FourPipeFanCoil actuators for external control

Dear All,

I'm trying to control with actuators a ZoneHVAC:FourPipeFanCoil since now I was able to control the mass flow rate with the following actuator:

EnergyManagementSystem:Actuator,
    m_42,                    !- Name
    ZONE1  FAN COIL UNIT SUPPLY FAN,  !- Actuated Component Unique Name 
    Fan,    !- Actuated Component Type System Node Setpoint
    Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint

I have tried to control the out temperature from the heating coil with the following actuator but I was not able to achieve it:

EnergyManagementSystem:Actuator,
    t_42,                    !- Name
    ZONE1 FAN COIL UNIT SUPPLY OUTLET,  !- Actuated Component Unique Name 
    System Node Setpoint,    !- Actuated Component Type
    Temperature Setpoint;    !- Actuated Component Control Type

Any Idea on how I can control the air temperature outlet?

I'm able to do it in an air terminal with AirTerminal:SingleDuct:ConstantVolume:NoReheat like the following :

AirTerminal:SingleDuct:ConstantVolume:NoReheat, ZONE2 Single Duct CAV No Reheat, !- Name On 24/7, !- Availability Schedule Name Air Loop Zone Splitter Outlet Node 3, !- Air Inlet Node Name ZONE2 Single Duct CAV No Reheat Supply Outlet, !- Air Outlet Node Name 433.830000; !- Maximum Air Flow Rate {m3/s}

By controlling the flowing actuators:

EnergyManagementSystem:Actuator,
    t_41,                    !- Name
    AIR LOOP AHU HEATING COIL AIR OUTLET NODE,  !- Actuated Component Unique Name
    System Node Setpoint,    !- Actuated Component Type
    Temperature Setpoint;    !- Actuated Component Control Type

EnergyManagementSystem:Actuator,
    m_41,                    !- Name
    AIR LOOP AHU SUPPLY FAN,  !- Actuated Component Unique Name
    Fan,    !- Actuated Component Type System Node Setpoint
    Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint

Here you find the details of the ZoneHVAC:FourPipeFanCoil

ZoneHVAC:FourPipeFanCoil,
    ZONE1 Fan Coil Unit,  !- Name
    FAN COIL_FCA_Heating control schedule,  !- Availability Schedule Name
    ConstantFanVariableFlow, !- Capacity Control Method
    autosize,                !- Maximum Supply Air Flow Rate {m3/s}
    0.33,                    !- Low Speed Supply Air Flow Ratio
    0.66,                    !- Medium Speed Supply Air Flow Ratio
    0.0,                     !- Maximum Outdoor Air Flow Rate {m3/s}
    ,                        !- Outdoor Air Schedule Name
    ZONE1 Fan Coil Unit Return,  !- Air Inlet Node Name
    ZONE1  Fan Coil Unit Supply Outlet,  !- Air Outlet Node Name
    OutdoorAir:Mixer,        !- Outdoor Air Mixer Object Type
    ZONE1  Fan Coil Unit Outdoor Air Mixer,  !- Outdoor Air Mixer Name
    Fan:ConstantVolume,      !- Supply Air Fan Object Type
    ZONE1 Fan Coil Unit Supply Fan,  !- Supply Air Fan Name
    Coil:Cooling:Water,      !- Cooling Coil Object Type
    ZONE1 Fan Coil Unit Cooling Coil,  !- Cooling Coil Name
    autosize,                !- Maximum Cold Water Flow Rate {m3/s}
    0.000000,                !- Minimum Cold Water Flow Rate {m3/s}
    0.0010,                  !- Cooling Convergence Tolerance
    Coil:Heating:Water,      !- Heating Coil Object Type
    ZONE1 Coil Unit Heating Coil,  !- Heating Coil Name
    autosize,                !- Maximum Hot Water Flow Rate {m3/s}
    0.000000,                !- Minimum Hot Water Flow Rate {m3/s}
    0.0010;                  !- Heating Convergence Tolerance


Coil:Heating:Water,
    ZONE1 Fan Coil Unit Heating Coil,  !- Name
    On 24/7,                 !- Availability Schedule Name
    autosize,                !- U-Factor Times Area Value {W/K}
    autosize,                !- Maximum Water Flow Rate {m3/s}
    ZONE1 Fan Coil Unit Heating Coil Water Inlet Node,  !- Water Inlet Node Name
    ZONE1 Fan Coil Unit Heating Coil Water Outlet Node,  !- Water Outlet Node Name
    ZONE1 Fan Coil Unit Cooling Coil Outlet,  !- Air Inlet Node Name
    ZONE1 Fan Coil Unit Supply Outlet,  !- Air Outlet Node Name
    UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
    autosize,                !- Rated Capacity {W}
    80.0,                    !- Rated Inlet Water Temperature {C}
    16.0,                    !- Rated Inlet Air Temperature {C}
    70.0,                    !- Rated Outlet Water Temperature {C}
    35.0,                    !- Rated Outlet Air Temperature {C}
    0.50;                    !- Rated Ratio for Air and Water Convection


Fan:ConstantVolume,
    ZONE1 Fan Coil Unit Supply Fan,  !- Name
    FAN COIL_Heating control schedule,  !- Availability Schedule Name
    0.700000,                !- Fan Total Efficiency
    100.00,                  !- Pressure Rise {Pa}
    autosize,                !- Maximum Flow Rate {m3/s}
    0.900000,                !- Motor Efficiency
    1.00,                    !- Motor In Airstream Fraction
    ZONE1 Fan Coil Unit Mixed Air Outlet,  !- Air Inlet Node Name
    ZONE1 Fan Coil Unit Supply Fan Outlet,  !- Air Outlet Node Name
    General;                 !- End-Use Subcategory

FourPipeFanCoil actuators for external control

Dear All,

I'm trying to control with actuators a ZoneHVAC:FourPipeFanCoil since now I was able to control the mass flow rate with the following actuator:

EnergyManagementSystem:Actuator,
    m_42,                    !- Name
    ZONE1  FAN COIL UNIT SUPPLY FAN,  !- Actuated Component Unique Name 
    Fan,    !- Actuated Component Type System Node Setpoint
    Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint

I have tried to control the out temperature from the heating coil with the following actuator but I was not able to achieve it:

EnergyManagementSystem:Actuator,
    t_42,                    !- Name
    ZONE1 FAN COIL UNIT SUPPLY OUTLET,  !- Actuated Component Unique Name 
    System Node Setpoint,    !- Actuated Component Type
    Temperature Setpoint;    !- Actuated Component Control Type

Any Idea on how I can control the air temperature outlet?

I'm able to do it in an air terminal with AirTerminal:SingleDuct:ConstantVolume:NoReheat like the following :

AirTerminal:SingleDuct:ConstantVolume:NoReheat, ZONE2 Single Duct CAV No Reheat, !- Name On 24/7, !- Availability Schedule Name Air Loop Zone Splitter Outlet Node 3, !- Air Inlet Node Name ZONE2 Single Duct CAV No Reheat Supply Outlet, !- Air Outlet Node Name 433.830000; !- Maximum Air Flow Rate {m3/s}

By controlling the flowing actuators:

EnergyManagementSystem:Actuator,
    t_41,                    !- Name
    AIR LOOP AHU HEATING COIL AIR OUTLET NODE,  !- Actuated Component Unique Name
    System Node Setpoint,    !- Actuated Component Type
    Temperature Setpoint;    !- Actuated Component Control Type

EnergyManagementSystem:Actuator,
    m_41,                    !- Name
    AIR LOOP AHU SUPPLY FAN,  !- Actuated Component Unique Name
    Fan,    !- Actuated Component Type System Node Setpoint
    Fan Air Mass Flow Rate; !- Actuated Component Control Type Mass Flow Rate Setpoint

Here you find the details of the ZoneHVAC:FourPipeFanCoil

ZoneHVAC:FourPipeFanCoil,
    ZONE1 Fan Coil Unit,  !- Name
    FAN COIL_FCA_Heating control schedule,  !- Availability Schedule Name
    ConstantFanVariableFlow, !- Capacity Control Method
    autosize,                !- Maximum Supply Air Flow Rate {m3/s}
    0.33,                    !- Low Speed Supply Air Flow Ratio
    0.66,                    !- Medium Speed Supply Air Flow Ratio
    0.0,                     !- Maximum Outdoor Air Flow Rate {m3/s}
    ,                        !- Outdoor Air Schedule Name
    ZONE1 Fan Coil Unit Return,  !- Air Inlet Node Name
    ZONE1  Fan Coil Unit Supply Outlet,  !- Air Outlet Node Name
    OutdoorAir:Mixer,        !- Outdoor Air Mixer Object Type
    ZONE1  Fan Coil Unit Outdoor Air Mixer,  !- Outdoor Air Mixer Name
    Fan:ConstantVolume,      !- Supply Air Fan Object Type
    ZONE1 Fan Coil Unit Supply Fan,  !- Supply Air Fan Name
    Coil:Cooling:Water,      !- Cooling Coil Object Type
    ZONE1 Fan Coil Unit Cooling Coil,  !- Cooling Coil Name
    autosize,                !- Maximum Cold Water Flow Rate {m3/s}
    0.000000,                !- Minimum Cold Water Flow Rate {m3/s}
    0.0010,                  !- Cooling Convergence Tolerance
    Coil:Heating:Water,      !- Heating Coil Object Type
    ZONE1 Coil Unit Heating Coil,  !- Heating Coil Name
    autosize,                !- Maximum Hot Water Flow Rate {m3/s}
    0.000000,                !- Minimum Hot Water Flow Rate {m3/s}
    0.0010;                  !- Heating Convergence Tolerance


Coil:Heating:Water,
    ZONE1 Fan Coil Unit Heating Coil,  !- Name
    On 24/7,                 !- Availability Schedule Name
    autosize,                !- U-Factor Times Area Value {W/K}
    autosize,                !- Maximum Water Flow Rate {m3/s}
    ZONE1 Fan Coil Unit Heating Coil Water Inlet Node,  !- Water Inlet Node Name
    ZONE1 Fan Coil Unit Heating Coil Water Outlet Node,  !- Water Outlet Node Name
    ZONE1 Fan Coil Unit Cooling Coil Outlet,  !- Air Inlet Node Name
    ZONE1 Fan Coil Unit Supply Outlet,  !- Air Outlet Node Name
    UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
    autosize,                !- Rated Capacity {W}
    80.0,                    !- Rated Inlet Water Temperature {C}
    16.0,                    !- Rated Inlet Air Temperature {C}
    70.0,                    !- Rated Outlet Water Temperature {C}
    35.0,                    !- Rated Outlet Air Temperature {C}
    0.50;                    !- Rated Ratio for Air and Water Convection


Fan:ConstantVolume,
    ZONE1 Fan Coil Unit Supply Fan,  !- Name
    FAN COIL_Heating control schedule,  !- Availability Schedule Name
    0.700000,                !- Fan Total Efficiency
    100.00,                  !- Pressure Rise {Pa}
    autosize,                !- Maximum Flow Rate {m3/s}
    0.900000,                !- Motor Efficiency
    1.00,                    !- Motor In Airstream Fraction
    ZONE1 Fan Coil Unit Mixed Air Outlet,  !- Air Inlet Node Name
    ZONE1 Fan Coil Unit Supply Fan Outlet,  !- Air Outlet Node Name
    General;                 !- End-Use Subcategory