SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using: IDF,SetpointManager:OutdoorAirReset,CAG ChW Temp Manager,Temperature, 7.2,15.6,6.7,26.7,CAG ChW Supply Setpoint Nodes,,,,,;

Thank

Output in version 8.3: Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1 Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using: IDF,SetpointManager:OutdoorAirReset,CAG using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,Temperature, 7.2,15.6,6.7,26.7,CAG Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,,,,,;

Thank

Nodes, , , , , ;

Output in version 8.3: 8.3:

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 8.48779409 02/21 12:15:00 26.187 9.433117172 9.433117172 02/21 12:30:00 26.353 8.665709466 8.665709466 02/21 12:45:00 26.519 9.14925803 9.14925803 02/21 13:00:00 26.685 8.77316689 8.77316689 02/21 13:15:00 26.78875 8.651484388 8.651484388 02/21 13:30:00 26.8925 8.694165106 8.694165106 02/21 13:45:00 26.99625 8.541134899 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,
  ,
  ,
  ,
  ,
  ;

Output in version 8.3:

| Date/Time | Environment:Site Outdoor Air Drybulb Temperature C | CAG CHW SUPPLY OUTLET:System Node Temperature C | | 02/21 12:00:00 | 26.021 7.036441441 | 7.036441441 |

02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,
  ,
  ,
  ,
  ,
  ;

Output in version 8.3:

| Date/Time | Environment:Site Outdoor Air Drybulb Temperature C | CAG CHW SUPPLY OUTLET:System Node Temperature C | | 02/21 12:00:00 | 26.021 | 7.036441441 |7.036441441

02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,
  ,
  ,
  ,
  ,
  ;

Output in version 8.3:

Date/Time | Environment:Site Outdoor Air Drybulb Temperature C | CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 | 26.021 | 7.036441441

7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,
  ,
  ,
  ,
  ,
  ;

Output in version 8.3:

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,
  ,
  ,
  ,
  ,
  ;

Output in version 8.3:

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7

Output in version 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511

SetpointManager:OutdoorAirReset

I'm using the "SetpointManager:OutdoorAirReset" but it not working. The temperature of chiller outlet was not controlled. When I simulated in the 8.3 version was working, but after I upgrade to the version 9.1 this control didn't work more.

This is the control I am using:

SetpointManager:OutdoorAirReset,
  CAG ChW Temp Manager,
  Temperature, 
  7.2,
  15.6,
  6.7,
  26.7,
  CAG ChW Supply Setpoint Nodes,
  ,
  ,
  ,
  ,
  ;

Output in version 8.3:

8.3: Date/Time Environment:Site Outdoor Air Drybulb Temperature C CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 7.036441441 02/21 12:15:00 26.187 6.954189189 02/21 12:30:00 26.353 6.871936937 02/21 12:45:00 26.519 6.789684685 02/21 13:00:00 26.685 6.707432432 02/21 13:15:00 26.78875 6.7 02/21 13:30:00 26.8925 6.7 02/21 13:45:00 26.99625 6.7 02/21 14:00:00 27.1 6.7C:\fakepath\Modelo8.3.PNG

Output in version 9.1

Date/Time Environment:Site Outdoor Air Drybulb Temperature C9.1 C:\fakepath\Modelo9.1.PNG CAG CHW SUPPLY OUTLET:System Node Temperature C 02/21 12:00:00 26.021 8.48779409 02/21 12:15:00 26.187 9.433117172 02/21 12:30:00 26.353 8.665709466 02/21 12:45:00 26.519 9.14925803 02/21 13:00:00 26.685 8.77316689 02/21 13:15:00 26.78875 8.651484388 02/21 13:30:00 26.8925 8.694165106 02/21 13:45:00 26.99625 8.541134899 02/21 14:00:00 27.1 8.532365511