How to set the cooling to zero
Hi all,
it is my first time typing here and asking for some help. I am having issues in setting the cooling to zero.
My goal is to run a simulation where in the rooms there is a heating system (simplified, i just need to understand how much heating we need to keep the internal temperature abiove a certain target) but not cooling system.
I have built my EnergyPlus model through the GH-plugins HB and LB. Therefore, i set the coolign setpoint to 100°C in order to not have any cooling. However, i have Ideal cooling Loads more than 0 and no matter what changes i do (limit flow rate or limit capacity of the cooling to 0), i still have Ideal Cooling Loads more than 0. I also tried to build it from scratch again through Zone HVAC: Zone controls and Thermostats (ZoneControl:Thermostat, ThermostatSetpoint:SingleHeating) but i wasn't able to make it work unfrotunately.
Unfortunately i have no rights (yet) to attach any .idf file since i just signed in to this forum. I'll post here below the text editor from my idf file (sorry for that).
It would be great if you can help me with this. Thanks a lot
idf text: !-Generator IDFEditor 1.50 !-Option SortedOrder
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically. !- Use '!' comments if they need to be retained when using the IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION ===========
Version, 9.2.0; !- Version Identifier
!- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
SimulationControl, Yes, !- Do Zone Sizing Calculation Yes, !- Do System Sizing Calculation Yes, !- Do Plant Sizing Calculation No, !- Run Simulation for Sizing Periods Yes; !- Run Simulation for Weather File Run Periods
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
Building, 210301_FR11_GroundTemp05m.idf, !- Name 225.0, !- North Axis {deg} City, !- Terrain , !- Loads Convergence Tolerance Value , !- Temperature Convergence Tolerance Value {deltaC} FullExterior, !- Solar Distribution 50, !- Maximum Number of Warmup Days 6; !- Minimum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
ShadowCalculation, AverageOverDaysInFrequency, !- Calculation Method 30, !- Calculation Frequency 3000; !- Maximum Figures in Shadow Overlap Calculations
!- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
Timestep, 6; !- Number of Timesteps per Hour
!- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
!Latitude !Longitude !Time Zone !Elevation Site:Location, FRANKFURT AM MAIN DEU, !- Name 50.05, !- Latitude {deg} 8.60, !- Longitude {deg} 1.0, !- Time Zone {hr} 113.0; !- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Htg 99.6% Condns DB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type -10.5, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type -10.5, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.2, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Hum_n 99.6% Condns DP=>MCDB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type -8.4, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Dewpoint, !- Humidity Condition Type -14.3, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.2, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Htg Wind 99.6% Condns WS=>MCDB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type 9.2, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 9.2, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 12.6, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns DB=>MWB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 30.8, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 19.2, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns WB=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 27.6, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 20.6, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns DP=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 22.4, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Dewpoint, !- Humidity Condition Type 18.5, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns Enth=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 27.5, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Enthalpy, !- Humidity Condition Type , !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} 59700.0, !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
!- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod, customRun, !- Name 1, !- Begin Month 1, !- Begin Day of Month , !- Begin Year 12, !- End Month 31, !- End Day of Month , !- End Year Monday, !- Day of Week for Start Day Yes, !- Use Weather File Holidays and Special Days Yes, !- Use Weather File Daylight Saving Period No, !- Apply Weekend Holiday Rule Yes, !- Use Weather File Rain Indicators Yes; !- Use Weather File Snow Indicators
!- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
Site:GroundTemperature:BuildingSurface, 5.45, !- January Ground Temperature {C} 2.69, !- February Ground Temperature {C} 1.94, !- March Ground Temperature {C} 2.59, !- April Ground Temperature {C} 6.31, !- May Ground Temperature {C} 10.48, !- June Ground Temperature {C} 14.41, !- July Ground Temperature {C} 17.25, !- August Ground Temperature {C} 18.07, !- September Ground Temperature {C} 16.74, !- October Ground Temperature {C} 13.53, !- November Ground Temperature {C} 9.48; !- December Ground Temperature {C}
!- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
ScheduleTypeLimits, ANY NUMBER; !- Name
ScheduleTypeLimits, CONTROL TYPE, !- Name 0, !- Lower Limit Value 4, !- Upper Limit Value DISCRETE; !- Numeric Type
ScheduleTypeLimits, FRACTION, !- Name 0, !- Lower Limit Value 1, !- Upper Limit Value CONTINUOUS; !- Numeric Type
ScheduleTypeLimits, ON/OFF, !- Name 0, !- Lower Limit Value 1, !- Upper Limit Value DISCRETE; !- Numeric Type
!- =========== ALL OBJECTS IN CLASS: SCHEDULE:CONSTANT ===========
Schedule:Constant, SCHOCCUPANCY, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHHEATING, !- Name ANY NUMBER, !- Schedule Type Limits Name 5.5; !- Hourly Value
Schedule:Constant, SCHLIGHTING, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHCOOLING, !- Name ANY NUMBER, !- Schedule Type Limits Name 100; !- Hourly Value
Schedule:Constant, SCHEQUIPMENT, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
Schedule:Constant, SCHACTIVITY, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHINFILTRATION, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
Schedule:Constant, SCHVENTILATION, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
!- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
Material, CONCRETE 180MM - UG, !- Name Rough, !- Roughness 0.18, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 435MM - EXTWALLUG, !- Name Rough, !- Roughness 0.435, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 800MM - UG, !- Name Rough, !- Roughness 0.8, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 300MM - EG, !- Name Rough, !- Roughness 0.3, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 200MM - EXTWALLEG, !- Name Rough, !- Roughness 0.2, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 200MM - EG, !- Name Rough, !- Roughness 0.18, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction, INTWALL_UG, !- Name CONCRETE 180MM - UG; !- Outside Layer
Construction, EXTWALL_UG, !- Name CONCRETE 435MM - EXTWALLUG; !- Outside Layer
Construction, FLOOR_UG, !- Name CONCRETE 800MM - UG; !- Outside Layer
Construction, CEILING_UG, !- Name CONCRETE 300MM - EG; !- Outside Layer
Construction, EXTWALL_EG, !- Name CONCRETE 200MM - EXTWALLEG; !- Outside Layer
Construction, INTWALL_EG, !- Name CONCRETE 200MM - EG; !- Outside Layer
Construction, FLOOR_EG, !- Name CONCRETE 300MM - EG; !- Outside Layer
Construction, CEILING_EG, !- Name CONCRETE 200MM - EG; !- Outside Layer
!- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
GlobalGeometryRules, LowerLeftCorner, !- Starting Vertex Position CounterClockWise, !- Vertex Entry Direction Relative, !- Coordinate System Relative, !- Daylighting Reference Point Coordinate System Relative; !- Rectangular Surface Coordinate System
!- =========== ALL OBJECTS IN CLASS: ZONE ===========
Zone, UG_Zone01, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone01, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone02, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone03, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
!- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
BuildingSurface:Detailed, IntWall_UG_1, !- Name WALL, !- Surface Type IntWall_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_UG_1, !- Name WALL, !- Surface Type ExtWall_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_UG_1, !- Name FLOOR, !- Surface Type Floor_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} -4.570000171661377, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} -4.570000171661377; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_UG_1, !- Name CEILING, !- Surface Type Ceiling_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_UG_2, !- Name WALL, !- Surface Type IntWall_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_UG_2, !- Name WALL, !- Surface Type ExtWall_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG01_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone01, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG01_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG01_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG01_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG01_2, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone01, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG01_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG02_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG02_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG02_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG02_2, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_3, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG03_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone03, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_2, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_2, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_3, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_3, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_3, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_4, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_4, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_4, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_5, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_5, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_5, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7048473358154297, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_6, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_6, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_6, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7298479080200195, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_7, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_8, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: SHADING:BUILDING:DETAILED ===========
Shading:Building:Detailed, shdSrf_0_0_b90a876d-2e23-4934-a1ea-eb354434a763_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 0.0, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_1_61a85451-5b8b-4da2-a0aa-7b3aa827d960_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 0.0, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_2_65a48d6a-38f6-4ebd-94b4-2d4089f42a31_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_3_4fce51dd-1182-4de6-9667-3a11345aaa38_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_4_8206864d-d9d0-49b5-ad79-0688ecf7028b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_5_336fe436-712f-4b99-b26b-dc88a2eb8a8f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} -4.570000171661377, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} -4.570000171661377; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_0_b9373496-57e1-472a-82fb-5f9845741f09_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_1_f4c8fe12-dc4f-4f60-89c0-27dbe4d501d0_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} -3.5527136788005009e-15, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} -3.5527136788005009e-15, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_2_44abf29c-6f41-4b86-a090-0204ec000324_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_3_af12752a-efdc-4550-a084-bf88bd5464c7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 7.1750001907348633, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_4_53c0d9e9-ecbb-4b98-add4-b7ce29ca881f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 51.154998779296875, !- Vertex 4 X-coordinate {m} 7.1750001907348633, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_5_82854e05-d078-457a-b6d3-630d2b17a497_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 51.154998779296875, !- Vertex 4 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_6_e7a8175f-4fd0-47c1-96ae-bb8196c406f7_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_7_6ac027da-6e91-4421-aad9-4092b6120c58_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_8_ea7aeb99-6d0a-4aaa-9a6c-e4db1d9abe94_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_9_da0a65e5-e9f6-4a68-8339-d07f4010e2f6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_10_92dd4dd0-c1ed-41be-974a-f6af061c8e14_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_11_53838df5-4d09-4505-a66b-a1d10b3ea273_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_12_ace0117f-05ff-4644-8b36-26043a284640_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_13_fd933bf3-04e0-489f-9e08-d9091ce7e424_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_0_a565cad4-7696-466b-bef4-5338da1190a5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_1_7f75496e-e51e-4dc1-8846-cc35b448b81d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 49.255001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_2_0c655ff7-337b-4157-89b3-47dd9faa64dc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 49.255001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_3_1c6e9705-c4b0-48e1-9e20-cf887328c85d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_4_fb4b0b8e-7910-4280-8b51-7c5e079ae7e2_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_5_7debdfe7-00ec-44d5-b8b3-bf65bde97f9d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.967815399169922, !- Vertex 1 X-coordinate {m} 8.026214599609375, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.973907470703125, !- Vertex 2 X-coordinate {m} 2.764657735824585, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.969338417053223, !- Vertex 3 X-coordinate {m} 3.1028683185577393, !- Vertex 3 Y-coordinate {m} 1.3250000476837158, !- Vertex 3 Z-coordinate {m} 13.96476936340332, !- Vertex 4 X-coordinate {m} 8.0821609497070313, !- Vertex 4 Y-coordinate {m} 1.3250000476837158; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_6_a491bcac-46ee-48c1-8919-0d9d4d3e4a30_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.96476936340332, !- Vertex 1 X-coordinate {m} 8.0821609497070313, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.969338417053223, !- Vertex 2 X-coordinate {m} 3.1028683185577393, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 3.4410789012908936, !- Vertex 3 Y-coordinate {m} 2.6500000953674316, !- Vertex 3 Z-coordinate {m} 13.961723327636719, !- Vertex 4 X-coordinate {m} 8.1381072998046875, !- Vertex 4 Y-coordinate {m} 2.6500000953674316; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_7_076a0715-f471-4da6-a704-99311f33a46b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.961723327636719, !- Vertex 1 X-coordinate {m} 8.1381072998046875, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 3.4410789012908936, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 3.7792894840240479, !- Vertex 3 Y-coordinate {m} 3.9749999046325684, !- Vertex 3 Z-coordinate {m} 13.958677291870117, !- Vertex 4 X-coordinate {m} 8.1940536499023438, !- Vertex 4 Y-coordinate {m} 3.9749999046325684; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_8_bd83513b-46c2-4860-86d2-5aef66afdcf7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.958677291870117, !- Vertex 1 X-coordinate {m} 8.1940536499023438, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.960200309753418, !- Vertex 2 X-coordinate {m} 3.7792894840240479, !- Vertex 2 Y-coordinate {m} 3.9749999046325684, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 4.117499828338623, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} 8.25, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_9_dc5c08d5-1e39-4a32-a07e-c3ca1c16538f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.961723327636719, !- Vertex 1 X-coordinate {m} 13.287772178649902, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.967815399169922, !- Vertex 2 X-coordinate {m} 8.026214599609375, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 8.0821609497070313, !- Vertex 3 Y-coordinate {m} 1.3250000476837158, !- Vertex 3 Z-coordinate {m} 13.960200309753418, !- Vertex 4 X-coordinate {m} 13.061454772949219, !- Vertex 4 Y-coordinate {m} 1.3250000476837158; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_10_235f4522-62c2-4404-959a-9724f1fe4907_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.960200309753418, !- Vertex 1 X-coordinate {m} 13.061454772949219, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 8.0821609497070313, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.961723327636719, !- Vertex 3 X-coordinate {m} 8.1381072998046875, !- Vertex 3 Y-coordinate {m} 2.6500000953674316, !- Vertex 3 Z-coordinate {m} 13.958677291870117, !- Vertex 4 X-coordinate {m} 12.835136413574219, !- Vertex 4 Y-coordinate {m} 2.6500000953674316; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_11_bac00d48-2b84-42ef-8679-b7578fa1e298_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.958677291870117, !- Vertex 1 X-coordinate {m} 12.835136413574219, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.961723327636719, !- Vertex 2 X-coordinate {m} 8.1381072998046875, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.958677291870117, !- Vertex 3 X-coordinate {m} 8.1940536499023438, !- Vertex 3 Y-coordinate {m} 3.9749999046325684, !- Vertex 3 Z-coordinate {m} 13.957154273986816, !- Vertex 4 X-coordinate {m} 12.608818054199219, !- Vertex 4 Y-coordinate {m} 3.9749999046325684; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_12_1cfe46be-24de-4f46-a1bc-9a11039364d6_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.957154273986816, !- Vertex 1 X-coordinate {m} 12.608818054199219, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 8.1940536499023438, !- Vertex 2 Y-coordinate {m} 3.9749999046325684, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 8.25, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} 12.382499694824219, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_13_4cc69a79-0c2b-4269-b7bd-722f16b80459_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.973907470703125, !- Vertex 1 X-coordinate {m} 2.764657735824585, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.969338417053223, !- Vertex 3 X-coordinate {m} 3.1028683185577393, !- Vertex 3 Y-coordinate {m} 1.3250000476837158; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_14_d2d2ea8a-85a7-4789-86d1-226a31a70bb6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.969338417053223, !- Vertex 1 X-coordinate {m} 3.1028683185577393, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 3.4410789012908936, !- Vertex 3 Y-coordinate {m} 2.6500000953674316; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_15_b67951ff-92e3-4513-98d9-95cea6345df1_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.96476936340332, !- Vertex 1 X-coordinate {m} 3.4410789012908936, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 3.7792894840240479, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_16_38547ea7-d3a3-4e57-a05b-5e41d5ad9c19_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 3.4410789012908936, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.977126121520996, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_17_6992fc54-63f5-4e09-904b-5db8fcdae939_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.960200309753418, !- Vertex 1 X-coordinate {m} 3.7792894840240479, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 4.117499828338623, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_18_8f733456-7cf6-48f6-b398-36636495e5f2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.961723327636719, !- Vertex 2 X-coordinate {m} 13.287772178649902, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 13.061454772949219, !- Vertex 3 Y-coordinate {m} 1.3250000476837158; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_19_b1ec1831-0ed1-482d-9492-68efbf8c764f_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.960200309753418, !- Vertex 2 X-coordinate {m} 13.061454772949219, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.958677291870117, !- Vertex 3 X-coordinate {m} 12.835136413574219, !- Vertex 3 Y-coordinate {m} 2.6500000953674316; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_20_a7a4b53e-cae4-4418-9065-7946503726fa_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 12.835136413574219, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.957154273986816, !- Vertex 3 X-coordinate {m} 12.608818054199219, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_21_3f4d7947-636f-407f-9171-cb42592b625d_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} 12.382499694824219, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957154273986816, !- Vertex 3 X-coordinate {m} 12.608818054199219, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_22_e48cadd0-e70c-43fb-8039-fda0f52fbbf1_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 12.835136413574219, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_23_e98b88ff-407f-4956-a8b1-8035e91f6bd5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_24_83269d7a-846b-47ca-9c56-75575ee7adc6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_25_36208d9b-d68b-4a7a-954c-e3a4c743cb90_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_26_77821171-aba9-4a4a-8a4f-347b558ac565_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_27_b17f340a-e067-45d9-a99a-6b3d57078d2b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_28_0d30e11a-d33c-460c-8d7a-4236559abe1b_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_29_24e92e9a-4769-4d2e-9279-67d598da5a34_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_30_5ac8c1c6-4653-499e-8ca8-b322c322a218_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_0_50cd95d4-796e-4486-b3c5-f4a4d7f2f72c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.977126121520996, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_1_51c1f489-9a93-421e-9c78-24dc799c7f4c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.957986831665039, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_2_30fa3315-9af2-4d20-a2c5-a81664d9ed22_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_3_3fda03af-0456-4ff2-b358-222970cc561e_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_4_364028f6-aa05-4f9b-ab75-12e585aa18bc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7298479080200195, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_5_a5ded2b1-3daa-40ee-ad8b-39acab6a8d87_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7048473358154297, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_6_160435f8-a0e0-47f1-b4b9-55ce70aa1bbd_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_7_4b5248a5-a8bf-4d87-97fe-e3479c429aca_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_8_6a8078f2-cb25-4061-98a8-bb0d61f99e83_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_9_36fc718f-17d1-4371-8a0a-b40ad92729da_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_10_28945240-f8df-4b20-abb5-7b7f663f9ea9_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_11_fc3b1151-1785-448b-9d81-7e99743e1fb7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.977126121520996, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_12_8172805a-ce12-4a87-b024-b5e9891f79d7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.963973045349121, !- Vertex 4 X-coordinate {m} 11.34501838684082, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_13_cd93ae0b-5339-4df0-9eac-ff39486c4e37_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_14_00c7580a-62cd-4271-a367-bbbfb04ddc6b_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_15_fde1954c-a04d-45c2-8152-70875b961313_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_16_f624c1a8-8021-4904-b703-aa2217ed83e4_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_17_ad6b4178-2572-4015-baf8-55eb9eeea5f0_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.977126121520996, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_18_35f42890-34cf-40f7-b3b6-068a3aaf19b2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_19_f6ce5cde-7c2d-4184-9a81-89f6cbf53aa0_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_20_7816c1be-ee7e-4044-9315-9eb2a5962961_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_21_3024da7a-129f-47b4-a264-d7e5eb92378f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_22_570fb345-ae26-4b06-86a1-204d71dd946c_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_23_f55e016d-6454-4b47-888e-ee482ed12598_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_24_6109f30e-2829-4538-b144-9641ccbd4be8_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_25_cace7993-5ef0-4ee4-9e2d-5ca3394d82b2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.972288131713867, !- Vertex 2 X-coordinate {m} 4.1631946563720703, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_26_d6406774-0179-4d8b-bf92-0960ce0d2845_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_27_2122136b-f823-47a6-a3cf-6fe75a375bbe_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_28_07ddcdfa-94f0-412c-97a3-70a71ef597f3_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_29_6af74ada-6427-45ff-8e6a-74a0beb265a2_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_0_a9053094-dffd-4b86-b5f8-7aa0d1b2ee0f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_1_3b286971-2df9-46fe-83ea-fadc1d7a256c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} -0.016832431778311729, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_2_988d1371-0f44-42ff-bc2f-a8bd9ea9d298_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} -0.016832431778311729, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} -0.016832431778311729, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_3_2fbf6dce-05be-47ce-afd2-bd47a4d85e22_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2671480178833008, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2671480178833008, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_4_c9f7830e-e37b-4160-8852-270d4339719c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2771472930908203, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2671480178833008, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_5_1bce5418-be13-4afe-a4a9-dfbd563a48b5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2771472930908203, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_6_48643cd9-1800-44d5-a5d9-314a966a3417_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 16.504999160766602, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 16.504999160766602, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_7_6e858d40-f744-4070-b056-c36ef4841659_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_8_949ccf11-f412-4f96-ba5e-1d218879ad7c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.2672653198242188, !- Vertex 4 X-coordinate {m} -0.016697768121957779, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_9_5bcbe1e7-61af-4e29-8f7a-3274b142686b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.3805017471313477, !- Vertex 4 X-coordinate {m} -0.016649600118398666, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_10_d10900c2-33e0-4089-8e4d-cae912fce5ea_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_11_fbd92c75-eeb6-431a-98bb-7df3422f2e63_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_12_5a355612-a5c5-4624-8329-705b8529d4d7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2672653198242188, !- Vertex 2 X-coordinate {m} -0.016697768121957779, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_13_d9ed9515-6d03-44f9-b9ed-0e22fa0382ad_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.3805017471313477, !- Vertex 2 X-coordinate {m} -0.016649600118398666, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_14_7af53846-d7fe-4422-a6a3-f9516a020c51_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_15_b2bdc37c-1087-4fc0-b6a2-927e9efd517c_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_0_4e591051-a95d-4e49-924a-c8d59bbefcb8_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_1_314e7a4c-e090-432e-be71-52749debe10f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} -0.016832431778311729, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_2_980a8946-eea9-4469-b55e-2ee09622c978_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} -0.016832431778311729, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} -0.016832431778311729, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_3_8e86b00d-9e5a-4a52-a340-09766dc2aac5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2671480178833008, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2671480178833008, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_4_41702fcb-6814-4436-8473-64b701e90871_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2771472930908203, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2671480178833008, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_5_1aadecd6-4623-48f2-9231-1c0569dc78bc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2771472930908203, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_6_f9c1ac16-78bf-4353-9bc9-676cba406345_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 16.504999160766602, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 16.504999160766602, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_7_068e3425-25c8-47a0-84a5-c8fc4c4098c9_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_8_b35af553-3780-401d-9a79-9596cdacbf76_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2672653198242188, !- Vertex 4 X-coordinate {m} -0.016697768121957779, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_9_be36059b-ffa9-452b-8024-eb731a39fe3d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.3805017471313477, !- Vertex 4 X-coordinate {m} -0.016649600118398666, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_10_040e1c7f-a6df-4be2-bd6b-948e6da430ac_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_11_261295b7-ffcf-43e1-af45-814576e17fcf_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_12_64186e1c-dfef-4dd6-b591-ef511d8bcfcf_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 8.2672653198242188, !- Vertex 2 X-coordinate {m} -0.016697768121957779, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_13_a207b346-a146-464a-ba6a-83fc1749e66b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 9.3805017471313477, !- Vertex 2 X-coordinate {m} -0.016649600118398666, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_14_18a3f056-cde8-4330-8ae9-c5fc00829a07_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 15.899999618530273; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_15_b90da5e0-8243-4e38-a260-24ad049d600a_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 15.899999618530273; !- Vertex 3 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: PEOPLE ===========
People, EG_Zone03OfficePeople, !- Name EG_Zone03, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, UG_Zone01OfficePeople, !- Name UG_Zone01, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, EG_Zone01OfficePeople, !- Name EG_Zone01, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, EG_Zone02OfficePeople, !- Name EG_Zone02, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
!- =========== ALL OBJECTS IN CLASS: LIGHTS ===========
Lights, EG_Zone03OfficeLights, !- Name EG_Zone03, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, UG_Zone01OfficeLights, !- Name UG_Zone01, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, EG_Zone01OfficeLights, !- Name EG_Zone01, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, EG_Zone02OfficeLights, !- Name EG_Zone02, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
!- =========== ALL OBJECTS IN CLASS: ELECTRICEQUIPMENT ===========
ElectricEquipment, EG_Zone03ElectricEquipment, !- Name EG_Zone03, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, UG_Zone01ElectricEquipment, !- Name UG_Zone01, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, EG_Zone01ElectricEquipment, !- Name EG_Zone01, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, EG_Zone02ElectricEquipment, !- Name EG_Zone02, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
!- =========== ALL OBJECTS IN CLASS: ZONEINFILTRATION:DESIGNFLOWRATE ===========
ZoneInfiltration:DesignFlowRate, EG_Zone03_Infiltration, !- Name EG_Zone03, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 0.0001613944288326255, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, UG_Zone01_Infiltration, !- Name UG_Zone01, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 0.0, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, EG_Zone01_Infiltration, !- Name EG_Zone01, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 6.6422764229751539e-05, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, EG_Zone02_Infiltration, !- Name EG_Zone02, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 5.0124372093330299e-05, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:THERMOSTAT ===========
HVACTemplate:Thermostat, EG_Zone03_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, UG_Zone01_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, EG_Zone01_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, EG_Zone02_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:IDEALLOADSAIRSYSTEM ===========
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone03, !- Zone Name EG_Zone03_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone03OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, UG_Zone01, !- Zone Name UG_Zone01_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} UG_Zone01OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone01, !- Zone Name EG_Zone01_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone01OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone02, !- Zone Name EG_Zone02_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone02OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
!- =========== ALL OBJECTS IN CLASS: DESIGNSPECIFICATION:OUTDOORAIR ===========
DesignSpecification:OutdoorAir, EG_Zone03OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444414, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, UG_Zone01OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.00044430555555555532, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, EG_Zone01OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444483, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, EG_Zone02OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444435, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
!- =========== ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========
Sizing:Parameters, 1.25, !- Heating Sizing Factor 1.15; !- Cooling Sizing Factor
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========
Output:VariableDictionary, regular; !- Key Field
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:LIST ===========
Output:Surfaces:List, Details; !- Report Type
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
Output:Surfaces:Drawing, DXF, !- Report Type Triangulate3DFace; !- Report Specifications 1
!- =========== ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
Output:Table:SummaryReports, AllSummary; !- Report 1 Name
!- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
OutputControl:Table:Style, CommaAndHTML, !- Column Separator JtoKWH; !- Unit Conversion
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
Output:Variable, *, !- Key Value Zone Operative Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Outdoor Air Drybulb Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mechanical Ventilation Air Changes per Hour, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Infiltration Air Change Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Ideal Loads Zone Total Cooling Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Ideal Loads Zone Total Heating Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mean Air Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mean Radiant Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Electric Equipment Total Heating Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Ground Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Deep Ground Temperature, !- Variable Name hourly; !- Reporting Frequency
How to set the cooling to zero
Hi all,
it is my first time typing here and asking for some help. I am having issues in setting the cooling to zero.
My goal is to run a simulation where in the rooms there is a heating system (simplified, i just need to understand how much heating we need to keep the internal temperature abiove a certain target) but not cooling system.
I have built my EnergyPlus model through the GH-plugins HB and LB. Therefore, i set the coolign setpoint to 100°C in order to not have any cooling. However, i have Ideal cooling Loads more than 0 and no matter what changes i do (limit flow rate or limit capacity of the cooling to 0), i still have Ideal Cooling Loads more than 0. I also tried to build it from scratch again through Zone HVAC: Zone controls and Thermostats (ZoneControl:Thermostat, ThermostatSetpoint:SingleHeating) but i wasn't able to make it work unfrotunately.
Unfortunately i have no rights (yet) to attach any .idf file since i just signed in to this forum. I'll post here below the text editor from my idf file (sorry for that).
It would be great if you can help me with this. Thanks a lot
idf text: !-Generator IDFEditor 1.50 !-Option SortedOrder
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically. !- Use '!' comments if they need to be retained when using the IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION ===========
Version, 9.2.0; !- Version Identifier
!- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
SimulationControl, Yes, !- Do Zone Sizing Calculation Yes, !- Do System Sizing Calculation Yes, !- Do Plant Sizing Calculation No, !- Run Simulation for Sizing Periods Yes; !- Run Simulation for Weather File Run Periods
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
Building, 210301_FR11_GroundTemp05m.idf, !- Name 225.0, !- North Axis {deg} City, !- Terrain , !- Loads Convergence Tolerance Value , !- Temperature Convergence Tolerance Value {deltaC} FullExterior, !- Solar Distribution 50, !- Maximum Number of Warmup Days 6; !- Minimum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
ShadowCalculation, AverageOverDaysInFrequency, !- Calculation Method 30, !- Calculation Frequency 3000; !- Maximum Figures in Shadow Overlap Calculations
!- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
Timestep, 6; !- Number of Timesteps per Hour
!- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
!Latitude !Longitude !Time Zone !Elevation Site:Location, FRANKFURT AM MAIN DEU, !- Name 50.05, !- Latitude {deg} 8.60, !- Longitude {deg} 1.0, !- Time Zone {hr} 113.0; !- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Htg 99.6% Condns DB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type -10.5, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type -10.5, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.2, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Hum_n 99.6% Condns DP=>MCDB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type -8.4, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Dewpoint, !- Humidity Condition Type -14.3, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.2, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Htg Wind 99.6% Condns WS=>MCDB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type 9.2, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 9.2, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 12.6, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns DB=>MWB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 30.8, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 19.2, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns WB=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 27.6, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 20.6, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns DP=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 22.4, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Dewpoint, !- Humidity Condition Type 18.5, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns Enth=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 27.5, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Enthalpy, !- Humidity Condition Type , !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} 59700.0, !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
!- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod, customRun, !- Name 1, !- Begin Month 1, !- Begin Day of Month , !- Begin Year 12, !- End Month 31, !- End Day of Month , !- End Year Monday, !- Day of Week for Start Day Yes, !- Use Weather File Holidays and Special Days Yes, !- Use Weather File Daylight Saving Period No, !- Apply Weekend Holiday Rule Yes, !- Use Weather File Rain Indicators Yes; !- Use Weather File Snow Indicators
!- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
Site:GroundTemperature:BuildingSurface, 5.45, !- January Ground Temperature {C} 2.69, !- February Ground Temperature {C} 1.94, !- March Ground Temperature {C} 2.59, !- April Ground Temperature {C} 6.31, !- May Ground Temperature {C} 10.48, !- June Ground Temperature {C} 14.41, !- July Ground Temperature {C} 17.25, !- August Ground Temperature {C} 18.07, !- September Ground Temperature {C} 16.74, !- October Ground Temperature {C} 13.53, !- November Ground Temperature {C} 9.48; !- December Ground Temperature {C}
!- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
ScheduleTypeLimits, ANY NUMBER; !- Name
ScheduleTypeLimits, CONTROL TYPE, !- Name 0, !- Lower Limit Value 4, !- Upper Limit Value DISCRETE; !- Numeric Type
ScheduleTypeLimits, FRACTION, !- Name 0, !- Lower Limit Value 1, !- Upper Limit Value CONTINUOUS; !- Numeric Type
ScheduleTypeLimits, ON/OFF, !- Name 0, !- Lower Limit Value 1, !- Upper Limit Value DISCRETE; !- Numeric Type
!- =========== ALL OBJECTS IN CLASS: SCHEDULE:CONSTANT ===========
Schedule:Constant, SCHOCCUPANCY, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHHEATING, !- Name ANY NUMBER, !- Schedule Type Limits Name 5.5; !- Hourly Value
Schedule:Constant, SCHLIGHTING, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHCOOLING, !- Name ANY NUMBER, !- Schedule Type Limits Name 100; !- Hourly Value
Schedule:Constant, SCHEQUIPMENT, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
Schedule:Constant, SCHACTIVITY, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHINFILTRATION, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
Schedule:Constant, SCHVENTILATION, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
!- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
Material, CONCRETE 180MM - UG, !- Name Rough, !- Roughness 0.18, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 435MM - EXTWALLUG, !- Name Rough, !- Roughness 0.435, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 800MM - UG, !- Name Rough, !- Roughness 0.8, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 300MM - EG, !- Name Rough, !- Roughness 0.3, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 200MM - EXTWALLEG, !- Name Rough, !- Roughness 0.2, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 200MM - EG, !- Name Rough, !- Roughness 0.18, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction, INTWALL_UG, !- Name CONCRETE 180MM - UG; !- Outside Layer
Construction, EXTWALL_UG, !- Name CONCRETE 435MM - EXTWALLUG; !- Outside Layer
Construction, FLOOR_UG, !- Name CONCRETE 800MM - UG; !- Outside Layer
Construction, CEILING_UG, !- Name CONCRETE 300MM - EG; !- Outside Layer
Construction, EXTWALL_EG, !- Name CONCRETE 200MM - EXTWALLEG; !- Outside Layer
Construction, INTWALL_EG, !- Name CONCRETE 200MM - EG; !- Outside Layer
Construction, FLOOR_EG, !- Name CONCRETE 300MM - EG; !- Outside Layer
Construction, CEILING_EG, !- Name CONCRETE 200MM - EG; !- Outside Layer
!- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
GlobalGeometryRules, LowerLeftCorner, !- Starting Vertex Position CounterClockWise, !- Vertex Entry Direction Relative, !- Coordinate System Relative, !- Daylighting Reference Point Coordinate System Relative; !- Rectangular Surface Coordinate System
!- =========== ALL OBJECTS IN CLASS: ZONE ===========
Zone, UG_Zone01, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone01, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone02, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone03, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
!- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
BuildingSurface:Detailed, IntWall_UG_1, !- Name WALL, !- Surface Type IntWall_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_UG_1, !- Name WALL, !- Surface Type ExtWall_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_UG_1, !- Name FLOOR, !- Surface Type Floor_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} -4.570000171661377, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} -4.570000171661377; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_UG_1, !- Name CEILING, !- Surface Type Ceiling_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_UG_2, !- Name WALL, !- Surface Type IntWall_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_UG_2, !- Name WALL, !- Surface Type ExtWall_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG01_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone01, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG01_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG01_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG01_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG01_2, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone01, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG01_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG02_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG02_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG02_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG02_2, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_3, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG03_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone03, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_2, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_2, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_3, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_3, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_3, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_4, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_4, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_4, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_5, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_5, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_5, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7048473358154297, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_6, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_6, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_6, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7298479080200195, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_7, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_8, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: SHADING:BUILDING:DETAILED ===========
Shading:Building:Detailed, shdSrf_0_0_b90a876d-2e23-4934-a1ea-eb354434a763_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 0.0, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_1_61a85451-5b8b-4da2-a0aa-7b3aa827d960_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 0.0, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_2_65a48d6a-38f6-4ebd-94b4-2d4089f42a31_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_3_4fce51dd-1182-4de6-9667-3a11345aaa38_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_4_8206864d-d9d0-49b5-ad79-0688ecf7028b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_5_336fe436-712f-4b99-b26b-dc88a2eb8a8f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} -4.570000171661377, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} -4.570000171661377; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_0_b9373496-57e1-472a-82fb-5f9845741f09_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_1_f4c8fe12-dc4f-4f60-89c0-27dbe4d501d0_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} -3.5527136788005009e-15, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} -3.5527136788005009e-15, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_2_44abf29c-6f41-4b86-a090-0204ec000324_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_3_af12752a-efdc-4550-a084-bf88bd5464c7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 7.1750001907348633, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_4_53c0d9e9-ecbb-4b98-add4-b7ce29ca881f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 51.154998779296875, !- Vertex 4 X-coordinate {m} 7.1750001907348633, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_5_82854e05-d078-457a-b6d3-630d2b17a497_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 51.154998779296875, !- Vertex 4 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_6_e7a8175f-4fd0-47c1-96ae-bb8196c406f7_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_7_6ac027da-6e91-4421-aad9-4092b6120c58_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_8_ea7aeb99-6d0a-4aaa-9a6c-e4db1d9abe94_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_9_da0a65e5-e9f6-4a68-8339-d07f4010e2f6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_10_92dd4dd0-c1ed-41be-974a-f6af061c8e14_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_11_53838df5-4d09-4505-a66b-a1d10b3ea273_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_12_ace0117f-05ff-4644-8b36-26043a284640_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_13_fd933bf3-04e0-489f-9e08-d9091ce7e424_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_0_a565cad4-7696-466b-bef4-5338da1190a5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_1_7f75496e-e51e-4dc1-8846-cc35b448b81d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 49.255001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_2_0c655ff7-337b-4157-89b3-47dd9faa64dc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 49.255001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_3_1c6e9705-c4b0-48e1-9e20-cf887328c85d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_4_fb4b0b8e-7910-4280-8b51-7c5e079ae7e2_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_5_7debdfe7-00ec-44d5-b8b3-bf65bde97f9d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.967815399169922, !- Vertex 1 X-coordinate {m} 8.026214599609375, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.973907470703125, !- Vertex 2 X-coordinate {m} 2.764657735824585, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.969338417053223, !- Vertex 3 X-coordinate {m} 3.1028683185577393, !- Vertex 3 Y-coordinate {m} 1.3250000476837158, !- Vertex 3 Z-coordinate {m} 13.96476936340332, !- Vertex 4 X-coordinate {m} 8.0821609497070313, !- Vertex 4 Y-coordinate {m} 1.3250000476837158; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_6_a491bcac-46ee-48c1-8919-0d9d4d3e4a30_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.96476936340332, !- Vertex 1 X-coordinate {m} 8.0821609497070313, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.969338417053223, !- Vertex 2 X-coordinate {m} 3.1028683185577393, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 3.4410789012908936, !- Vertex 3 Y-coordinate {m} 2.6500000953674316, !- Vertex 3 Z-coordinate {m} 13.961723327636719, !- Vertex 4 X-coordinate {m} 8.1381072998046875, !- Vertex 4 Y-coordinate {m} 2.6500000953674316; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_7_076a0715-f471-4da6-a704-99311f33a46b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.961723327636719, !- Vertex 1 X-coordinate {m} 8.1381072998046875, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 3.4410789012908936, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 3.7792894840240479, !- Vertex 3 Y-coordinate {m} 3.9749999046325684, !- Vertex 3 Z-coordinate {m} 13.958677291870117, !- Vertex 4 X-coordinate {m} 8.1940536499023438, !- Vertex 4 Y-coordinate {m} 3.9749999046325684; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_8_bd83513b-46c2-4860-86d2-5aef66afdcf7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.958677291870117, !- Vertex 1 X-coordinate {m} 8.1940536499023438, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.960200309753418, !- Vertex 2 X-coordinate {m} 3.7792894840240479, !- Vertex 2 Y-coordinate {m} 3.9749999046325684, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 4.117499828338623, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} 8.25, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_9_dc5c08d5-1e39-4a32-a07e-c3ca1c16538f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.961723327636719, !- Vertex 1 X-coordinate {m} 13.287772178649902, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.967815399169922, !- Vertex 2 X-coordinate {m} 8.026214599609375, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 8.0821609497070313, !- Vertex 3 Y-coordinate {m} 1.3250000476837158, !- Vertex 3 Z-coordinate {m} 13.960200309753418, !- Vertex 4 X-coordinate {m} 13.061454772949219, !- Vertex 4 Y-coordinate {m} 1.3250000476837158; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_10_235f4522-62c2-4404-959a-9724f1fe4907_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.960200309753418, !- Vertex 1 X-coordinate {m} 13.061454772949219, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 8.0821609497070313, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.961723327636719, !- Vertex 3 X-coordinate {m} 8.1381072998046875, !- Vertex 3 Y-coordinate {m} 2.6500000953674316, !- Vertex 3 Z-coordinate {m} 13.958677291870117, !- Vertex 4 X-coordinate {m} 12.835136413574219, !- Vertex 4 Y-coordinate {m} 2.6500000953674316; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_11_bac00d48-2b84-42ef-8679-b7578fa1e298_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.958677291870117, !- Vertex 1 X-coordinate {m} 12.835136413574219, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.961723327636719, !- Vertex 2 X-coordinate {m} 8.1381072998046875, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.958677291870117, !- Vertex 3 X-coordinate {m} 8.1940536499023438, !- Vertex 3 Y-coordinate {m} 3.9749999046325684, !- Vertex 3 Z-coordinate {m} 13.957154273986816, !- Vertex 4 X-coordinate {m} 12.608818054199219, !- Vertex 4 Y-coordinate {m} 3.9749999046325684; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_12_1cfe46be-24de-4f46-a1bc-9a11039364d6_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.957154273986816, !- Vertex 1 X-coordinate {m} 12.608818054199219, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 8.1940536499023438, !- Vertex 2 Y-coordinate {m} 3.9749999046325684, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 8.25, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} 12.382499694824219, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_13_4cc69a79-0c2b-4269-b7bd-722f16b80459_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.973907470703125, !- Vertex 1 X-coordinate {m} 2.764657735824585, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.969338417053223, !- Vertex 3 X-coordinate {m} 3.1028683185577393, !- Vertex 3 Y-coordinate {m} 1.3250000476837158; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_14_d2d2ea8a-85a7-4789-86d1-226a31a70bb6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.969338417053223, !- Vertex 1 X-coordinate {m} 3.1028683185577393, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 3.4410789012908936, !- Vertex 3 Y-coordinate {m} 2.6500000953674316; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_15_b67951ff-92e3-4513-98d9-95cea6345df1_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.96476936340332, !- Vertex 1 X-coordinate {m} 3.4410789012908936, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 3.7792894840240479, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_16_38547ea7-d3a3-4e57-a05b-5e41d5ad9c19_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 3.4410789012908936, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.977126121520996, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_17_6992fc54-63f5-4e09-904b-5db8fcdae939_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.960200309753418, !- Vertex 1 X-coordinate {m} 3.7792894840240479, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 4.117499828338623, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_18_8f733456-7cf6-48f6-b398-36636495e5f2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.961723327636719, !- Vertex 2 X-coordinate {m} 13.287772178649902, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 13.061454772949219, !- Vertex 3 Y-coordinate {m} 1.3250000476837158; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_19_b1ec1831-0ed1-482d-9492-68efbf8c764f_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.960200309753418, !- Vertex 2 X-coordinate {m} 13.061454772949219, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.958677291870117, !- Vertex 3 X-coordinate {m} 12.835136413574219, !- Vertex 3 Y-coordinate {m} 2.6500000953674316; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_20_a7a4b53e-cae4-4418-9065-7946503726fa_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 12.835136413574219, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.957154273986816, !- Vertex 3 X-coordinate {m} 12.608818054199219, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_21_3f4d7947-636f-407f-9171-cb42592b625d_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} 12.382499694824219, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957154273986816, !- Vertex 3 X-coordinate {m} 12.608818054199219, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_22_e48cadd0-e70c-43fb-8039-fda0f52fbbf1_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 12.835136413574219, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_23_e98b88ff-407f-4956-a8b1-8035e91f6bd5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_24_83269d7a-846b-47ca-9c56-75575ee7adc6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_25_36208d9b-d68b-4a7a-954c-e3a4c743cb90_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_26_77821171-aba9-4a4a-8a4f-347b558ac565_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_27_b17f340a-e067-45d9-a99a-6b3d57078d2b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_28_0d30e11a-d33c-460c-8d7a-4236559abe1b_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_29_24e92e9a-4769-4d2e-9279-67d598da5a34_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_30_5ac8c1c6-4653-499e-8ca8-b322c322a218_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_0_50cd95d4-796e-4486-b3c5-f4a4d7f2f72c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.977126121520996, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_1_51c1f489-9a93-421e-9c78-24dc799c7f4c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.957986831665039, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_2_30fa3315-9af2-4d20-a2c5-a81664d9ed22_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_3_3fda03af-0456-4ff2-b358-222970cc561e_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_4_364028f6-aa05-4f9b-ab75-12e585aa18bc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7298479080200195, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_5_a5ded2b1-3daa-40ee-ad8b-39acab6a8d87_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7048473358154297, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_6_160435f8-a0e0-47f1-b4b9-55ce70aa1bbd_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_7_4b5248a5-a8bf-4d87-97fe-e3479c429aca_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_8_6a8078f2-cb25-4061-98a8-bb0d61f99e83_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_9_36fc718f-17d1-4371-8a0a-b40ad92729da_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_10_28945240-f8df-4b20-abb5-7b7f663f9ea9_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_11_fc3b1151-1785-448b-9d81-7e99743e1fb7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.977126121520996, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_12_8172805a-ce12-4a87-b024-b5e9891f79d7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.963973045349121, !- Vertex 4 X-coordinate {m} 11.34501838684082, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_13_cd93ae0b-5339-4df0-9eac-ff39486c4e37_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_14_00c7580a-62cd-4271-a367-bbbfb04ddc6b_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_15_fde1954c-a04d-45c2-8152-70875b961313_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_16_f624c1a8-8021-4904-b703-aa2217ed83e4_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_17_ad6b4178-2572-4015-baf8-55eb9eeea5f0_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.977126121520996, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_18_35f42890-34cf-40f7-b3b6-068a3aaf19b2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_19_f6ce5cde-7c2d-4184-9a81-89f6cbf53aa0_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_20_7816c1be-ee7e-4044-9315-9eb2a5962961_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_21_3024da7a-129f-47b4-a264-d7e5eb92378f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_22_570fb345-ae26-4b06-86a1-204d71dd946c_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_23_f55e016d-6454-4b47-888e-ee482ed12598_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_24_6109f30e-2829-4538-b144-9641ccbd4be8_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_25_cace7993-5ef0-4ee4-9e2d-5ca3394d82b2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.972288131713867, !- Vertex 2 X-coordinate {m} 4.1631946563720703, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_26_d6406774-0179-4d8b-bf92-0960ce0d2845_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_27_2122136b-f823-47a6-a3cf-6fe75a375bbe_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_28_07ddcdfa-94f0-412c-97a3-70a71ef597f3_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_29_6af74ada-6427-45ff-8e6a-74a0beb265a2_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_0_a9053094-dffd-4b86-b5f8-7aa0d1b2ee0f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_1_3b286971-2df9-46fe-83ea-fadc1d7a256c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} -0.016832431778311729, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_2_988d1371-0f44-42ff-bc2f-a8bd9ea9d298_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} -0.016832431778311729, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} -0.016832431778311729, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_3_2fbf6dce-05be-47ce-afd2-bd47a4d85e22_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2671480178833008, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2671480178833008, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_4_c9f7830e-e37b-4160-8852-270d4339719c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2771472930908203, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2671480178833008, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_5_1bce5418-be13-4afe-a4a9-dfbd563a48b5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2771472930908203, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_6_48643cd9-1800-44d5-a5d9-314a966a3417_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 16.504999160766602, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 16.504999160766602, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_7_6e858d40-f744-4070-b056-c36ef4841659_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_8_949ccf11-f412-4f96-ba5e-1d218879ad7c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.2672653198242188, !- Vertex 4 X-coordinate {m} -0.016697768121957779, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_9_5bcbe1e7-61af-4e29-8f7a-3274b142686b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.3805017471313477, !- Vertex 4 X-coordinate {m} -0.016649600118398666, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_10_d10900c2-33e0-4089-8e4d-cae912fce5ea_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_11_fbd92c75-eeb6-431a-98bb-7df3422f2e63_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_12_5a355612-a5c5-4624-8329-705b8529d4d7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2672653198242188, !- Vertex 2 X-coordinate {m} -0.016697768121957779, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_13_d9ed9515-6d03-44f9-b9ed-0e22fa0382ad_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.3805017471313477, !- Vertex 2 X-coordinate {m} -0.016649600118398666, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_14_7af53846-d7fe-4422-a6a3-f9516a020c51_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_15_b2bdc37c-1087-4fc0-b6a2-927e9efd517c_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_0_4e591051-a95d-4e49-924a-c8d59bbefcb8_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_1_314e7a4c-e090-432e-be71-52749debe10f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} -0.016832431778311729, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_2_980a8946-eea9-4469-b55e-2ee09622c978_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} -0.016832431778311729, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} -0.016832431778311729, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_3_8e86b00d-9e5a-4a52-a340-09766dc2aac5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2671480178833008, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2671480178833008, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_4_41702fcb-6814-4436-8473-64b701e90871_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2771472930908203, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2671480178833008, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_5_1aadecd6-4623-48f2-9231-1c0569dc78bc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2771472930908203, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_6_f9c1ac16-78bf-4353-9bc9-676cba406345_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 16.504999160766602, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 16.504999160766602, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_7_068e3425-25c8-47a0-84a5-c8fc4c4098c9_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_8_b35af553-3780-401d-9a79-9596cdacbf76_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2672653198242188, !- Vertex 4 X-coordinate {m} -0.016697768121957779, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_9_be36059b-ffa9-452b-8024-eb731a39fe3d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.3805017471313477, !- Vertex 4 X-coordinate {m} -0.016649600118398666, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_10_040e1c7f-a6df-4be2-bd6b-948e6da430ac_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_11_261295b7-ffcf-43e1-af45-814576e17fcf_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_12_64186e1c-dfef-4dd6-b591-ef511d8bcfcf_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 8.2672653198242188, !- Vertex 2 X-coordinate {m} -0.016697768121957779, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_13_a207b346-a146-464a-ba6a-83fc1749e66b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 9.3805017471313477, !- Vertex 2 X-coordinate {m} -0.016649600118398666, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_14_18a3f056-cde8-4330-8ae9-c5fc00829a07_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 15.899999618530273; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_15_b90da5e0-8243-4e38-a260-24ad049d600a_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 15.899999618530273; !- Vertex 3 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: PEOPLE ===========
People, EG_Zone03OfficePeople, !- Name EG_Zone03, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, UG_Zone01OfficePeople, !- Name UG_Zone01, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, EG_Zone01OfficePeople, !- Name EG_Zone01, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, EG_Zone02OfficePeople, !- Name EG_Zone02, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
!- =========== ALL OBJECTS IN CLASS: LIGHTS ===========
Lights, EG_Zone03OfficeLights, !- Name EG_Zone03, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, UG_Zone01OfficeLights, !- Name UG_Zone01, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, EG_Zone01OfficeLights, !- Name EG_Zone01, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, EG_Zone02OfficeLights, !- Name EG_Zone02, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
!- =========== ALL OBJECTS IN CLASS: ELECTRICEQUIPMENT ===========
ElectricEquipment, EG_Zone03ElectricEquipment, !- Name EG_Zone03, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, UG_Zone01ElectricEquipment, !- Name UG_Zone01, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, EG_Zone01ElectricEquipment, !- Name EG_Zone01, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, EG_Zone02ElectricEquipment, !- Name EG_Zone02, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
!- =========== ALL OBJECTS IN CLASS: ZONEINFILTRATION:DESIGNFLOWRATE ===========
ZoneInfiltration:DesignFlowRate, EG_Zone03_Infiltration, !- Name EG_Zone03, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 0.0001613944288326255, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, UG_Zone01_Infiltration, !- Name UG_Zone01, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 0.0, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, EG_Zone01_Infiltration, !- Name EG_Zone01, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 6.6422764229751539e-05, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, EG_Zone02_Infiltration, !- Name EG_Zone02, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 5.0124372093330299e-05, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:THERMOSTAT ===========
HVACTemplate:Thermostat, EG_Zone03_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, UG_Zone01_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, EG_Zone01_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, EG_Zone02_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:IDEALLOADSAIRSYSTEM ===========
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone03, !- Zone Name EG_Zone03_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone03OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, UG_Zone01, !- Zone Name UG_Zone01_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} UG_Zone01OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone01, !- Zone Name EG_Zone01_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone01OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone02, !- Zone Name EG_Zone02_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone02OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
!- =========== ALL OBJECTS IN CLASS: DESIGNSPECIFICATION:OUTDOORAIR ===========
DesignSpecification:OutdoorAir, EG_Zone03OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444414, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, UG_Zone01OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.00044430555555555532, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, EG_Zone01OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444483, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, EG_Zone02OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444435, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
!- =========== ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========
Sizing:Parameters, 1.25, !- Heating Sizing Factor 1.15; !- Cooling Sizing Factor
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========
Output:VariableDictionary, regular; !- Key Field
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:LIST ===========
Output:Surfaces:List, Details; !- Report Type
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
Output:Surfaces:Drawing, DXF, !- Report Type Triangulate3DFace; !- Report Specifications 1
!- =========== ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
Output:Table:SummaryReports, AllSummary; !- Report 1 Name
!- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
OutputControl:Table:Style, CommaAndHTML, !- Column Separator JtoKWH; !- Unit Conversion
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
Output:Variable, *, !- Key Value Zone Operative Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Outdoor Air Drybulb Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mechanical Ventilation Air Changes per Hour, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Infiltration Air Change Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Ideal Loads Zone Total Cooling Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Ideal Loads Zone Total Heating Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mean Air Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mean Radiant Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Electric Equipment Total Heating Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Ground Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Deep Ground Temperature, !- Variable Name hourly; !- Reporting Frequency
How to set the cooling to zero
Hi all, all,
it is my first time typing here and asking for some help. I am having issues in setting the cooling to zero. zero.
My goal is to run a simulation where in the rooms there is a heating system (simplified, i just need to understand how much heating we need to keep the internal temperature abiove a certain target) but not cooling system. system.
I have built my EnergyPlus model through the GH-plugins HB and LB. Therefore, i set the coolign setpoint to 100°C in order to not have any cooling. However, i have Ideal cooling Loads more than 0 and no matter what changes i do (limit flow rate or limit capacity of the cooling to 0), i still have Ideal Cooling Loads more than 0. I also tried to build it from scratch again through Zone HVAC: Zone controls and Thermostats (ZoneControl:Thermostat, ThermostatSetpoint:SingleHeating) but i wasn't able to make it work unfrotunately.
Unfortunately i have no rights (yet) to attach any unfrotunately.
Here below you can find the link to my .idf file since i just signed in to this forum. I'll post here below the text editor from my idf file (sorry for that). file: https://drive.google.com/drive/folders/1B3IJFMsBQMEeNjHSIlzO8p6gvgUBgqpP?usp=sharing
It would be great if you can help me with this. this.
Thanks a lot
idf text: !-Generator IDFEditor 1.50 !-Option SortedOrder
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically. !- Use '!' comments if they need to be retained when using the IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION ===========
Version, 9.2.0; !- Version Identifier
!- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
SimulationControl, Yes, !- Do Zone Sizing Calculation Yes, !- Do System Sizing Calculation Yes, !- Do Plant Sizing Calculation No, !- Run Simulation for Sizing Periods Yes; !- Run Simulation for Weather File Run Periods
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
Building, 210301_FR11_GroundTemp05m.idf, !- Name 225.0, !- North Axis {deg} City, !- Terrain , !- Loads Convergence Tolerance Value , !- Temperature Convergence Tolerance Value {deltaC} FullExterior, !- Solar Distribution 50, !- Maximum Number of Warmup Days 6; !- Minimum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
ShadowCalculation, AverageOverDaysInFrequency, !- Calculation Method 30, !- Calculation Frequency 3000; !- Maximum Figures in Shadow Overlap Calculations
!- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
Timestep, 6; !- Number of Timesteps per Hour
!- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
!Latitude !Longitude !Time Zone !Elevation Site:Location, FRANKFURT AM MAIN DEU, !- Name 50.05, !- Latitude {deg} 8.60, !- Longitude {deg} 1.0, !- Time Zone {hr} 113.0; !- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Htg 99.6% Condns DB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type -10.5, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type -10.5, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.2, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Hum_n 99.6% Condns DP=>MCDB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type -8.4, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Dewpoint, !- Humidity Condition Type -14.3, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.2, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Htg Wind 99.6% Condns WS=>MCDB, !- Name 1, !- Month 21, !- Day of Month WinterDesignDay, !- Day Type 9.2, !- Maximum Dry-Bulb Temperature {C} 0.0, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 9.2, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 12.6, !- Wind Speed {m/s} 30, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAEClearSky, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name , !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} , !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless} 0.00; !- Sky Clearness
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns DB=>MWB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 30.8, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 19.2, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns WB=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 27.6, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Wetbulb, !- Humidity Condition Type 20.6, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns DP=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 22.4, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Dewpoint, !- Humidity Condition Type 18.5, !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} , !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
SizingPeriod:DesignDay, FRANKFURT AM MAIN Ann Clg .4% Condns Enth=>MDB, !- Name 7, !- Month 21, !- Day of Month SummerDesignDay, !- Day Type 27.5, !- Maximum Dry-Bulb Temperature {C} 10.6, !- Daily Dry-Bulb Temperature Range {deltaC} DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type , !- Dry-Bulb Temperature Range Modifier Day Schedule Name Enthalpy, !- Humidity Condition Type , !- Wetbulb or DewPoint at Maximum Dry-Bulb {C} , !- Humidity Condition Day Schedule Name , !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir} 59700.0, !- Enthalpy at Maximum Dry-Bulb {J/kg} , !- Daily Wet-Bulb Temperature Range {deltaC} 99975., !- Barometric Pressure {Pa} 3.7, !- Wind Speed {m/s} 210, !- Wind Direction {deg} No, !- Rain Indicator No, !- Snow Indicator No, !- Daylight Saving Time Indicator ASHRAETau, !- Solar Model Indicator , !- Beam Solar Day Schedule Name , !- Diffuse Solar Day Schedule Name 0.467, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless} 1.949; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
!- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod, customRun, !- Name 1, !- Begin Month 1, !- Begin Day of Month , !- Begin Year 12, !- End Month 31, !- End Day of Month , !- End Year Monday, !- Day of Week for Start Day Yes, !- Use Weather File Holidays and Special Days Yes, !- Use Weather File Daylight Saving Period No, !- Apply Weekend Holiday Rule Yes, !- Use Weather File Rain Indicators Yes; !- Use Weather File Snow Indicators
!- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
Site:GroundTemperature:BuildingSurface, 5.45, !- January Ground Temperature {C} 2.69, !- February Ground Temperature {C} 1.94, !- March Ground Temperature {C} 2.59, !- April Ground Temperature {C} 6.31, !- May Ground Temperature {C} 10.48, !- June Ground Temperature {C} 14.41, !- July Ground Temperature {C} 17.25, !- August Ground Temperature {C} 18.07, !- September Ground Temperature {C} 16.74, !- October Ground Temperature {C} 13.53, !- November Ground Temperature {C} 9.48; !- December Ground Temperature {C}
!- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
ScheduleTypeLimits, ANY NUMBER; !- Name
ScheduleTypeLimits, CONTROL TYPE, !- Name 0, !- Lower Limit Value 4, !- Upper Limit Value DISCRETE; !- Numeric Type
ScheduleTypeLimits, FRACTION, !- Name 0, !- Lower Limit Value 1, !- Upper Limit Value CONTINUOUS; !- Numeric Type
ScheduleTypeLimits, ON/OFF, !- Name 0, !- Lower Limit Value 1, !- Upper Limit Value DISCRETE; !- Numeric Type
!- =========== ALL OBJECTS IN CLASS: SCHEDULE:CONSTANT ===========
Schedule:Constant, SCHOCCUPANCY, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHHEATING, !- Name ANY NUMBER, !- Schedule Type Limits Name 5.5; !- Hourly Value
Schedule:Constant, SCHLIGHTING, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHCOOLING, !- Name ANY NUMBER, !- Schedule Type Limits Name 100; !- Hourly Value
Schedule:Constant, SCHEQUIPMENT, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
Schedule:Constant, SCHACTIVITY, !- Name ANY NUMBER, !- Schedule Type Limits Name 0; !- Hourly Value
Schedule:Constant, SCHINFILTRATION, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
Schedule:Constant, SCHVENTILATION, !- Name ANY NUMBER, !- Schedule Type Limits Name 1; !- Hourly Value
!- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
Material, CONCRETE 180MM - UG, !- Name Rough, !- Roughness 0.18, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 435MM - EXTWALLUG, !- Name Rough, !- Roughness 0.435, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 800MM - UG, !- Name Rough, !- Roughness 0.8, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 300MM - EG, !- Name Rough, !- Roughness 0.3, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 200MM - EXTWALLEG, !- Name Rough, !- Roughness 0.2, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2300, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
Material, CONCRETE 200MM - EG, !- Name Rough, !- Roughness 0.18, !- Thickness {m} 2.3, !- Conductivity {W/m-K} 2500, !- Density {kg/m3} 850, !- Specific Heat {J/kg-K} 0.9, !- Thermal Absorptance 0.7, !- Solar Absorptance 0.7; !- Visible Absorptance
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction, INTWALL_UG, !- Name CONCRETE 180MM - UG; !- Outside Layer
Construction, EXTWALL_UG, !- Name CONCRETE 435MM - EXTWALLUG; !- Outside Layer
Construction, FLOOR_UG, !- Name CONCRETE 800MM - UG; !- Outside Layer
Construction, CEILING_UG, !- Name CONCRETE 300MM - EG; !- Outside Layer
Construction, EXTWALL_EG, !- Name CONCRETE 200MM - EXTWALLEG; !- Outside Layer
Construction, INTWALL_EG, !- Name CONCRETE 200MM - EG; !- Outside Layer
Construction, FLOOR_EG, !- Name CONCRETE 300MM - EG; !- Outside Layer
Construction, CEILING_EG, !- Name CONCRETE 200MM - EG; !- Outside Layer
!- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
GlobalGeometryRules, LowerLeftCorner, !- Starting Vertex Position CounterClockWise, !- Vertex Entry Direction Relative, !- Coordinate System Relative, !- Daylighting Reference Point Coordinate System Relative; !- Rectangular Surface Coordinate System
!- =========== ALL OBJECTS IN CLASS: ZONE ===========
Zone, UG_Zone01, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone01, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone02, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
Zone, EG_Zone03, !- Name 0, !- Direction of Relative North {deg} 0.0, !- X Origin {m} 0.0, !- Y Origin {m} 0.0, !- Z Origin {m} 1, !- Type 1, !- Multiplier , !- Ceiling Height {m} , !- Volume {m3} , !- Floor Area {m2} , !- Zone Inside Convection Algorithm , !- Zone Outside Convection Algorithm Yes; !- Part of Total Floor Area
!- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
BuildingSurface:Detailed, IntWall_UG_1, !- Name WALL, !- Surface Type IntWall_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_UG_1, !- Name WALL, !- Surface Type ExtWall_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_UG_1, !- Name FLOOR, !- Surface Type Floor_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} -4.570000171661377, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} -4.570000171661377; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_UG_1, !- Name CEILING, !- Surface Type Ceiling_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_UG_2, !- Name WALL, !- Surface Type IntWall_UG, !- Construction Name UG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_UG_2, !- Name WALL, !- Surface Type ExtWall_UG, !- Construction Name UG_Zone01, !- Zone Name Ground, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG01_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone01, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG01_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG01_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG01_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG01_2, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone01, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG01_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone01, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG02_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG02_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG02_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG02_2, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone02, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG02_3, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone02, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_1, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_1, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_1, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, ExtWall_EG03_1, !- Name WALL, !- Surface Type ExtWall_EG, !- Construction Name EG_Zone03, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 3.1800000667572021, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_2, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_2, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_2, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_3, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_3, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 3.1800000667572021, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_3, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_4, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_4, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_4, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_5, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_5, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_5, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7048473358154297, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, Floor_EG03_6, !- Name FLOOR, !- Surface Type Floor_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, Ceiling_EG03_6, !- Name CEILING, !- Surface Type Ceiling_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_6, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7298479080200195, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_7, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed, IntWall_EG03_8, !- Name WALL, !- Surface Type IntWall_EG, !- Construction Name EG_Zone03, !- Zone Name Adiabatic, !- Outside Boundary Condition , !- Outside Boundary Condition Object NoSun, !- Sun Exposure NoWind, !- Wind Exposure autocalculate, !- View Factor to Ground 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 12.715000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 3.1800000667572021, !- Vertex 2 X-coordinate {m} 12.715000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 3.1800000667572021, !- Vertex 3 X-coordinate {m} 12.715000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 12.715000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: SHADING:BUILDING:DETAILED ===========
Shading:Building:Detailed, shdSrf_0_0_b90a876d-2e23-4934-a1ea-eb354434a763_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 0.0, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_1_61a85451-5b8b-4da2-a0aa-7b3aa827d960_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 0.0, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_2_65a48d6a-38f6-4ebd-94b4-2d4089f42a31_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.979999542236328, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_3_4fce51dd-1182-4de6-9667-3a11345aaa38_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_4_8206864d-d9d0-49b5-ad79-0688ecf7028b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.979999542236328, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 0.0, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_0_5_336fe436-712f-4b99-b26b-dc88a2eb8a8f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 0.0, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 0.0, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 13.979999542236328, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} -4.570000171661377, !- Vertex 3 Z-coordinate {m} 13.979999542236328, !- Vertex 4 X-coordinate {m} 0.0, !- Vertex 4 Y-coordinate {m} -4.570000171661377; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_0_b9373496-57e1-472a-82fb-5f9845741f09_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_1_f4c8fe12-dc4f-4f60-89c0-27dbe4d501d0_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} -3.5527136788005009e-15, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} -3.5527136788005009e-15, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 25.079999923706055, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_2_44abf29c-6f41-4b86-a090-0204ec000324_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_3_af12752a-efdc-4550-a084-bf88bd5464c7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 7.1750001907348633, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_4_53c0d9e9-ecbb-4b98-add4-b7ce29ca881f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 51.154998779296875, !- Vertex 4 X-coordinate {m} 7.1750001907348633, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_5_82854e05-d078-457a-b6d3-630d2b17a497_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 51.154998779296875, !- Vertex 4 X-coordinate {m} 3.5527136788005009e-15, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_6_e7a8175f-4fd0-47c1-96ae-bb8196c406f7_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_7_6ac027da-6e91-4421-aad9-4092b6120c58_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_8_ea7aeb99-6d0a-4aaa-9a6c-e4db1d9abe94_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_9_da0a65e5-e9f6-4a68-8339-d07f4010e2f6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} -4.570000171661377, !- Vertex 1 Z-coordinate {m} 25.079999923706055, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} -4.570000171661377, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} -4.570000171661377; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_10_92dd4dd0-c1ed-41be-974a-f6af061c8e14_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 51.154998779296875, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 51.154998779296875, !- Vertex 3 X-coordinate {m} 0.0, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_11_53838df5-4d09-4505-a66b-a1d10b3ea273_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 7.1750001907348633, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_12_ace0117f-05ff-4644-8b36-26043a284640_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 51.154998779296875, !- Vertex 2 X-coordinate {m} 0.0, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 7.1750001907348633, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_1_13_fd933bf3-04e0-489f-9e08-d9091ce7e424_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 25.079999923706055, !- Vertex 1 X-coordinate {m} 0.0, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 7.1750001907348633, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 25.079999923706055, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_0_a565cad4-7696-466b-bef4-5338da1190a5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_1_7f75496e-e51e-4dc1-8846-cc35b448b81d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 49.255001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_2_0c655ff7-337b-4157-89b3-47dd9faa64dc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 49.255001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_3_1c6e9705-c4b0-48e1-9e20-cf887328c85d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_4_fb4b0b8e-7910-4280-8b51-7c5e079ae7e2_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_5_7debdfe7-00ec-44d5-b8b3-bf65bde97f9d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.967815399169922, !- Vertex 1 X-coordinate {m} 8.026214599609375, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.973907470703125, !- Vertex 2 X-coordinate {m} 2.764657735824585, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.969338417053223, !- Vertex 3 X-coordinate {m} 3.1028683185577393, !- Vertex 3 Y-coordinate {m} 1.3250000476837158, !- Vertex 3 Z-coordinate {m} 13.96476936340332, !- Vertex 4 X-coordinate {m} 8.0821609497070313, !- Vertex 4 Y-coordinate {m} 1.3250000476837158; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_6_a491bcac-46ee-48c1-8919-0d9d4d3e4a30_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.96476936340332, !- Vertex 1 X-coordinate {m} 8.0821609497070313, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.969338417053223, !- Vertex 2 X-coordinate {m} 3.1028683185577393, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 3.4410789012908936, !- Vertex 3 Y-coordinate {m} 2.6500000953674316, !- Vertex 3 Z-coordinate {m} 13.961723327636719, !- Vertex 4 X-coordinate {m} 8.1381072998046875, !- Vertex 4 Y-coordinate {m} 2.6500000953674316; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_7_076a0715-f471-4da6-a704-99311f33a46b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.961723327636719, !- Vertex 1 X-coordinate {m} 8.1381072998046875, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 3.4410789012908936, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 3.7792894840240479, !- Vertex 3 Y-coordinate {m} 3.9749999046325684, !- Vertex 3 Z-coordinate {m} 13.958677291870117, !- Vertex 4 X-coordinate {m} 8.1940536499023438, !- Vertex 4 Y-coordinate {m} 3.9749999046325684; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_8_bd83513b-46c2-4860-86d2-5aef66afdcf7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.958677291870117, !- Vertex 1 X-coordinate {m} 8.1940536499023438, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.960200309753418, !- Vertex 2 X-coordinate {m} 3.7792894840240479, !- Vertex 2 Y-coordinate {m} 3.9749999046325684, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 4.117499828338623, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} 8.25, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_9_dc5c08d5-1e39-4a32-a07e-c3ca1c16538f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.961723327636719, !- Vertex 1 X-coordinate {m} 13.287772178649902, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.967815399169922, !- Vertex 2 X-coordinate {m} 8.026214599609375, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 8.0821609497070313, !- Vertex 3 Y-coordinate {m} 1.3250000476837158, !- Vertex 3 Z-coordinate {m} 13.960200309753418, !- Vertex 4 X-coordinate {m} 13.061454772949219, !- Vertex 4 Y-coordinate {m} 1.3250000476837158; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_10_235f4522-62c2-4404-959a-9724f1fe4907_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.960200309753418, !- Vertex 1 X-coordinate {m} 13.061454772949219, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 8.0821609497070313, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.961723327636719, !- Vertex 3 X-coordinate {m} 8.1381072998046875, !- Vertex 3 Y-coordinate {m} 2.6500000953674316, !- Vertex 3 Z-coordinate {m} 13.958677291870117, !- Vertex 4 X-coordinate {m} 12.835136413574219, !- Vertex 4 Y-coordinate {m} 2.6500000953674316; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_11_bac00d48-2b84-42ef-8679-b7578fa1e298_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.958677291870117, !- Vertex 1 X-coordinate {m} 12.835136413574219, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.961723327636719, !- Vertex 2 X-coordinate {m} 8.1381072998046875, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.958677291870117, !- Vertex 3 X-coordinate {m} 8.1940536499023438, !- Vertex 3 Y-coordinate {m} 3.9749999046325684, !- Vertex 3 Z-coordinate {m} 13.957154273986816, !- Vertex 4 X-coordinate {m} 12.608818054199219, !- Vertex 4 Y-coordinate {m} 3.9749999046325684; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_12_1cfe46be-24de-4f46-a1bc-9a11039364d6_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.957154273986816, !- Vertex 1 X-coordinate {m} 12.608818054199219, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 8.1940536499023438, !- Vertex 2 Y-coordinate {m} 3.9749999046325684, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 8.25, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.955631256103516, !- Vertex 4 X-coordinate {m} 12.382499694824219, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_13_4cc69a79-0c2b-4269-b7bd-722f16b80459_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.973907470703125, !- Vertex 1 X-coordinate {m} 2.764657735824585, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.969338417053223, !- Vertex 3 X-coordinate {m} 3.1028683185577393, !- Vertex 3 Y-coordinate {m} 1.3250000476837158; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_14_d2d2ea8a-85a7-4789-86d1-226a31a70bb6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.969338417053223, !- Vertex 1 X-coordinate {m} 3.1028683185577393, !- Vertex 1 Y-coordinate {m} 1.3250000476837158, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.96476936340332, !- Vertex 3 X-coordinate {m} 3.4410789012908936, !- Vertex 3 Y-coordinate {m} 2.6500000953674316; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_15_b67951ff-92e3-4513-98d9-95cea6345df1_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.96476936340332, !- Vertex 1 X-coordinate {m} 3.4410789012908936, !- Vertex 1 Y-coordinate {m} 2.6500000953674316, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 3.7792894840240479, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_16_38547ea7-d3a3-4e57-a05b-5e41d5ad9c19_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.96476936340332, !- Vertex 2 X-coordinate {m} 3.4410789012908936, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.977126121520996, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_17_6992fc54-63f5-4e09-904b-5db8fcdae939_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.960200309753418, !- Vertex 1 X-coordinate {m} 3.7792894840240479, !- Vertex 1 Y-coordinate {m} 3.9749999046325684, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 4.117499828338623, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_18_8f733456-7cf6-48f6-b398-36636495e5f2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.961723327636719, !- Vertex 2 X-coordinate {m} 13.287772178649902, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.960200309753418, !- Vertex 3 X-coordinate {m} 13.061454772949219, !- Vertex 3 Y-coordinate {m} 1.3250000476837158; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_19_b1ec1831-0ed1-482d-9492-68efbf8c764f_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.960200309753418, !- Vertex 2 X-coordinate {m} 13.061454772949219, !- Vertex 2 Y-coordinate {m} 1.3250000476837158, !- Vertex 2 Z-coordinate {m} 13.958677291870117, !- Vertex 3 X-coordinate {m} 12.835136413574219, !- Vertex 3 Y-coordinate {m} 2.6500000953674316; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_20_a7a4b53e-cae4-4418-9065-7946503726fa_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 12.835136413574219, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.957154273986816, !- Vertex 3 X-coordinate {m} 12.608818054199219, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_21_3f4d7947-636f-407f-9171-cb42592b625d_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.955631256103516, !- Vertex 1 X-coordinate {m} 12.382499694824219, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.955631256103516, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957154273986816, !- Vertex 3 X-coordinate {m} 12.608818054199219, !- Vertex 3 Y-coordinate {m} 3.9749999046325684; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_22_e48cadd0-e70c-43fb-8039-fda0f52fbbf1_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.958677291870117, !- Vertex 2 X-coordinate {m} 12.835136413574219, !- Vertex 2 Y-coordinate {m} 2.6500000953674316, !- Vertex 2 Z-coordinate {m} 13.955631256103516, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_23_e98b88ff-407f-4956-a8b1-8035e91f6bd5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 49.255001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_24_83269d7a-846b-47ca-9c56-75575ee7adc6_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_25_36208d9b-d68b-4a7a-954c-e3a4c743cb90_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_26_77821171-aba9-4a4a-8a4f-347b558ac565_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 3.5263094902038574, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_27_b17f340a-e067-45d9-a99a-6b3d57078d2b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 49.255001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 49.255001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 3.5263094902038574, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_28_0d30e11a-d33c-460c-8d7a-4236559abe1b_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_29_24e92e9a-4769-4d2e-9279-67d598da5a34_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 3.5263094902038574, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_2_30_5ac8c1c6-4653-499e-8ca8-b322c322a218_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 3.5263094902038574, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_0_50cd95d4-796e-4486-b3c5-f4a4d7f2f72c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.977126121520996, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.957986831665039, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.977126121520996, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_1_51c1f489-9a93-421e-9c78-24dc799c7f4c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 13.957986831665039, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 13.957986831665039, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_2_30fa3315-9af2-4d20-a2c5-a81664d9ed22_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 9.630000114440918, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_3_3fda03af-0456-4ff2-b358-222970cc561e_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_4_364028f6-aa05-4f9b-ab75-12e585aa18bc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.7298479080200195, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7298479080200195, !- Vertex 4 X-coordinate {m} 11.340000152587891, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_5_a5ded2b1-3daa-40ee-ad8b-39acab6a8d87_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.7048473358154297, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_6_160435f8-a0e0-47f1-b4b9-55ce70aa1bbd_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 10.789999961853027, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_7_4b5248a5-a8bf-4d87-97fe-e3479c429aca_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.4671478271484375, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_8_6a8078f2-cb25-4061-98a8-bb0d61f99e83_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 9.3950004577636719, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_9_36fc718f-17d1-4371-8a0a-b40ad92729da_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_10_28945240-f8df-4b20-abb5-7b7f663f9ea9_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 5.054999828338623, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_11_fc3b1151-1785-448b-9d81-7e99743e1fb7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.977126121520996, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_12_8172805a-ce12-4a87-b024-b5e9891f79d7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 9.630000114440918, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.963973045349121, !- Vertex 4 X-coordinate {m} 11.34501838684082, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_13_cd93ae0b-5339-4df0-9eac-ff39486c4e37_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_14_00c7580a-62cd-4271-a367-bbbfb04ddc6b_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_15_fde1954c-a04d-45c2-8152-70875b961313_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_16_f624c1a8-8021-4904-b703-aa2217ed83e4_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_17_ad6b4178-2572-4015-baf8-55eb9eeea5f0_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 13.977126121520996, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_18_35f42890-34cf-40f7-b3b6-068a3aaf19b2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7298479080200195, !- Vertex 2 X-coordinate {m} 11.340000152587891, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_19_f6ce5cde-7c2d-4184-9a81-89f6cbf53aa0_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 0.0; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_20_7816c1be-ee7e-4044-9315-9eb2a5962961_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 0.0, !- Vertex 1 Z-coordinate {m} 5.054999828338623, !- Vertex 2 X-coordinate {m} 4.1550002098083496, !- Vertex 2 Y-coordinate {m} 0.0, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 0.0, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 0.0; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_21_3024da7a-129f-47b4-a264-d7e5eb92378f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.630000114440918, !- Vertex 1 X-coordinate {m} 11.340000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.957986831665039, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.630000114440918, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_22_570fb345-ae26-4b06-86a1-204d71dd946c_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.7048473358154297, !- Vertex 2 X-coordinate {m} 10.789999961853027, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_23_f55e016d-6454-4b47-888e-ee482ed12598_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.4671478271484375, !- Vertex 2 X-coordinate {m} 9.3950004577636719, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_24_6109f30e-2829-4538-b144-9641ccbd4be8_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.4671478271484375, !- Vertex 3 X-coordinate {m} 9.3950004577636719, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_25_cace7993-5ef0-4ee4-9e2d-5ca3394d82b2_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} 4.1550002098083496, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.972288131713867, !- Vertex 2 X-coordinate {m} 4.1631946563720703, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.963973045349121, !- Vertex 3 X-coordinate {m} 11.34501838684082, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_26_d6406774-0179-4d8b-bf92-0960ce0d2845_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 6.8949999809265137, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.977126121520996, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 13.972288131713867, !- Vertex 3 X-coordinate {m} 4.1631946563720703, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 6.8949999809265137, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_27_2122136b-f823-47a6-a3cf-6fe75a375bbe_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.7048473358154297, !- Vertex 1 X-coordinate {m} 10.789999961853027, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7298479080200195, !- Vertex 3 X-coordinate {m} 11.340000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_28_07ddcdfa-94f0-412c-97a3-70a71ef597f3_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 8.4671478271484375, !- Vertex 1 X-coordinate {m} 9.3950004577636719, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 13.963973045349121, !- Vertex 2 X-coordinate {m} 11.34501838684082, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.7048473358154297, !- Vertex 3 X-coordinate {m} 10.789999961853027, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_3_29_6af74ada-6427-45ff-8e6a-74a0beb265a2_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.054999828338623, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 6.8949999809265137, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 6.8949999809265137, !- Vertex 3 X-coordinate {m} 4.1550002098083496, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 5.054999828338623, !- Vertex 4 X-coordinate {m} 4.1550002098083496, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_0_a9053094-dffd-4b86-b5f8-7aa0d1b2ee0f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_1_3b286971-2df9-46fe-83ea-fadc1d7a256c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} -0.016832431778311729, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_2_988d1371-0f44-42ff-bc2f-a8bd9ea9d298_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} -0.016832431778311729, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} -0.016832431778311729, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_3_2fbf6dce-05be-47ce-afd2-bd47a4d85e22_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2671480178833008, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2671480178833008, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_4_c9f7830e-e37b-4160-8852-270d4339719c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2771472930908203, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2671480178833008, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_5_1bce5418-be13-4afe-a4a9-dfbd563a48b5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2771472930908203, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_6_48643cd9-1800-44d5-a5d9-314a966a3417_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 16.504999160766602, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 16.504999160766602, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_7_6e858d40-f744-4070-b056-c36ef4841659_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_8_949ccf11-f412-4f96-ba5e-1d218879ad7c_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 8.2672653198242188, !- Vertex 4 X-coordinate {m} -0.016697768121957779, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_9_5bcbe1e7-61af-4e29-8f7a-3274b142686b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 5.3000001907348633, !- Vertex 3 Z-coordinate {m} 9.3805017471313477, !- Vertex 4 X-coordinate {m} -0.016649600118398666, !- Vertex 4 Y-coordinate {m} 5.3000001907348633; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_10_d10900c2-33e0-4089-8e4d-cae912fce5ea_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_11_fbd92c75-eeb6-431a-98bb-7df3422f2e63_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 5.3000001907348633, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 5.3000001907348633, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 5.3000001907348633; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_12_5a355612-a5c5-4624-8329-705b8529d4d7_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2672653198242188, !- Vertex 2 X-coordinate {m} -0.016697768121957779, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_13_d9ed9515-6d03-44f9-b9ed-0e22fa0382ad_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.3805017471313477, !- Vertex 2 X-coordinate {m} -0.016649600118398666, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_14_7af53846-d7fe-4422-a6a3-f9516a020c51_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_4_15_b2bdc37c-1087-4fc0-b6a2-927e9efd517c_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_0_4e591051-a95d-4e49-924a-c8d59bbefcb8_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} -0.014999999664723873, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} -0.014999999664723873, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_1_314e7a4c-e090-432e-be71-52749debe10f_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} -0.016832431778311729, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_2_980a8946-eea9-4469-b55e-2ee09622c978_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} -0.016832431778311729, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} -0.016832431778311729, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_3_8e86b00d-9e5a-4a52-a340-09766dc2aac5_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2671480178833008, !- Vertex 1 X-coordinate {m} 2.7100000381469727, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 5.1550002098083496, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2671480178833008, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_4_41702fcb-6814-4436-8473-64b701e90871_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2771472930908203, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2671480178833008, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_5_1aadecd6-4623-48f2-9231-1c0569dc78bc_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 11.590000152587891, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2771472930908203, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_6_f9c1ac16-78bf-4353-9bc9-676cba406345_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 9.380000114440918, !- Vertex 1 X-coordinate {m} 16.504999160766602, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 9.380000114440918, !- Vertex 4 X-coordinate {m} 16.504999160766602, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_7_068e3425-25c8-47a0-84a5-c8fc4c4098c9_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 47.505001068115234, !- Vertex 1 X-coordinate {m} 16.514999389648438, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 47.505001068115234, !- Vertex 4 X-coordinate {m} 16.514999389648438, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_8_b35af553-3780-401d-9a79-9596cdacbf76_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 5.1550002098083496, !- Vertex 2 X-coordinate {m} 2.7100000381469727, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 8.2672653198242188, !- Vertex 4 X-coordinate {m} -0.016697768121957779, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_9_be36059b-ffa9-452b-8024-eb731a39fe3d_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 8.2771472930908203, !- Vertex 2 X-coordinate {m} 11.590000152587891, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 10.600000381469727, !- Vertex 3 Z-coordinate {m} 9.3805017471313477, !- Vertex 4 X-coordinate {m} -0.016649600118398666, !- Vertex 4 Y-coordinate {m} 10.600000381469727; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_10_040e1c7f-a6df-4be2-bd6b-948e6da430ac_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} -0.014999999664723873, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_11_261295b7-ffcf-43e1-af45-814576e17fcf_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 10.600000381469727, !- Vertex 1 Z-coordinate {m} 9.380000114440918, !- Vertex 2 X-coordinate {m} 16.504999160766602, !- Vertex 2 Y-coordinate {m} 10.600000381469727, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 10.600000381469727; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_12_64186e1c-dfef-4dd6-b591-ef511d8bcfcf_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 5.1550002098083496, !- Vertex 1 X-coordinate {m} -0.016832431778311729, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 8.2672653198242188, !- Vertex 2 X-coordinate {m} -0.016697768121957779, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 8.2671480178833008, !- Vertex 3 X-coordinate {m} 2.7100000381469727, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 5.1550002098083496, !- Vertex 4 X-coordinate {m} 2.7100000381469727, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_13_a207b346-a146-464a-ba6a-83fc1749e66b_0, !- Name , !- Transmittance Schedule Name 4, !- Number of Vertices 8.2672653198242188, !- Vertex 1 X-coordinate {m} -0.016697768121957779, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 9.3805017471313477, !- Vertex 2 X-coordinate {m} -0.016649600118398666, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 11.590000152587891, !- Vertex 3 Y-coordinate {m} 15.899999618530273, !- Vertex 3 Z-coordinate {m} 8.2771472930908203, !- Vertex 4 X-coordinate {m} 11.590000152587891, !- Vertex 4 Y-coordinate {m} 15.899999618530273; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_14_18a3f056-cde8-4330-8ae9-c5fc00829a07_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} -0.014999999664723873, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 47.505001068115234, !- Vertex 3 X-coordinate {m} 16.514999389648438, !- Vertex 3 Y-coordinate {m} 15.899999618530273; !- Vertex 3 Z-coordinate {m}
Shading:Building:Detailed, shdSrf_5_15_b90da5e0-8243-4e38-a260-24ad049d600a_0, !- Name , !- Transmittance Schedule Name 3, !- Number of Vertices 9.3805017471313477, !- Vertex 1 X-coordinate {m} -0.016649600118398666, !- Vertex 1 Y-coordinate {m} 15.899999618530273, !- Vertex 1 Z-coordinate {m} 47.505001068115234, !- Vertex 2 X-coordinate {m} 16.514999389648438, !- Vertex 2 Y-coordinate {m} 15.899999618530273, !- Vertex 2 Z-coordinate {m} 9.380000114440918, !- Vertex 3 X-coordinate {m} 16.504999160766602, !- Vertex 3 Y-coordinate {m} 15.899999618530273; !- Vertex 3 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: PEOPLE ===========
People, EG_Zone03OfficePeople, !- Name EG_Zone03, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, UG_Zone01OfficePeople, !- Name UG_Zone01, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, EG_Zone01OfficePeople, !- Name EG_Zone01, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
People, EG_Zone02OfficePeople, !- Name EG_Zone02, !- Zone or ZoneList Name SCHOCCUPANCY, !- Number of People Schedule Name People/Area, !- Number of People Calculation Method , !- Number of People 0.0, !- People per Zone Floor Area {person/m2} , !- Zone Floor Area per Person {m2/person} 0.29999999999999999, !- Fraction Radiant , !- Sensible Heat Fraction SCHACTIVITY; !- Activity Level Schedule Name
!- =========== ALL OBJECTS IN CLASS: LIGHTS ===========
Lights, EG_Zone03OfficeLights, !- Name EG_Zone03, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, UG_Zone01OfficeLights, !- Name UG_Zone01, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, EG_Zone01OfficeLights, !- Name EG_Zone01, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
Lights, EG_Zone02OfficeLights, !- Name EG_Zone02, !- Zone or ZoneList Name SCHLIGHTING, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Lighting Level {W} 0.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Return Air Fraction , !- Fraction Radiant , !- Fraction Visible ; !- Fraction Replaceable
!- =========== ALL OBJECTS IN CLASS: ELECTRICEQUIPMENT ===========
ElectricEquipment, EG_Zone03ElectricEquipment, !- Name EG_Zone03, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, UG_Zone01ElectricEquipment, !- Name UG_Zone01, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, EG_Zone01ElectricEquipment, !- Name EG_Zone01, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
ElectricEquipment, EG_Zone02ElectricEquipment, !- Name EG_Zone02, !- Zone or ZoneList Name SCHEQUIPMENT, !- Schedule Name Watts/Area, !- Design Level Calculation Method , !- Design Level {W} 10.0, !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} , !- Fraction Latent , !- Fraction Radiant , !- Fraction Lost ElectricEquipment; !- End-Use Subcategory
!- =========== ALL OBJECTS IN CLASS: ZONEINFILTRATION:DESIGNFLOWRATE ===========
ZoneInfiltration:DesignFlowRate, EG_Zone03_Infiltration, !- Name EG_Zone03, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 0.0001613944288326255, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, UG_Zone01_Infiltration, !- Name UG_Zone01, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 0.0, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, EG_Zone01_Infiltration, !- Name EG_Zone01, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 6.6422764229751539e-05, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate, EG_Zone02_Infiltration, !- Name EG_Zone02, !- Zone or ZoneList Name SCHINFILTRATION, !- Schedule Name Flow/ExteriorArea, !- Design Flow Rate Calculation Method , !- Design Flow Rate {m3/s} , !- Flow per Zone Floor Area {m3/s-m2} 5.0124372093330299e-05, !- Flow per Exterior Surface Area {m3/s-m2} , !- Air Changes per Hour {1/hr} , !- Constant Term Coefficient , !- Temperature Term Coefficient , !- Velocity Term Coefficient ; !- Velocity Squared Term Coefficient
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:THERMOSTAT ===========
HVACTemplate:Thermostat, EG_Zone03_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, UG_Zone01_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, EG_Zone01_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
HVACTemplate:Thermostat, EG_Zone02_HVAC, !- Name SCHHEATING, !- Heating Setpoint Schedule Name '', !- Constant Heating Setpoint {C} SCHCOOLING, !- Cooling Setpoint Schedule Name ''; !- Constant Cooling Setpoint {C}
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:IDEALLOADSAIRSYSTEM ===========
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone03, !- Zone Name EG_Zone03_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone03OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, UG_Zone01, !- Zone Name UG_Zone01_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} UG_Zone01OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone01, !- Zone Name EG_Zone01_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone01OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
HVACTemplate:Zone:IdealLoadsAirSystem, EG_Zone02, !- Zone Name EG_Zone02_HVAC, !- Template Thermostat Name , !- System Availability Schedule Name 40, !- Maximum Heating Supply Air Temperature {C} , !- Minimum Cooling Supply Air Temperature {C} 0.008, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0085, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir} , !- Heating Limit , !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} LimitFlowRate, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} , !- Heating Availability Schedule Name , !- Cooling Availability Schedule Name None, !- Dehumidification Control Type , !- Cooling Sensible Heat Ratio {dimensionless} , !- Dehumidification Setpoint {percent} None, !- Humidification Control Type , !- Humidification Setpoint {percent} DetailedSpecification, !- Outdoor Air Method , !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} EG_Zone02OutdoorAirCntrl,!- Design Specification Outdoor Air Object Name , !- Demand Controlled Ventilation Type DifferentialDryBulb; !- Outdoor Air Economizer Type
!- =========== ALL OBJECTS IN CLASS: DESIGNSPECIFICATION:OUTDOORAIR ===========
DesignSpecification:OutdoorAir, EG_Zone03OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444414, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, UG_Zone01OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.00044430555555555532, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, EG_Zone01OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444483, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
DesignSpecification:OutdoorAir, EG_Zone02OutdoorAirCntrl,!- Name Sum, !- Outdoor Air Method 0.0, !- Outdoor Air Flow per Person {m3/s-person} 0.0029444444444444435, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2} 0, !- Outdoor Air Flow per Zone {m3/s} 0, !- Outdoor Air Flow Air Changes per Hour {1/hr} SCHVentilation; !- Outdoor Air Schedule Name
!- =========== ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========
Sizing:Parameters, 1.25, !- Heating Sizing Factor 1.15; !- Cooling Sizing Factor
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========
Output:VariableDictionary, regular; !- Key Field
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:LIST ===========
Output:Surfaces:List, Details; !- Report Type
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
Output:Surfaces:Drawing, DXF, !- Report Type Triangulate3DFace; !- Report Specifications 1
!- =========== ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
Output:Table:SummaryReports, AllSummary; !- Report 1 Name
!- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
OutputControl:Table:Style, CommaAndHTML, !- Column Separator JtoKWH; !- Unit Conversion
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
Output:Variable, *, !- Key Value Zone Operative Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Outdoor Air Drybulb Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mechanical Ventilation Air Changes per Hour, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Infiltration Air Change Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Ideal Loads Zone Total Cooling Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Ideal Loads Zone Total Heating Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mean Air Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Zone Mean Radiant Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Electric Equipment Total Heating Rate, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Ground Temperature, !- Variable Name hourly; !- Reporting Frequency
Output:Variable, *, !- Key Value Site Deep Ground Temperature, !- Variable Name hourly; !- Reporting Frequency
How to set the cooling to zero
Hi all,
it is my first time typing here and asking for some help. I am having issues in setting the cooling to zero.
My goal is to run a simulation where in the rooms there is a heating system (simplified, i just need to understand how much heating we need to keep the internal temperature abiove a certain target) but not cooling system.
I have built my EnergyPlus model through the GH-plugins HB and LB. Therefore, i set the coolign setpoint to 100°C in order to not have any cooling. However, i have Ideal cooling Loads more than 0 and no matter what changes i do (limit flow rate or limit capacity of the cooling to 0), i still have Ideal Cooling Loads more than 0. I also tried to build it from scratch again through Zone HVAC: Zone controls and Thermostats (ZoneControl:Thermostat, ThermostatSetpoint:SingleHeating) but i wasn't able to make it work unfrotunately.
Here below you can find the link to my .idf file: https://drive.google.com/drive/folders/1B3IJFMsBQMEeNjHSIlzO8p6gvgUBgqpP?usp=sharing
It would be great if you can help me with this.
Thanks a lot