Zone cross mixing in energyplus

I have an inquiry on setting up ZoneCrossMixing object.

I simulated 2 cases (cross mixing case and no cross mixing case) by changing the relation of inter-zone heat & mass transfer and compared. However, there was no difference in the temperature of each zone in the non-air-conditioned time zone in each case. So I really appreciate if you could have advices or comments on this matter.

The description of how I set the ZoneCrossMixing object in the cross mixing case is as follows. If you see the object of PneandPn((perimeter North East zone & perimeter North zone), I set the ZoneCrossMixing object as follows, Zone Pne and Zone Pn to be source and receiving zone. The reason I set is that crossmixing occurs only in the case of “the temperature of source Zone-the one of Receiving Zone>= ΔT (default=zero )”. I believe that it should occur in the case of the “temperature of Receiving Zone-the one of source Zone>= ΔT (default=zero)”. So I set this way to all the inter-zone.

And I set the design flow to an amount equivalent to 0.5 ventilation per hour in a smaller zone. (Pne floor area: 40.96m2, Pn floor area: 245.76m2, Ceiling Height: 2.6m) In the idf editor, design flow rate unit is m3/s, so I used this unit. However, I suspect that the correct unit is m3/min. (Because after I changed the unit, I got the result seemed to be correct.)

ZoneCrossMixing, 1F:PneAndPn, !- Name 1F:Pne, !- Zone Name On, !- Schedule Name Flow/Zone, !- Design Flow Rate Calculation Method 0.016, !- Design Flow Rate {m3/s} , !- Flow Rate per Zone Floor Area {m3/s-m2} , !- Flow Rate per Person {m3/s-person} , !- Air Changes per Hour {1/hr} 1F:Pn; !- Source Zone Name

ZoneCrossMixing, 1F:PnAndPne, !- Name 1F:Pn, !- Zone Name On, !- Schedule Name Flow/Zone, !- Design Flow Rate Calculation Method 0.016, !- Design Flow Rate {m3/s} , !- Flow Rate per Zone Floor Area {m3/s-m2} , !- Flow Rate per Person {m3/s-person} , !- Air Changes per Hour {1/hr} 1F:Pne; !- Source Zone Name

Zone cross mixing in energyplus

I have an inquiry on setting up ZoneCrossMixing object.

I simulated 2 cases (cross mixing case and no cross mixing case) by changing the relation of inter-zone heat & mass transfer and compared. However, there was no difference in the temperature of each zone in the non-air-conditioned time zone in each case. So I really appreciate if you could have advices or comments on this matter.

The description of how I set the ZoneCrossMixing object in the cross mixing case is as follows. If you see the object of PneandPn((perimeter North East zone & perimeter North zone), I set the ZoneCrossMixing object as follows, Zone Pne and Zone Pn to be source and receiving zone. The reason I set is that crossmixing occurs only in the case of “the temperature of source Zone-the one of Receiving Zone>= ΔT (default=zero )”. I believe that it should occur in the case of the “temperature of Receiving Zone-the one of source Zone>= ΔT (default=zero)”. So I set this way to all the inter-zone.

And I set the design flow to an amount equivalent to 0.5 ventilation per hour in a smaller zone. (Pne floor area: 40.96m2, Pn floor area: 245.76m2, Ceiling Height: 2.6m) In the idf editor, design flow rate unit is m3/s, so I used this unit. However, I suspect that the correct unit is m3/min. (Because after I changed the unit, I got the result seemed to be correct.)

ZoneCrossMixing, 1F:PneAndPn, !- Name 1F:Pne, !- Zone Name On, !- Schedule Name Flow/Zone, !- Design Flow Rate Calculation Method 0.016, !- Design Flow Rate {m3/s} , !- Flow Rate per Zone Floor Area {m3/s-m2} , !- Flow Rate per Person {m3/s-person} , !- Air Changes per Hour {1/hr} 1F:Pn; !- Source Zone Name

ZoneCrossMixing, 1F:PnAndPne, !- Name 1F:Pn, !- Zone Name On, !- Schedule Name Flow/Zone, !- Design Flow Rate Calculation Method 0.016, !- Design Flow Rate {m3/s} , !- Flow Rate per Zone Floor Area {m3/s-m2} , !- Flow Rate per Person {m3/s-person} , !- Air Changes per Hour {1/hr} 1F:Pne; !- Source Zone Name

Zone cross mixing in energyplus

I have an inquiry on setting up ZoneCrossMixing object.

I simulated 2 cases (cross mixing case and no cross mixing case) by changing the relation of inter-zone heat & mass transfer and compared. However, there was no difference in the temperature of each zone in the non-air-conditioned time zone in each case. So I really appreciate if you could have advices or comments on this matter.

The description of how I set the ZoneCrossMixing object in the cross mixing case is as follows. If you see the object of PneandPn((perimeter North East zone & perimeter North zone), I set the ZoneCrossMixing object as follows, Zone Pne and Zone Pn to be source and receiving zone. The reason I set is that crossmixing occurs only in the case of “the temperature of source Zone-the one of Receiving Zone>= ΔT (default=zero )”. I believe that it should occur in the case of the “temperature of Receiving Zone-the one of source Zone>= ΔT (default=zero)”. So I set this way to all the inter-zone.

And I set the design flow to an amount equivalent to 0.5 ventilation per hour in a smaller zone. (Pne floor area: 40.96m2, Pn floor area: 245.76m2, Ceiling Height: 2.6m) In the idf editor, design flow rate unit is m3/s, so I used this unit. However, I suspect that the correct unit is m3/min. (Because after I changed the unit, I got the result seemed to be correct.)

ZoneCrossMixing,
 1F:PneAndPn,             !- Name
 1F:Pne,                  !- Zone Name
 On,                      !- Schedule Name
 Flow/Zone,               !- Design Flow Rate Calculation Method
 0.016,                     !- Design Flow Rate {m3/s}
 ,                        !- Flow Rate per Zone Floor Area {m3/s-m2}
 ,                        !- Flow Rate per Person {m3/s-person}
 ,                    !- Air Changes per Hour {1/hr}
 1F:Pn;                   !- Source Zone Name

Name ZoneCrossMixing, 1F:PnAndPne, !- Name 1F:Pn, !- Zone Name On, !- Schedule Name Flow/Zone, !- Design Flow Rate Calculation Method 0.016, !- Design Flow Rate {m3/s} , !- Flow Rate per Zone Floor Area {m3/s-m2} , !- Flow Rate per Person {m3/s-person} , !- Air Changes per Hour {1/hr} 1F:Pne; !- Source Zone Name

Name

Zone cross mixing in energyplus

I have an inquiry on setting up ZoneCrossMixing object.

I simulated 2 cases (cross mixing case and no cross mixing case) by changing the relation of inter-zone heat & mass transfer and compared. However, there was no difference in the temperature of each zone in the non-air-conditioned time zone in each case. So I really appreciate if you could have advices or comments on this matter.

The description of how I set the ZoneCrossMixing object in the cross mixing case is as follows. If you see the object of PneandPn((perimeter North East zone & perimeter North zone), I set the ZoneCrossMixing object as follows, Zone Pne and Zone Pn to be source and receiving zone. The reason I set is that crossmixing occurs only in the case of “the temperature of source Zone-the one of Receiving Zone>= ΔT (default=zero )”. I believe that it should occur in the case of the “temperature of Receiving Zone-the one of source Zone>= ΔT (default=zero)”. So I set this way to all the inter-zone.

And I set the design flow to an amount equivalent to 0.5 ventilation per hour in a smaller zone. (Pne floor area: 40.96m2, Pn floor area: 245.76m2, Ceiling Height: 2.6m) In the idf editor, design flow rate unit is m3/s, so I used this unit. However, I suspect that the correct unit is m3/min. (Because after I changed the unit, I got the result seemed to be correct.)

ZoneCrossMixing,
1F:PneAndPn,             !- Name
1F:Pne,                  !- Zone Name
On,                      !- Schedule Name
Flow/Zone,               !- Design Flow Rate Calculation Method
0.016,                     !- Design Flow Rate {m3/s}
,                        !- Flow Rate per Zone Floor Area {m3/s-m2}
,                        !- Flow Rate per Person {m3/s-person}
,                    !- Air Changes per Hour {1/hr}
1F:Pn;                   !- Source Zone Name

ZoneCrossMixing,
1F:PnAndPne,             !- Name
1F:Pn,                   !- Zone Name
On,                      !- Schedule Name
Flow/Zone,               !- Design Flow Rate Calculation Method
0.016,                     !- Design Flow Rate {m3/s}
,                        !- Flow Rate per Zone Floor Area {m3/s-m2}
,                        !- Flow Rate per Person {m3/s-person}
,                     !- Air Changes per Hour {1/hr}
1F:Pne;                  !- Source Zone Name

Zone cross mixing in energyplus

I have an inquiry on setting up ZoneCrossMixing object.

I simulated 2 cases (cross mixing case and no cross mixing case) by changing the relation of inter-zone heat & mass transfer and compared. However, there was no difference in the temperature of each zone in the non-air-conditioned time zone in each case. So I really appreciate if you could have advices or comments on this matter.

The description of how I set the ZoneCrossMixing object in the cross mixing case is as follows. If you see the object of PneandPn((perimeter North East zone & perimeter North zone), I set the ZoneCrossMixing object as follows, Zone Pne and Zone Pn to be source and receiving zone. The reason I set is that crossmixing occurs only in the case of “the temperature of source Zone-the one of Receiving Zone>= ΔT (default=zero )”. I believe that it should occur in the case of the “temperature of Receiving Zone-the one of source Zone>= ΔT (default=zero)”. So I set this way to all the inter-zone.

And I set the design flow to an amount equivalent to 0.5 ventilation per hour in a smaller zone. (Pne floor area: 40.96m2, Pn floor area: 245.76m2, Ceiling Height: 2.6m) In the idf editor, design flow rate unit is m3/s, so I used this unit. However, I suspect that the correct unit is m3/min. (Because after I changed the unit, I got the result seemed to be correct.)

ZoneCrossMixing,
1F:PneAndPn,             !- Name
1F:Pne,                  !- Zone Name
On,                      !- Schedule Name
Flow/Zone,               !- Design Flow Rate Calculation Method
0.016,                     !- Design Flow Rate {m3/s}
,                        !- Flow Rate per Zone Floor Area {m3/s-m2}
,                        !- Flow Rate per Person {m3/s-person}
,                    !- Air Changes per Hour {1/hr}
1F:Pn;                   !- Source Zone Name

ZoneCrossMixing,
1F:PnAndPne,             !- Name
1F:Pn,                   !- Zone Name
On,                      !- Schedule Name
Flow/Zone,               !- Design Flow Rate Calculation Method
0.016,                     !- Design Flow Rate {m3/s}
,                        !- Flow Rate per Zone Floor Area {m3/s-m2}
,                        !- Flow Rate per Person {m3/s-person}
,                     !- Air Changes per Hour {1/hr}
1F:Pne;                  !- Source Zone Name