Removing bypass in a loop to convert to series arrangement

Hi Everyone, I am working off the example file on ground heat exchangers (GSHP-GLHE). I have made modifications to remove the bypass in the condenser supply side loop so that its a simple series arrangement with: 1) Constant speed pump 2) Ground Heat Exchanger But I get the following error. If a loop does not have any mixers or splitters does EnergyPlus still need a Connector list? If so what should I specify?

Program Version,EnergyPlus, Version 9.3.0-baff08990c, YMD=2020.06.07 19:39, * Severe * <root>[CondenserLoop][Condenser Loop] - Missing required property 'condenser_side_connector_list_name'. * Fatal * Errors occurred on processing input file. Preceding condition(s) cause termination. ...Summary of Errors that led to program termination: ..... Reference severe error count=1 ..... Last severe error=<root>[CondenserLoop][Condenser Loop] - Missing required property 'condenser_side_connector_list_name'. *** Warning: Node connection errors not checked - most system input has not been read (see previous warning). *** Fatal error -- final processing. Program exited before simulations began. See previous error messages. *** EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. *** EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors. *** EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 0.23sec

Removing bypass in a loop to convert to series arrangement

Hi Everyone, I am working off the example file on ground heat exchangers (GSHP-GLHE). I have made modifications to remove the bypass in the condenser supply side loop so that its a simple series arrangement with: 1) Constant speed pump 2) Ground Heat Exchanger But I get the following error. If a loop does not have any mixers or splitters does EnergyPlus still need a Connector list? If so what should I specify?

Program Version,EnergyPlus, Version 9.3.0-baff08990c, YMD=2020.06.07 19:39,
 * Severe  * ** Severe  ** <root>[CondenserLoop][Condenser Loop] - Missing required property 'condenser_side_connector_list_name'.
 * **  Fatal  * ** Errors occurred on processing input file. Preceding condition(s) cause termination.
 ...Summary of Errors that led to program termination:
 ..... Reference severe error count=1
 ..... Last severe error=<root>[CondenserLoop][Condenser Loop] - Missing required property 'condenser_side_connector_list_name'.
 *** ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
 *** ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
 *** ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
 *** ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
 *** ************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 1 Severe Errors; Elapsed Time=00hr 00min  0.23sec0.23sec

Thanks

Removing bypass in a loop to convert to series arrangement

Hi Everyone, I am working off the example file on ground heat exchangers (GSHP-GLHE). I have made modifications to remove the bypass in the condenser supply side loop so that its a simple series arrangement with: 1) Constant speed pump 2) Ground Heat Exchanger But I get the following error. If a loop does not have any mixers or splitters does EnergyPlus still need a Connector list? If so what should I specify?

Program Version,EnergyPlus, Version 9.3.0-baff08990c, YMD=2020.06.07 19:39,
** Severe  ** <root>[CondenserLoop][Condenser Loop] - Missing required property 'condenser_side_connector_list_name'.
**  Fatal  ** Errors occurred on processing input file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=<root>[CondenserLoop][Condenser Loop] - Missing required property 'condenser_side_connector_list_name'.
************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 1 Severe Errors; Elapsed Time=00hr 00min  0.23sec

Thanks