actuated Component Type
    Schedule Value;          !- Actuated Component Control Type

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========

EnergyManagementSystem:ProgramCallingManager,
    EMS_PCM_Pool_Load_Schedule_Override,  !- Name
    AfterComponentInputReadIn,  !- EnergyPlus Model Calling Point
    EMS_Program_Pool_Load_Schedule_Override;  !- Program Name 1

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========

EnergyManagementSystem:Program,
    EMS_Program_Pool_Load_Schedule_Override,  !- Name
    IF (CurrentEnvironment == 1) && (CurrentTime == 1),  !- Program Line 1
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- Program Line 2
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 2),  !- A4
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A5
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 3),  !- A6
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A7
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 4),  !- A8
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A9
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 5),  !- A10
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A11
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 6),  !- A12
    SET Swimming_Pool_Load_Schedule_Override = 376992.2,  !- A13
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 7),  !- A14
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A15
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 8),  !- A16
    SET Swimming_Pool_Load_Schedule_Override = 658.6,  !- A17
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 9),  !- A18
    SET Swimming_Pool_Load_Schedule_Override = 170214.3,  !- A19
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 10),  !- A20
    SET Swimming_Pool_Load_Schedule_Override = 4427.3,  !- A21
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 11),  !- A22
    SET Swimming_Pool_Load_Schedule_Override = 83041.5,  !- A23
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 12),  !- A24
    SET Swimming_Pool_Load_Schedule_Override = 165126.8,  !- A25
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 13),  !- A26
    SET Swimming_Pool_Load_Schedule_Override = 5655.7,  !- A27
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 14),  !- A28
    SET Swimming_Pool_Load_Schedule_Override = 159247.5,  !- A29
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 15),  !- A30
    SET Swimming_Pool_Load_Schedule_Override = 8976.7,  !- A31
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 16),  !- A32
    SET Swimming_Pool_Load_Schedule_Override = 154043.9,  !- A33
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 17),  !- A34
    SET Swimming_Pool_Load_Schedule_Override = 12206.8,  !- A35
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 18),  !- A36
    SET Swimming_Pool_Load_Schedule_Override = 75720.2,  !- A37
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 19),  !- A38
    SET Swimming_Pool_Load_Schedule_Override = 159007.2,  !- A39
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 20),  !- A40
    SET Swimming_Pool_Load_Schedule_Override = 2813.3,  !- A41
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 21),  !- A42
    SET Swimming_Pool_Load_Schedule_Override = 159402.8,  !- A43
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 22),  !- A44
    SET Swimming_Pool_Load_Schedule_Override = 6384.2,  !- A45
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 23),  !- A46
    SET Swimming_Pool_Load_Schedule_Override = 150281.2,  !- A47
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 24),  !- A48
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A49
    ENDIF;                   !- A50

How to set LoadProfile:Plant on DesignDay

(This post is slightly related to my previous post about SwimmingPool:Indoor.)

I want to use LoadProfile:Plant in conjection with many Coil:Heating:Water objects in a hot water plant loop as shown below.

image description

I already know 8760 hours of load profile for LoadProfile:Plant, but the entire load in the hot water loop is unknon. So, I want to simulate sizing run and autosize the boiler, pump and heating coils.

LoadProfile:Plant is used with ScheduleFile. I also know the load profile for LoadProfile:Plant on WinterDesignDay and SummerDesignDay. However, the load profile on DesignDays cannot be input to ScheduleFile. How can I set set load of LoadProfile:Plant on DesignDays?

According to Application Guide for EMS, it seems that "CurrentEnvironment == 1" represents WinterDesignDay when WinterDesignDay is Obj1 of SizingPeriod:DesignDay. I tried to override ScheduleFile during the sizing run with EMS, but my EMS input does not work for now. During the sizing run, EnergyPlus refers to loads on the same date as the sizing day in ScheduleFile i.e. load on January 21st for WinterDesignDay in my case, which is not what I expect.

I would appreciate it if anyone could correct my EMS input below or advise any other way to set LoadProfile:Plant on DesignDays.

! CHICAGO_IL_USA Annual Heating 99% Design Conditions DB, MaxDB= -17.3°C
SizingPeriod:DesignDay,
    CHICAGO_IL_USA Annual Heating 99% Design Conditions DB,  !- Name
    1,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    -17.3,                   !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    ,                        !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Day Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    -17.3,                   !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    99063.,                  !- Barometric Pressure {Pa}
    4.9,                     !- Wind Speed {m/s}
    270,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.0;                     !- Sky Clearness

Schedule:File,
    Swimming_Pool_Load_Schedule,  !- Name
    ,                        !- Schedule Type Limits Name
    C:\Project\Swimming_Pool_Load_Schedule\Swimming_Pool_Load_Schedule.csv,  !- File Name
    2,                       !- Column Number
    1,                       !- Rows to Skip at Top
    8760,                    !- Number of Hours of Data
    Comma,                   !- Column Separator
    No,                      !- Interpolate to Timestep
    60,                      !- Minutes per Item
    No;                      !- Adjust Schedule for Daylight Savings

LoadProfile:Plant,
    Swimming_Pool,  !- Name
    Swimming_Pool Inlet,  !- Inlet Node Name
    Swimming_Pool Outlet,  !- Outlet Node Name
    Swimming_Pool_Load_Schedule,  !- Load Schedule Name
    0.0398,                   !- Peak Flow Rate {m3/s}
    ASHRAE90.1_Schedule_H_Ventilation;  !- Flow Rate Fraction Schedule Name

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========

EnergyManagementSystem:Actuator,
    Swimming_Pool_Load_Schedule_Override,  !- Name
    Swimming_Pool_Load_Schedule,  !- Actuated Component Unique Name
    Schedule:File,           !- Actuated Component Type
    Schedule Value;          !- Actuated Component Control Type

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========

EnergyManagementSystem:ProgramCallingManager,
    EMS_PCM_Pool_Load_Schedule_Override,  !- Name
    AfterComponentInputReadIn,  !- EnergyPlus Model Calling Point
    EMS_Program_Pool_Load_Schedule_Override;  !- Program Name 1

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========

EnergyManagementSystem:Program,
    EMS_Program_Pool_Load_Schedule_Override,  !- Name
    IF (CurrentEnvironment == 1) && (CurrentTime == 1),  !- Program Line 1
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- Program Line 2
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 2),  !- A4
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A5
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 3),  !- A6
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A7
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 4),  !- A8
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A9
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 5),  !- A10
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A11
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 6),  !- A12
    SET Swimming_Pool_Load_Schedule_Override = 376992.2,  !- A13
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 7),  !- A14
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A15
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 8),  !- A16
    SET Swimming_Pool_Load_Schedule_Override = 658.6,  !- A17
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 9),  !- A18
    SET Swimming_Pool_Load_Schedule_Override = 170214.3,  !- A19
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 10),  !- A20
    SET Swimming_Pool_Load_Schedule_Override = 4427.3,  !- A21
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 11),  !- A22
    SET Swimming_Pool_Load_Schedule_Override = 83041.5,  !- A23
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 12),  !- A24
    SET Swimming_Pool_Load_Schedule_Override = 165126.8,  !- A25
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 13),  !- A26
    SET Swimming_Pool_Load_Schedule_Override = 5655.7,  !- A27
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 14),  !- A28
    SET Swimming_Pool_Load_Schedule_Override = 159247.5,  !- A29
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 15),  !- A30
    SET Swimming_Pool_Load_Schedule_Override = 8976.7,  !- A31
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 16),  !- A32
    SET Swimming_Pool_Load_Schedule_Override = 154043.9,  !- A33
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 17),  !- A34
    SET Swimming_Pool_Load_Schedule_Override = 12206.8,  !- A35
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 18),  !- A36
    SET Swimming_Pool_Load_Schedule_Override = 75720.2,  !- A37
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 19),  !- A38
    SET Swimming_Pool_Load_Schedule_Override = 159007.2,  !- A39
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 20),  !- A40
    SET Swimming_Pool_Load_Schedule_Override = 2813.3,  !- A41
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 21),  !- A42
    SET Swimming_Pool_Load_Schedule_Override = 159402.8,  !- A43
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 22),  !- A44
    SET Swimming_Pool_Load_Schedule_Override = 6384.2,  !- A45
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 23),  !- A46
    SET Swimming_Pool_Load_Schedule_Override = 150281.2,  !- A47
    ELSEIF (CurrentEnvironment == 1) && (CurrentTime == 24),  !- A48
    SET Swimming_Pool_Load_Schedule_Override = 0,  !- A49
    ENDIF;                   !- A50