Guidance on 90.1 Appendix G system selection, Exception 2 (for spaces with differing peak thermal loads)
Hi all, a question on 90.1 Appendix G baseline system selection, specifically the exception related to areas with differing internal gains from the predominant space type.
I note the Exception 2 in the 90.1-2013 Appendix G section covering baseline system selection:
"If the baseline HVAC system type is 5, 6, 7, 8, 9,10, 11, 12, or 13 use separate single-zone systems conforming with the requirements of System 3 or System 4 (depending on building heating source) for any spaces that have occupancy or process loads or schedules that differ significantly from the rest of the building. Peak thermal loads that differ by 10 Btu/h·ft2 or more from the average of other spaces served by the system or schedules that differ by more than 40 equivalent full-load hours per week from other spaces served by the system are considered to differ significantly."
I believe the spirit of this exception is to apply PSZ baseline systems to areas with HIGHER internal gains than the predominant space type. However, does it also apply to spaces with LOWER internal gains than the predominant type?
For example: if the predominant building type is 100,000 ft2 of laboratory space modeled with significant plug loads (on a System 7) but there are 30,000 ft2 of circulation space with plug loads that are >10 Btu/h/ft2 LESS THAN the labs, would this circulation space qualify for this exception, and thus require a System 3 or 4 baseline?
I believe It would seem the spirit of this exception is to apply PSZ baseline systems to areas with HIGHER internal gains than the predominant space type. However, does it type, though this is not explicitly stated. Could this clause also apply to spaces with LOWER internal gains than the predominant type?
For example: if the predominant building type is 100,000 ft2 of laboratory space modeled with significant plug loads (on a System 7) but there are 30,000 ft2 of circulation other circulation/office space with plug loads that are >10 Btu/h/ft2 LESS THAN the labs, would this circulation space qualify for this exception, and thus require a System 3 or 4 baseline?
Hi all, a question on 90.1 90.1-2013 Appendix G baseline system selection, specifically the exception related to areas with differing internal gains from the predominant space type.
It would seem the spirit of this exception is to apply PSZ baseline systems to areas with HIGHER internal gains than the predominant space type, though this is not explicitly stated. Could this clause also apply to spaces with LOWER internal gains than the predominant type?
For example: if the predominant building type is 100,000 ft2 of laboratory space modeled with significant plug loads (on a System 7) but there are 30,000 ft2 of other circulation/office space with plug loads that are >10 Btu/h/ft2 LESS THAN the labs, would this circulation space qualify for this exception, and thus require a System 3 or 4 baseline?
Hi all, a question on 90.1-2013 Appendix G baseline system selection, specifically the exception related to areas with differing internal gains from the predominant space type.
Guidance on 90.1 90.1-2013 Appendix G system selection, Exception 2 (for spaces with differing peak thermal loads)
For example: if the predominant building type is 100,000 ft2 of laboratory space modeled with significant plug loads (on a System 7) but there are 30,000 ft2 of other circulation/office space with plug loads that are >10 Btu/h/ft2 LESS THAN the labs, would this circulation space qualify for this exception, and thus require qualify for a System 3 or 4 baseline?
Guidance on 90.1-2013 Appendix G system selection, Exception 2 (for spaces with differing peak thermal loads)
For example: if the predominant building type is 100,000 ft2 of laboratory space modeled with significant plug loads (on a System 7) but there are 30,000 ft2 of other circulation/office space with plug loads that are >10 Btu/h/ft2 LESS THAN the labs, would this circulation space qualify for this exception, and thus qualify for a System 3 or 4 baseline?