"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

** Severe  ** SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
**   ~~~   ** Node connections in branch are not consistent with object nodes.
**  Fatal  ** Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP

Here is my ChillerHeater:Absorption:DirectFired object:

ChillerHeater:Absorption:DirectFired,
    GAHP,                    !- Name
    autosize,                !- Nominal Cooling Capacity {W}
    0.8,                     !- Heating to Cooling Capacity Ratio
    0.97,                    !- Fuel Input to Cooling Output Ratio
    1.25,                    !- Fuel Input to Heating Output Ratio
    0.01,                    !- Electric Input to Cooling Output Ratio
    ,                        !- Electric Input to Heating Output Ratio
    GAHP ChW Inlet,          !- Chilled Water Inlet Node Name
    GAHP ChW Outlet,         !- Chilled Water Outlet Node Name
    GAHP Cnd Inlet,          !- Condenser Inlet Node Name
    GAHP Cnd Outlet,         !- Condenser Outlet Node Name
    GAHP HW Inlet,           !- Hot Water Inlet Node Name
    GAHP HW Outlet,          !- Hot Water Outlet Node Name
    0.1,                     !- Minimum Part Load Ratio
    1,                       !- Maximum Part Load Ratio
    1,                       !- Optimum Part Load Ratio
    29,                      !- Design Entering Condenser Water Temperature {C}
    7,                       !- Design Leaving Chilled Water Temperature {C}
    autosize,                !- Design Chilled Water Flow Rate {m3/s}
    autosize,                !- Design Condenser Water Flow Rate {m3/s}
    autosize,                !- Design Hot Water Flow Rate {m3/s}
    GasAbsFlatBiQuad,        !- Cooling Capacity Function of Temperature Curve Name
    GasAbsFlatBiQuad,        !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
    GasAbsLinearQuad,        !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
    GasAbsFlatBiQuad,        !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
    GasAbsFlatQuad,          !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
    GasAbsInvLinearQuad,     !- Heating Capacity Function of Cooling Capacity Curve Name
    GasAbsLinearQuad,        !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
    EnteringCondenser,       !- Temperature Curve Input Variable
    AirCooled,               !- Condenser Type
    2,                       !- Chilled Water Temperature Lower Limit {C}
    ,                        !- Fuel Higher Heating Value {kJ/kg}
    NaturalGas,              !- Fuel Type
    1;                       !- Sizing Factor

I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. Now, the ChillerHeater replaced the chiller and the first of two boilers. The chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:error:

** * Severe  ** * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
** *   ~~~   ** * Node connections in branch are not consistent with object nodes.
** *  Fatal  ** * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
GAHP

Here is my ChillerHeater:Absorption:DirectFired object:

object:
ChillerHeater:Absorption:DirectFired,
   GAHP,                    !- Name
  !- Name
  autosize,            !- Nominal Cooling Capacity {W}
   0.8,                 !- Heating to Cooling Capacity Ratio
   0.97,                !- Fuel Input to Cooling Output Ratio
   1.25,                !- Fuel Input to Heating Output Ratio
   0.01,                !- Electric Input to Cooling Output Ratio
   ,                    !- Electric Input to Heating Output Ratio
   GAHP ChW Inlet,      !- Chilled Water Inlet Node Name
   GAHP ChW Outlet,     !- Chilled Water Outlet Node Name
   GAHP Cnd Inlet,      !- Condenser Inlet Node Name
   GAHP Cnd Outlet,     !- Condenser Outlet Node Name
   GAHP HW Inlet,       !- Hot Water Inlet Node Name
   GAHP HW Outlet,      !- Hot Water Outlet Node Name
   0.1,                 !- Minimum Part Load Ratio
   1,                   !- Maximum Part Load Ratio
   1,                   !- Optimum Part Load Ratio
   29,                  !- Design Entering Condenser Water Temperature {C}
   7,                   !- Design Leaving Chilled Water Temperature {C}
   autosize,            !- Design Chilled Water Flow Rate {m3/s}
   autosize,            !- Design Condenser Water Flow Rate {m3/s}
   autosize,            !- Design Hot Water Flow Rate {m3/s}
   GasAbsFlatBiQuad,    !- Cooling Capacity Function of Temperature Curve Name
   GasAbsFlatBiQuad,    !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
   GasAbsLinearQuad,    !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
   GasAbsFlatBiQuad,    !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
   GasAbsFlatQuad,      !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
    GasAbsInvLinearQuad,     !- GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
   GasAbsLinearQuad,    !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
   EnteringCondenser,   !- Temperature Curve Input Variable
   AirCooled,           !- Condenser Type
   2,                  !- Chilled Water Temperature Lower Limit {C}
   ,                    !- Fuel Higher Heating Value {kJ/kg}
   NaturalGas,          !- Fuel Type
   1;                   !- Sizing Factor
Factor

I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. Now, the ChillerHeater replaced the chiller and the first of two boilers. The chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively. exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. Now, I have an SVG file for the ChillerHeater replaced prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first of two boilers. boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image description

image description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. I have an SVG file for the prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image descriptionimage description

image descriptionimage description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. I have an SVG file for the prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image description

image description

image description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. I have an SVG file for the prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image descriptionimage description

image description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. I have an SVG file for the prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image descriptionimage description

image descriptionimage description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. I have an SVG file for the prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image description

image description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.

"Node connections in branch are not consistent with object nodes" when modeling a ChillerHeater:Absorption:DirectFired

I'm attempting to model a ChillerHeater:Absorption:DirectFired and I get this error:

* Severe  * SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
*   ~~~   * Node connections in branch are not consistent with object nodes.
*  Fatal  * Preceding conditions cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SimGasAbsorber: Invalid call to Gas Absorbtion Chiller-Heater GAHP
Here is my ChillerHeater:Absorption:DirectFired object:
ChillerHeater:Absorption:DirectFired,
  GAHP,               !- Name
  autosize,           !- Nominal Cooling Capacity {W}
  0.8,                !- Heating to Cooling Capacity Ratio
  0.97,               !- Fuel Input to Cooling Output Ratio
  1.25,               !- Fuel Input to Heating Output Ratio
  0.01,               !- Electric Input to Cooling Output Ratio
  ,                   !- Electric Input to Heating Output Ratio
  GAHP ChW Inlet,     !- Chilled Water Inlet Node Name
  GAHP ChW Outlet,    !- Chilled Water Outlet Node Name
  GAHP Cnd Inlet,     !- Condenser Inlet Node Name
  GAHP Cnd Outlet,    !- Condenser Outlet Node Name
  GAHP HW Inlet,      !- Hot Water Inlet Node Name
  GAHP HW Outlet,     !- Hot Water Outlet Node Name
  0.1,                !- Minimum Part Load Ratio
  1,                  !- Maximum Part Load Ratio
  1,                  !- Optimum Part Load Ratio
  29,                 !- Design Entering Condenser Water Temperature {C}
  7,                  !- Design Leaving Chilled Water Temperature {C}
  autosize,           !- Design Chilled Water Flow Rate {m3/s}
  autosize,           !- Design Condenser Water Flow Rate {m3/s}
  autosize,           !- Design Hot Water Flow Rate {m3/s}
  GasAbsFlatBiQuad,   !- Cooling Capacity Function of Temperature Curve Name
  GasAbsFlatBiQuad,   !- Fuel Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsFlatBiQuad,   !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
  GasAbsFlatQuad,     !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
  GasAbsInvLinearQuad,!- Heating Capacity Function of Cooling Capacity Curve Name
  GasAbsLinearQuad,   !- Fuel Input to Heat Output Ratio During Heating Only Operation Curve Name
  EnteringCondenser,  !- Temperature Curve Input Variable
  AirCooled,          !- Condenser Type
  2,                 !- Chilled Water Temperature Lower Limit {C}
  ,                   !- Fuel Higher Heating Value {kJ/kg}
  NaturalGas,         !- Fuel Type
  1;                  !- Sizing Factor
I have double-checked all my nodes in other classes and they seem correct. Before I inserted the ChillerHeater, my model had an air-cooled chiller and 2 boilers and it ran fine. I have an SVG file for the prior model and some screenshots are below. In anticipation of replacing them, I named both the chiller and the first boiler "GAHP". The demand side is not shown for brevity, but the chilled water loop serves one dummy fan coil without any load. The heating hot water loop serves numerous heating hot water coils with load on them.

image description

image description

In my current model that will not run due to the error, the ChillerHeater replaced the chiller and the first of two boilers. Please assist with any troubleshooting ideas. I'm using EnergyPlus 22.1.0 exclusively.