DaylightingDevice:Tubular Increases Lighting Power

Here are 3 idf files for a virtual office tower with different daylighting control settings. Their version is 8.9.0.

  • Case1: No daylighting control
  • Case2: Daylighting control in perimeter zone
  • Case3: Daylighting control in perimeter zone and interior zone with DaylightingDevice:Tubular

Case3 was created by adding DaylightingDevice:Tubular to Case2. However, lighting power in Case3 is higher than that in Case2. This is the problem. I don't know why.

image description

This is the 3D model. Only typical floors are modelled and multiplied. Vertical fins cover around the façade. image description

DaylightingDevice:Tubular in this model is not used in the usual way. Domes are not on the rooftop but on the wall. They are vertical. Diffusers are on the ceiling. The dome and the diffuser are not in a straight line. This system is not DaylightingDevice:Self, but more like DaylightingDevice:Tubular. Please refer to the sketch below.

image description

The increase of lighting power might be due to this unusual modelling, but I don't know what is actually not allowed in EnergyPlus.

DaylightingDevice:Tubular is in Office_N and Office_S on each floor. Perimeter area and Interior area are not separated. So, one zone has Daylighting:ReferencePoints for both exterior glazing and DaylightingDevice:Tubular. The simulation result looks as if DaylightingDevice:Tubular is offsetting the lighting power reduction in the perimeter area. It's weird.

Does anyone have any idea why DaylightingDevice:Tubular increases lighting power?

DaylightingDevice:Tubular Increases Lighting Power

Here are 3 idf files for a virtual office tower with different daylighting control settings. Their version is 8.9.0.

  • Case1: No daylighting control
  • Case2: Daylighting control in perimeter zonearea
  • Case3: Daylighting control in perimeter zone area and interior zone area with DaylightingDevice:Tubular

Case3 was created by adding DaylightingDevice:Tubular to Case2. However, lighting power in Case3 is higher than that in Case2. This is the problem. I don't know why.

image description

This is the 3D model. Only typical floors are modelled and multiplied. Vertical fins cover around the façade. image description

DaylightingDevice:Tubular in this model is not used in the usual way. Domes are not on the rooftop but on the wall. They are vertical. Diffusers are on the ceiling. The dome and the diffuser are not in a straight line. This system is not DaylightingDevice:Self, but more like DaylightingDevice:Tubular. Please refer to the sketch below.

image description

The increase of lighting power might be due to this unusual modelling, but I don't know what is actually not allowed in EnergyPlus.

DaylightingDevice:Tubular is in Office_N and Office_S on each floor. Perimeter area and Interior area are not separated. So, one zone has Daylighting:ReferencePoints for both exterior glazing and DaylightingDevice:Tubular. The simulation result looks as if DaylightingDevice:Tubular is offsetting the lighting power reduction in the perimeter area. It's weird.

Does anyone have any idea why DaylightingDevice:Tubular increases lighting power?


P.S.

Following Aaron's advice, I ran one more case:

  • Case4: Daylighting control in perimeter area and interior area without DaylightingDevice:Tubular

Case3 and Case4 have almost the same lighting power.

image description

Daylighting:ReferencePoint in intereior area is right under the diffuser of DaylightingDevice:Tubular, but it seems that my dome and diffuser are too small to get enough daylight.

Thus Daylighting:ReferencePoint is irrelevant. Daylighting:ReferencePoint added to interior area interferes with the original Daylighting:ReferencePoint in perimeter area. But I don't know why this happens.

DaylightingDevice:Tubular Increases Lighting Power

Here are 3 idf files for a virtual office tower with different daylighting control settings. Their version is 8.9.0.

  • Case1: No daylighting control
  • Case2: Daylighting control in perimeter area
  • Case3: Daylighting control in perimeter area and interior area with DaylightingDevice:Tubular

Case3 was created by adding DaylightingDevice:Tubular to Case2. However, lighting power in Case3 is higher than that in Case2. This is the problem. I don't know why.

image description

This is the 3D model. Only typical floors are modelled and multiplied. Vertical fins cover around the façade. image description

DaylightingDevice:Tubular in this model is not used in the usual way. Domes are not on the rooftop but on the wall. They are vertical. Diffusers are on the ceiling. The dome and the diffuser are not in a straight line. This system is not DaylightingDevice:Self, but more like DaylightingDevice:Tubular. Please refer to the sketch below.

image description

The increase of lighting power might be due to this unusual modelling, but I don't know what is actually not allowed in EnergyPlus.

DaylightingDevice:Tubular is in Office_N and Office_S on each floor. Perimeter area and Interior area are not separated. So, one zone has Daylighting:ReferencePoints for both exterior glazing and DaylightingDevice:Tubular. The simulation result looks as if DaylightingDevice:Tubular is offsetting the lighting power reduction in the perimeter area. It's weird.

Does anyone have any idea why DaylightingDevice:Tubular increases lighting power?


P.S.

Following Aaron's advice, I ran one more case:

  • Case4: Daylighting control in perimeter area and interior area without DaylightingDevice:Tubular

Case3 and Case4 have almost the same lighting power.

image description

Daylighting:ReferencePoint in intereior area is right under the diffuser of DaylightingDevice:Tubular, but it seems that my dome and diffuser are too small to get enough daylight.

Thus Daylighting:ReferencePoint is irrelevant. Daylighting:ReferencePoint added to interior area interferes with the original Daylighting:ReferencePoint in perimeter area. But I don't know why this happens.

Below is the simplified layout of Office_S. I think One thermal zone can have multiple Daylighting:ReferencePoints, and the lighting area controlled by each Daylighting:ReferencePoint is defined by Fraction of Zone controlled by Reference Point. Each daylighting control is independent. So, it does not make sense to increase lighitng power by adding Daylighting:ReferencePoint.

image description

Now, Daylighting Method is SplitFlux. I/O Reference says "Note when the DElight Daylighting Method is used, that the sum of all Reference Point control fractions must equal 1 to obtain correct overall results.", so I don't use DElight because the sum of all Reference Point control fractions in each thermal zone is less than 1 in my model.