How to add HeatExchanger:AirToAir:SensibleAndLatent with Supply Air Outlet Temperature Control to AirLoopHVAC:DedicatedOutdoorAirSystem

I want to add HeatExchanger:AirToAir:SensibleAndLatent to AirLoopHVAC:DedicatedOutdoorAirSystem, but I have a problem. Let me explain using an ExampleFile SmallOffice_CentralDOAS.idf. I added HeatExchanger:AirToAir:SensibleAndLatent as illustrated below. Here is the revised idf file (V9-6-0).

image description

When I set Supply Air Outlet Temperature Control of HeatExchanger:AirToAir:SensibleAndLatent to "No", there is no error and the simulation completes sucsessflly. However, when I set Supply Air Outlet Temperature Control to "Yes", the following severe error occurs and the simulation terminates even though I add a temperature setpoint with SetpointManager:Scheduled.

   ** Severe  ** Missing temperature setpoint for HeatExchanger:AirToAir:SensibleAndLatent "HEX" :
   **   ~~~   **   use a Setpoint Manager to establish a setpoint at the supply air outlet node of the Heat Exchanger.
   **  Fatal  **  Previous condition causes program termination.

At first, the same error occurred in another energy model which was much more complecated, so I tested with the simple ExampleFile to clarify the cause.

I tried several things such as adding OutdoorAir:Mixer and Controller:OutdoorAir which are usually not required for AirLoopHVAC:DedicatedOutdoorAirSystem. I also tried changing SetpointManager:Scheduled to SetpointManager:MixedAir, but they were all in vein. Any suggestions?

How to add HeatExchanger:AirToAir:SensibleAndLatent with Supply Air Outlet Temperature Control to AirLoopHVAC:DedicatedOutdoorAirSystem

I want to add HeatExchanger:AirToAir:SensibleAndLatent to AirLoopHVAC:DedicatedOutdoorAirSystem, but I have a problem. Let me explain using an ExampleFile SmallOffice_CentralDOAS.idf. I added HeatExchanger:AirToAir:SensibleAndLatent as illustrated below. Here is the revised idf file (V9-6-0).(V9-6-0). One more revision is that originally the OA Supply Fan was located in front of the heating coil i.e, blow-through configuration, but the Fan was changed after the cooling coil i.e., draw-through configuration.

image description

When I set Supply Air Outlet Temperature Control of HeatExchanger:AirToAir:SensibleAndLatent to "No", there is no error and the simulation completes sucsessflly. However, when I set Supply Air Outlet Temperature Control to "Yes", the following severe error occurs and the simulation terminates even though I add a temperature setpoint with SetpointManager:Scheduled.

   ** Severe  ** Missing temperature setpoint for HeatExchanger:AirToAir:SensibleAndLatent "HEX" :
   **   ~~~   **   use a Setpoint Manager to establish a setpoint at the supply air outlet node of the Heat Exchanger.
   **  Fatal  **  Previous condition causes program termination.

At first, the same error occurred in another energy model which was much more complecated, so I tested with the simple ExampleFile to clarify the cause.

I tried several things such as adding OutdoorAir:Mixer and Controller:OutdoorAir which are usually not required for AirLoopHVAC:DedicatedOutdoorAirSystem. I also tried changing SetpointManager:Scheduled to SetpointManager:MixedAir, but they were all in vein. Any suggestions?

How to add HeatExchanger:AirToAir:SensibleAndLatent with Supply Air Outlet Temperature Control to AirLoopHVAC:DedicatedOutdoorAirSystem

I want to add HeatExchanger:AirToAir:SensibleAndLatent to AirLoopHVAC:DedicatedOutdoorAirSystem, but I have a problem. Let me explain using an ExampleFile SmallOffice_CentralDOAS.idf. I added HeatExchanger:AirToAir:SensibleAndLatent as illustrated below. Here is the revised idf file (V9-6-0). One more revision is that originally the OA Supply Fan was located in front of the heating coil i.e, blow-through configuration, but the Fan was changed after the cooling coil i.e., draw-through configuration.

image description

When I set Supply Air Outlet Temperature Control of HeatExchanger:AirToAir:SensibleAndLatent to "No", there is no error and the simulation completes sucsessflly. However, when I set Supply Air Outlet Temperature Control to "Yes", the following severe error occurs and the simulation terminates even though I add a temperature setpoint with SetpointManager:Scheduled.

   ** Severe  ** Missing temperature setpoint for HeatExchanger:AirToAir:SensibleAndLatent "HEX" :
   **   ~~~   **   use a Setpoint Manager to establish a setpoint at the supply air outlet node of the Heat Exchanger.
   **  Fatal  **  Previous condition causes program termination.

At first, the same error occurred in another energy model which was much more complecated, so I tested with the simple ExampleFile to clarify the cause.

I tried several things such as adding OutdoorAir:Mixer and Controller:OutdoorAir which are usually not required for AirLoopHVAC:DedicatedOutdoorAirSystem. I also tried changing SetpointManager:Scheduled to SetpointManager:MixedAir, but they were all in vein. Any suggestions?

How to add HeatExchanger:AirToAir:SensibleAndLatent with Supply Air Outlet Temperature Control to AirLoopHVAC:DedicatedOutdoorAirSystem

I want to add HeatExchanger:AirToAir:SensibleAndLatent to AirLoopHVAC:DedicatedOutdoorAirSystem, but I have a problem. Let me explain using an ExampleFile SmallOffice_CentralDOAS.idf. I added HeatExchanger:AirToAir:SensibleAndLatent as illustrated below. Here is the revised idf file (V9-6-0). One more revision is that originally the OA Supply Fan was located in front of the heating coil i.e, blow-through configuration, but the Fan was changed after the cooling coil i.e., draw-through configuration.

image description

When I set Supply Air Outlet Temperature Control of HeatExchanger:AirToAir:SensibleAndLatent to "No", there is no error and the simulation completes sucsessflly. However, when I set Supply Air Outlet Temperature Control to "Yes", the following severe error occurs and the simulation terminates even though I add a temperature setpoint with SetpointManager:Scheduled.

   ** Severe  ** Missing temperature setpoint for HeatExchanger:AirToAir:SensibleAndLatent "HEX" :
   **   ~~~   **   use a Setpoint Manager to establish a setpoint at the supply air outlet node of the Heat Exchanger.
   **  Fatal  **  Previous condition causes program termination.

At first, the same error occurred in another energy model which was much more complecated, so I tested with the simple ExampleFile to clarify the cause.

I tried several things such as adding OutdoorAir:Mixer and Controller:OutdoorAir which are usually not required for AirLoopHVAC:DedicatedOutdoorAirSystem. I also tried changing SetpointManager:Scheduled to SetpointManager:MixedAir, but they were all in vein. Any suggestions?


I forgot to share my idf files. They are here. The version is V9-6-0.

How to add HeatExchanger:AirToAir:SensibleAndLatent with Supply Air Outlet Temperature Control to AirLoopHVAC:DedicatedOutdoorAirSystem

I want to add HeatExchanger:AirToAir:SensibleAndLatent to AirLoopHVAC:DedicatedOutdoorAirSystem, but I have a problem. Let me explain using an ExampleFile SmallOffice_CentralDOAS.idf. I added HeatExchanger:AirToAir:SensibleAndLatent as illustrated below. Here is the revised idf file (V9-6-0). One more revision is that originally the OA Supply Fan was located in front of the heating coil i.e, blow-through configuration, but the Fan was changed after the cooling coil i.e., draw-through configuration.

image description

When I set Supply Air Outlet Temperature Control of HeatExchanger:AirToAir:SensibleAndLatent to "No", there is no error and the simulation completes sucsessflly. However, when I set Supply Air Outlet Temperature Control to "Yes", the following severe error occurs and the simulation terminates even though I add a temperature setpoint with SetpointManager:Scheduled.

   ** Severe  ** Missing temperature setpoint for HeatExchanger:AirToAir:SensibleAndLatent "HEX" :
   **   ~~~   **   use a Setpoint Manager to establish a setpoint at the supply air outlet node of the Heat Exchanger.
   **  Fatal  **  Previous condition causes program termination.

At first, the same error occurred in another energy model which was much more complecated, so I tested with the simple ExampleFile to clarify the cause.

I tried several things such as adding OutdoorAir:Mixer and Controller:OutdoorAir which are usually not required for AirLoopHVAC:DedicatedOutdoorAirSystem. I also tried changing SetpointManager:Scheduled to SetpointManager:MixedAir, but they were all in vein. Any suggestions?


I forgot to share my idf files. They are here. The version is V9-6-0.