Hello,
I would like to use the E+ idf file generated by BEopt to run simulations directly in E+. However, even after updating the IDF file to the most current version, E+ comes up with >40 errors trying to simulate it. How can I use the BEopt output file in E+ without the errors?
-Stepp
Errors:
Program Version,EnergyPlus, Version 9.3.0-baff08990c, YMD=2020.05.26 14:0
There are a multiple errors with format:
* Warning * Meter:Custom="HEATING:GAS_1", no items assigned
* ~~~ * ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
There are also multiple errors with format: * Warning * Output:Meter: invalid Key Name="HEATING:ELECTRICITY_1" - not found.
There is a fatal error: * Fatal * UpdateMeterReporting: Previous Meter Specification errors cause program termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=GetStandardMeterResourceType: Illegal OutResourceType (for Meters) Entered=FUELOILNO1
Error Message in Entirety:
Program Version,EnergyPlus, Version 9.3.0-baff08990c, YMD=2020.05.26 14:00,
* Warning * 14:00
** Warning ** Sizing:Parameters: note Timesteps in Averaging Window entered value=[1] is less than 1 hour (i.e., 6 timesteps).
* Warning * timesteps).
** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
*** ignored.
************* Beginning Plant Sizing Calculations
* Warning * Calculations
** Warning ** Weather file location will be used rather than entered (IDF) Location object.
* ~~~ * object.
** ~~~ ** ..Location object=LOS ANGELES INTL ARPT CA
* ~~~ * CA
** ~~~ ** ..Weather File Location=Los Angeles Intl Arpt CA USA TMY3 WMO#=722950
* ~~~ * WMO#=722950
** ~~~ ** ..due to location differences, Latitude difference=[0.00] degrees, Longitude difference=[0.00] degrees.
* ~~~ * degrees.
** ~~~ ** ..Time Zone difference=[1.0] hour(s), Elevation difference=[3.20E-006] percent, [9.60E-007] meters.
* Warning * meters.
** Warning ** ProcessScheduleInput: Schedule:File="CLOTHESWASHER_1" 51880 records had errors - these values are set to 0.
* ~~~ * 0.
** ~~~ ** Use Output:Diagnostics,DisplayExtraWarnings; to see individual records in error.
* Warning * error.
** Warning ** ProcessScheduleInput: Schedule:File="DISHWASHER_1" 51729 records had errors - these values are set to 0.
* ~~~ * 0.
** ~~~ ** Use Output:Diagnostics,DisplayExtraWarnings; to see individual records in error.
* Warning * error.
** Warning ** ProcessScheduleInput: Schedule:File="SHOWERS_1" 51587 records had errors - these values are set to 0.
* ~~~ * 0.
** ~~~ ** Use Output:Diagnostics,DisplayExtraWarnings; to see individual records in error.
* Warning * error.
** Warning ** ProcessScheduleInput: Schedule:File="SINKS_1" 45293 records had errors - these values are set to 0.
* ~~~ * 0.
** ~~~ ** Use Output:Diagnostics,DisplayExtraWarnings; to see individual records in error.
* Warning * error.
** Warning ** No floor exists in Zone="DUMMY", zone floor area is zero. All values for this zone that are entered per floor area will be zero.
* Warning * zero.
** Warning ** CalculateZoneVolume: 2 zones are not fully enclosed. For more details use: Output:Diagnostics,DisplayExtrawarnings;
* Warning * Output:Diagnostics,DisplayExtrawarnings;
** Warning ** CheckUsedConstructions: There are 14 nominally unused constructions in input.
* ~~~ * input.
** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
* Warning * Output:Diagnostics,DisplayExtraWarnings;
** Warning ** The Standard Ratings is calculated for Coil:Cooling:DX:SingleSpeed = DX COOLING COIL_1 but not at the AHRI test condition due to curve out of bound.
* ~~~ * bound.
** ~~~ ** Review the Standard Ratings calculations in the Engineering Reference for this coil type. Also, use Output:Diagnostics, DisplayExtraWarnings for further guidance.
* Warning * guidance.
** Warning ** Check input. Pump nominal power or motor efficiency is set to 0, for pump=MAINS PRESSURE_1
* PRESSURE_1
** Severe * ** GetStandardMeterResourceType: Illegal OutResourceType (for Meters) Entered=FUELOILNO1
* ~~~ * Entered=FUELOILNO1
** ~~~ ** ..on Meter:Custom="HEATING:FUELOIL_1".
* Warning * Meter:Custom="HEATING:FUELOIL_1".
** Warning ** Meter:Custom="HEATING:GAS_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="HEATING:ELECTRICITY_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="COOLING HVAC FAN PUMP_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="HEATING HVAC FAN PUMP_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="WATERHEATING:PROPANE_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="WATERHEATING:FUELOIL_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="WATERHEATING:GAS_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="HPWHFAN:ELECTRICITY_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="SDHWPUMP:ELECTRICITY_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="ELECELEMUSAGEOUTPUT_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="TOTALLIGHTS:ELECTRICITY_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="VENTFANS:ELECTRICITY_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="PV:ELECTRICITY_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="ELECTRICITY:UNIT_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="GAS:UNIT_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="FUELOIL:UNIT_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Meter:Custom="PROPANE:UNIT_1", no items assigned
* ~~~ * assigned
** ~~~ ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.
* Warning * Meter:Custom.
** Warning ** Output:Meter: invalid Key Name="CUSTOMCRANKCASEHEATER_1:INTERIOREQUIPMENT:ELECTRICITY" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="HEATING:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="HEATINGSUPP:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="COOLING HVAC FAN PUMP_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="HEATING HVAC FAN PUMP_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="SDHWPUMP:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="HPWHFAN:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="RECIRCPUMP:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:ELECTRICITY" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="SDHWPUMP:ELECTRICITY" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="HPWHFAN:ELECTRICITY" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="TOTALLIGHTS:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="COMMONLIGHTS:ELECTRICITY" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="VENTFANS_1:FANS:ELECTRICITY" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="HEATING:GAS_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:GAS_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:GAS" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="APPL_1:INTERIOREQUIPMENT:GAS" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:FUELOIL_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:FUELOIL" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:PROPANE_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="WATERHEATING:PROPANE" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="APPL_1:EXTERIOREQUIPMENT:PROPANE" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="PV:ELECTRICITY_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="METERPIPELOSSESCENTRAL" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="ELECTRICITY:UNIT_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="ELECTRICITY:COMMON" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="GAS:UNIT_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="GAS:COMMON" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="PROPANE:UNIT_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="PROPANE:COMMON" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="FUELOIL:UNIT_1" - not found.
* Warning * found.
** Warning ** Output:Meter: invalid Key Name="FUELOIL:COMMON" - not found.
* found.
** Fatal * ** UpdateMeterReporting: Previous Meter Specification errors cause program termination.
termination.
...Summary of Errors that led to program termination:
termination:
..... Reference severe error count=1
count=1
..... Last severe error=GetStandardMeterResourceType: Illegal OutResourceType (for Meters) Entered=FUELOILNO1
*** Entered=FUELOILNO1
************* Fatal error -- final processing. More error messages may appear.
*** appear.
************* Testing Individual Branch Integrity
*** Integrity
************* All Branches passed integrity testing
*** testing
************* Testing Individual Supply Air Path Integrity
*** Integrity
************* All Supply Air Paths passed integrity testing
*** testing
************* Testing Individual Return Air Path Integrity
*** Integrity
************* All Return Air Paths passed integrity testing
*** testing
************* No node connection errors were found.
* Warning * found.
** Warning ** There is no BYPASS component in the demand-side of PlantLoop =DHW LOOP_1
* ~~~ * LOOP_1
** ~~~ ** You may be able to fix the fatal error above by adding a demand-side BYPASS PIPE.
*** *************
************* ===== Final Error Summary =====
*** =====
************* The following error categories occurred. Consider correcting or noting.
*** noting.
************* Nominally Unused Constructions
*** Constructions
************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
*** cause
************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
*** HeatBalanceAlgorithm
************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
***
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
*** Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 2 Warning; 0 Severe Errors.
*** Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 64 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 1.65sec