This is a simple Yes or No question.
When we hardsizeGross Rated Total Cooling Capacity
[W] in AirConditioner:VariableRefrigerantFlow
, do Equivalent Piping Length used for Piping Correction Factor in Cooling Mode
and Vertical Height used for Piping Correction Factor
change the actual cooling capacity by correcting the hardsized Gross Rated Total Cooling Capacity
? Or are they only relevant when Gross Rated Total Cooling Capacity
is autosized?
For example, if Gross Rated Total Cooling Capacity
is 10kW and Piping Correction Factor is 0.9, is the actual cooling capacity 10kW x 0.9 = 9kW? Or is it still 10kW?
Or to rephrase my question, when we hardsize Gross Rated Total Cooling Capacity
[W] in AirConditioner:VariableRefrigerantFlow
, should we input the cooling capacity taking into account the piping correction factor in advance? If the rated total cooling capacity on VRF product catalogue is 10kW and the piping correction factor that is manually calculated is 0.9, should we input 10kW x 0.9 = 9kW to Gross Rated Total Cooling Capacity
?