How would you force a strict temperature deadband on a CWLoop in EnergyPlus? I have a dualsetpoint manager on the outlet of the supply of my CWloop, a boiler to handle the heating load and a cooling tower for the cooling load, however it only maintains the upper temperature limit when there is a load on the building. When there is no load the temperature drifts upwards as can be seen in the image - the peaks are occurring outside of operating hours when there is no cooling load being demanded. The cooling towers are able to bring the loop down to the desired temperature (26.7C), but this is just a simplified 5 zone WSHP model and I have a much larger project where the temperature of the loop is allowed to get too hot when there is no load and the cooling towers can no longer bring it back to the desired temperature.
Is it something to do with the plantloop availability? my operation scheme or my setpoint managers?
I'm also not sure what is adding the load to the loop so if anyone has any insight here that would be very helpful. Is it to do with delayed heat rejection from the WSHPs condensing to the CW loop when there is no cooling demand in the building?