I want to adjust IPLV of Chiller:Electric:EIR
. I referred to Engineering Reference and calculate the IPLV in Excel before running simulation, which can avoid iterating simulation many times. When I change the coefficients of three chiller performance curves in the Excel, I can get the IPLV instantly.
However, the calculated IPLV (6.62) in the Excel is approximately 1.5% larger than the reported IPLV (6.52) in the html file. I did a sizing run to output the html file.
I saw this post, and I have already fix the Minimum Value of y (Entering condenser water temperature). IPLV calculating condition is within the Minimum/Maximum value of x/y.
What is causing this difference? I can't identify it. Is it due to the significant figures? Or are the numbers in Engineering Reference different from numbers actually used in EnergyPlus? I want to calculate IPLV accurately in Excel.
The excel, html file and the idf file (V9-6-0) are here. I want to calculate IPLV accurately in Excel to avoid running simulation again and again. Any suggestions would be appreciated.