Why Kiva results seems to

I model a single storey building with a big surface (15 744m²) heated to 15°C. The building has the following insulation: floor: 0.24 K.m²W-1; walls: 2.98 K.m²W-1; roof: 6.07K.m².W-1.

I use Kiva foundations with the following parameters:

Foundation:Kiva,
    Slab Details,             !- Name
    15,                       !- Initial Indoor Air Temperature
    ,                         !- Interior Horizontal Insulation Material Name
    ,                         !- Interior Horizontal Insulation Depth
    ,                         !- Interior Horizontal Insulation Width
    ,                         !- Interior Vertical Insulation Material Name
    ,                         !- Interior Vertical Insulation Depth
    ,                         !- Exterior Horizontal Insulation Material Name
    ,                         !- Exterior Horizontal Insulation Depth
    ,                         !- Exterior Horizontal Insulation Width
    ,                         !- Exterior Vertical Insulation Material Name
    ,                         !- Exterior Vertical Insulation Depth
    ,                         !- Wall Height Above Grade
    ,                         !- Wall Depth Below Slab
    ;                         !- Footing Wall Construction Name

Foundation:Kiva:Settings,
    1.8,                      !- Soil Conductivity
    3200,                     !- Soil Density
    836,                      !- Soil Specific Heat
    0.9,                      !- Ground Solar Absorptivity
    0.9,                      !- Ground Thermal Absorptivity
    0.03,                     !- Ground Surface Roughness
    40,                       !- FarField Width
    GroundWater,              !- DeepGround Boundary Condition
    10;                       !- DeepGround Depth


SurfaceProperty:ExposedFoundationPerimeter,
    PLANCHER +00_+00_+00,     !- Surface Name
    ExposedPerimeterFraction,    !- Exposed Perimeter Calculation Method
    ,                         !- Total Exposed Perimeter
    1,                        !- Exposed Perimeter Fraction
    ;                         !- Surface Segment 1 Exposed

The simulation gives 87MWh of heating over the whole year(ie. 5.4kWh/m²/year).

Secondly, I simulate the same building but with fixed ground temperature with the monthly median of the inside face temperature of the floor of the previous Kiva simulation (taken in the middle of the building). The simulation gives 100 MWh of heating over the whole year(ie. 6.35kWh/m²/year).

I expected the contrary because the second simulation takes the inside face temperature as the ground surface temperature (moreover on the center of the building floor). It seems that the comportement is worse when I use the procedure but with 18°C for the temperature set point.

Details: 192m x 82m (a surface of 15 744m²) with 3 meters of height. The building got 10 x 5 parts (19.2m x 8.2m each).

IDF and EPW:

https://drive.google.com/drive/folders/1EaurIWbC6-qknmFLbSmnPoG6T1axVcD3?usp=sharing

Why Kiva results seems to

I model a single storey building with a big surface (15 744m²) heated to 15°C. The building has the following insulation: floor: 0.24 K.m²W-1; walls: 2.98 K.m²W-1; roof: 6.07K.m².W-1.

I use Kiva foundations with the following parameters:

Foundation:Kiva,
    Slab Details,             !- Name
    15,                       !- Initial Indoor Air Temperature
    ,                         !- Interior Horizontal Insulation Material Name
    ,                         !- Interior Horizontal Insulation Depth
    ,                         !- Interior Horizontal Insulation Width
    ,                         !- Interior Vertical Insulation Material Name
    ,                         !- Interior Vertical Insulation Depth
    ,                         !- Exterior Horizontal Insulation Material Name
    ,                         !- Exterior Horizontal Insulation Depth
    ,                         !- Exterior Horizontal Insulation Width
    ,                         !- Exterior Vertical Insulation Material Name
    ,                         !- Exterior Vertical Insulation Depth
    ,                         !- Wall Height Above Grade
    ,                         !- Wall Depth Below Slab
    ;                         !- Footing Wall Construction Name

Foundation:Kiva:Settings,
    1.8,                      !- Soil Conductivity
    3200,                     !- Soil Density
    836,                      !- Soil Specific Heat
    0.9,                      !- Ground Solar Absorptivity
    0.9,                      !- Ground Thermal Absorptivity
    0.03,                     !- Ground Surface Roughness
    40,                       !- FarField Width
    GroundWater,              !- DeepGround Boundary Condition
    10;                       !- DeepGround Depth


SurfaceProperty:ExposedFoundationPerimeter,
    PLANCHER +00_+00_+00,     !- Surface Name
    ExposedPerimeterFraction,    !- Exposed Perimeter Calculation Method
    ,                         !- Total Exposed Perimeter
    1,                        !- Exposed Perimeter Fraction
    ;                         !- Surface Segment 1 Exposed

The simulation gives 87MWh of heating over the whole year(ie. 5.4kWh/m²/year).

Secondly, I simulate the same building but with fixed ground temperature with the monthly median of the inside face temperature of the floor of the previous Kiva simulation (taken in the middle of the building). The simulation gives 100 MWh of heating over the whole year(ie. 6.35kWh/m²/year).

I expected the contrary because the second simulation takes the inside face temperature as the ground surface temperature (moreover on the center of the building floor). It seems that the comportement is worse when I use the procedure but with 18°C for the temperature set point.

Details: 192m x 82m (a surface of 15 744m²) with 3 meters of height. The building got 10 x 5 parts (19.2m x 8.2m each).

IDF and EPW:

https://drive.google.com/drive/folders/1EaurIWbC6-qknmFLbSmnPoG6T1axVcD3?usp=sharing

Why Kiva results seems toto reduce heat needs

I model a single storey building with a big surface (15 744m²) heated to 15°C. The building has the following insulation: floor: 0.24 K.m²W-1; walls: 2.98 K.m²W-1; roof: 6.07K.m².W-1.

I use Kiva foundations with the following parameters:

Foundation:Kiva,
    Slab Details,             !- Name
    15,                       !- Initial Indoor Air Temperature
    ,                         !- Interior Horizontal Insulation Material Name
    ,                         !- Interior Horizontal Insulation Depth
    ,                         !- Interior Horizontal Insulation Width
    ,                         !- Interior Vertical Insulation Material Name
    ,                         !- Interior Vertical Insulation Depth
    ,                         !- Exterior Horizontal Insulation Material Name
    ,                         !- Exterior Horizontal Insulation Depth
    ,                         !- Exterior Horizontal Insulation Width
    ,                         !- Exterior Vertical Insulation Material Name
    ,                         !- Exterior Vertical Insulation Depth
    ,                         !- Wall Height Above Grade
    ,                         !- Wall Depth Below Slab
    ;                         !- Footing Wall Construction Name

Foundation:Kiva:Settings,
    1.8,                      !- Soil Conductivity
    3200,                     !- Soil Density
    836,                      !- Soil Specific Heat
    0.9,                      !- Ground Solar Absorptivity
    0.9,                      !- Ground Thermal Absorptivity
    0.03,                     !- Ground Surface Roughness
    40,                       !- FarField Width
    GroundWater,              !- DeepGround Boundary Condition
    10;                       !- DeepGround Depth


SurfaceProperty:ExposedFoundationPerimeter,
    PLANCHER +00_+00_+00,     !- Surface Name
    ExposedPerimeterFraction,    !- Exposed Perimeter Calculation Method
    ,                         !- Total Exposed Perimeter
    1,                        !- Exposed Perimeter Fraction
    ;                         !- Surface Segment 1 Exposed

The simulation gives 87MWh of heating over the whole year(ie. 5.4kWh/m²/year).

Secondly, I simulate the same building but with fixed ground temperature with the monthly median of the inside face temperature of the floor of the previous Kiva simulation (taken in the middle of the building). The simulation gives 100 MWh of heating over the whole year(ie. 6.35kWh/m²/year).

I expected the contrary because the second simulation takes the inside face temperature as the ground surface temperature (moreover on the center of the building floor). It seems that the comportement is worse when I use the procedure but with 18°C for the temperature set point.

Details: 192m x 82m (a surface of 15 744m²) with 3 meters of height. The building got 10 x 5 parts (19.2m x 8.2m each).

IDF and EPW:

https://drive.google.com/drive/folders/1EaurIWbC6-qknmFLbSmnPoG6T1axVcD3?usp=sharing

Udated

It's like there is less exchanges when I use the Kiva model for the ground. Please look at the graph representing the floor surface conduction heat transfert: image description In the fixed ground temperature IDF there is to material layers for the floor: concrete + Insulation, but in the Kiva IDF I just put one layer with the insulation because the slab is already the concrete layer.

Finally, if I take the maximum of the "Surface Inside Face Temperature C" for each month in the Kiva solution for the second approach, results give me 83.5MWh. That's less than 2% above the Kiva solution.