Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated.

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated.appreciated! @Julien Marrec @shorowit

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit@JulienMarrec @shorowit @Kyle Benne

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @JulienMarrec @Julien Marrec @shorowit @Kyle Benne

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle BenneBenne @Andrew Parker

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @Andrew ParkerParker

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @Andrew Parker

@aparker

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @aparker @Dan Macumber

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @aparker @Dan @ Dan Macumber

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @aparker @ Dan Macumber@macumber

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @aparker @macumber@macumber @David Goldwasser

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! @Julien Marrec @shorowit @Kyle Benne @aparker @macumber @David Goldwasserappreciated!

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated!

appreciated!

Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) (Coil:Cooling:DX:SingleSpeed) to Always_On Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Any ideas would be greatly appreciated! Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Here is the link to the idf file: https://www.energycodes.gov/development/commercial/prototype_models

Any ideas would be greatly appreciated! Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Here is the link to the idf file: https://www.energycodes.gov/development/commercial/prototype_modelshttps://drive.google.com/file/d/1qDIoUq1VHMhM-ByDoROeVojkgfpfKxHY/view?usp=sharing

Any ideas would be greatly appreciated! Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Here is the link to the idf file: https://drive.google.com/file/d/1qDIoUq1VHMhM-ByDoROeVojkgfpfKxHY/view?usp=sharing

Any ideas would be greatly appreciated! Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Here is the link to the idf file: https://drive.google.com/file/d/1qDIoUq1VHMhM-ByDoROeVojkgfpfKxHY/view?usp=sharing

Any ideas would be greatly appreciated! Sincerely, Mohammad

Zone Mean Air Temperature is not following building Set Point Temperature

Hi,

I'm wondering if anyone could assist me with the following modeling issue. Actually, I'm modeling a single-room office building in a summer day- while MAT is not following the cooling setpoint temperature for the beginning hours of the day (having zero cooling loads for those hours- regardless of the setpoint temperature for those hours of the day).

While it seems to be an occupancy schedule, I already changed the schedule of the Fan(on/off) as well as my cooling HVAC (Coil:Cooling:DX:SingleSpeed) to Always_On (which is basically a fractional schedule of 1 for all 24 hours of the day).

Here is the link to the idf file: file that I'm referring to: https://drive.google.com/file/d/1qDIoUq1VHMhM-ByDoROeVojkgfpfKxHY/view?usp=sharing

Any ideas would be greatly appreciated! Sincerely, Mohammad