For DX cooling/heating coils, the rated air volume flow rate per watt of rated total cooling/heating capacity is limited from 0.00004027m3/s/W to 0.00006041 m3/s/W (300 to 450 cfm/ton) (I/O Reference, Engineering Reference).
Most VRF indoor units can switch airflow like H/L or H/M/L, but normally, only one power consumption is on catalogues or technical data sheets, so I regard the power consumption the maximum fan power with the highest airflow rate i.e., I input the highest airflow rate to Cooling Supply Air Flow Rate
and Heating Supply Air Flow Rate
in ZoneHVAC:TerminalUnit:VariableRefrigerantFlow
. The drain pump power may be included in the power consumption, but I ignore it unless I can identify it. And I input the lowest airflow rate to No Cooling Supply Air Flow Rate
and No Heating Supply Air Flow Rate
in ZoneHVAC:TerminalUnit:VariableRefrigerantFlow
.
The problem is that the highest airflow rate in product catalogues often exceeds the upper limit of 0.00006041 m3/s/W. The airflow constraints are not in line with the actual products. Below is an extract from DAIKIN's catalogue as an exapmle.
I have a few questions:
- Why does EnergyPlus have lower and upper limits for DX coil's rated airflow rate per cooling/heaitng capacity?
- Will the limits be relaxed or eliminated in the future?
- For now, should we use the airflow that meets the limits rather than the maximum airflow from the multiple airflow listed in product catalogues?