Unreasonable results for water heating desuperheater

Previously, I modeled a water system with desuperheater in Model 1 which gave happy results (about half water heating energy saving). Now I need to integrate this technology into another model( Model2) with exactly the same approach. However, the Model 2 results showed about 10X water heating energy usage than its baseline, which is unreasonable.

The approach I used to model desuperheater is quite straightforward, I'd like to elaborate as following:

  • I created a constant temperature schedule of 55C (setpoint is 52.6667C)

.

Schedule:Constant,
  desuperheaterStp,        !- Name
  Temperature,             !- Schedule Type Limits Name
  55;                      !- Hourly Value
  • I used Coil:WaterHeating:Desuperheater object, the snippet was like

.

Coil:WaterHeating:Desuperheater,
   Desuperheater,             !- Name
   ,                          !- Availability Schedule Name
   desuperheaterStp,          !- Setpoint Temperature Schedule Name
   2,                         !- Dead Band Temperature Difference {deltaC}
   0.25,                      !- Rated Heat Reclaim Recovery Efficiency
   50,                        !- Rated Inlet Water Temperature {C}
   35,                        !- Rated Outdoor Air Temperature {C}
   60,                        !- Maximum Inlet Water Temperature for Heat Reclaim {C}
   ,                          !- Heat Reclaim Efficiency Function of Temperature Curve Name
   DesuperheaterIn,           !- Water Inlet Node Name
   DesuperheaterOut,          !- Water Outlet Node Name
   WaterHeater:Mixed,         !- Tank Object Type
   water heater,              !- Tank Name
   Coil:Cooling:DX:SingleSpeed,  !- Heating Source Object Type
   central ac clg coil,       !- Heating Source Name
   0.001,                     !- Water Flow Rate {m3/s}
   ,                          !- Water Pump Power {W}
   0.2;                       !- Fraction of Pump Heat to Water
  • And finally I got these two water nodes connected with WaterHeater:Mixed

.

WaterHeater:Mixed,
res wh,                  !- Name
0.136274824222915,       !- Tank Volume {m3}
WH Setpoint Temp,        !- Setpoint Temperature Schedule Name
2,                       !- Deadband Temperature Difference {deltaC}
99,                      !- Maximum Temperature Limit {C}
Cycle,                   !- Heater Control Type
5500.06477392209,        !- Heater Maximum Capacity {W}
0,                       !- Heater Minimum Capacity {W}
0,                       !- Heater Ignition Minimum Flow Rate {m3/s}
0,                       !- Heater Ignition Delay {s}
Electricity,             !- Heater Fuel Type
0.8,                     !- Heater Thermal Efficiency
,                        !- Part Load Factor Curve Name
0,                       !- Off Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- Off Cycle Parasitic Fuel Type
0,                       !- Off Cycle Parasitic Heat Fraction to Tank
0,                       !- On Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- On Cycle Parasitic Fuel Type
0,                       !- On Cycle Parasitic Heat Fraction to Tank
Outdoors,                !- Ambient Temperature Indicator
,                        !- Ambient Temperature Schedule Name
,                        !- Ambient Temperature Zone Name
Model Outdoor Air Node,  !- Ambient Temperature Outdoor Air Node Name
0.704227539803499,       !- Off Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- Off Cycle Loss Fraction to Zone
0.704227539803499,       !- On Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- On Cycle Loss Fraction to Zone
,                        !- Peak Use Flow Rate {m3/s}
,                        !- Use Flow Rate Fraction Schedule Name
,                        !- Cold Water Supply Temperature Schedule Name
Node 13,                 !- Use Side Inlet Node Name
Node 14,                 !- Use Side Outlet Node Name
1,                       !- Use Side Effectiveness
DesuperheaterOut,        !- Source Side Inlet Node Name
DesuperheaterIn,         !- Source Side Outlet Node Name
1,                       !- Source Side Effectiveness
Autosize,                !- Use Side Design Flow Rate {m3/s}
Autosize,                !- Source Side Design Flow Rate {m3/s}
1.5,                     !- Indirect Water Heating Recovery Time {hr}
IndirectHeatPrimarySetpoint,  !- Source Side Flow Control Mode
,                        !- Indirect Alternate Setpoint Temperature Schedule Name
General;                 !- End-Use Subcategory

Water system energy results:

Model1

  • Baseline : 13.21
  • Desuperheater : 6.07

Model2

  • Baseline : 11.09
  • Desuperheater : 119.2

Folder Link

Models and results folder

Unreasonable results for water heating desuperheater

Previously, I modeled a water system with desuperheater in Model 1 which gave happy results (about half water heating energy saving). Now I need to integrate this technology into another model( Model2) with exactly the same approach. However, the Model 2 results showed about 10X water heating energy usage than its baseline, which is unreasonable.

The approach I used to model desuperheater is quite straightforward, I'd like to elaborate as following:

  • I created a constant temperature schedule of 55C (setpoint is 52.6667C)

.

Schedule:Constant,
  desuperheaterStp,        !- Name
  Temperature,             !- Schedule Type Limits Name
  55;                      !- Hourly Value
  • I used Coil:WaterHeating:Desuperheater object, the snippet was like

.

Coil:WaterHeating:Desuperheater,
   Desuperheater,             !- Name
   ,                          !- Availability Schedule Name
   desuperheaterStp,          !- Setpoint Temperature Schedule Name
   2,                         !- Dead Band Temperature Difference {deltaC}
   0.25,                      !- Rated Heat Reclaim Recovery Efficiency
   50,                        !- Rated Inlet Water Temperature {C}
   35,                        !- Rated Outdoor Air Temperature {C}
   60,                        !- Maximum Inlet Water Temperature for Heat Reclaim {C}
   ,                          !- Heat Reclaim Efficiency Function of Temperature Curve Name
   DesuperheaterIn,           !- Water Inlet Node Name
   DesuperheaterOut,          !- Water Outlet Node Name
   WaterHeater:Mixed,         !- Tank Object Type
   water heater,              !- Tank Name
   Coil:Cooling:DX:SingleSpeed,  !- Heating Source Object Type
   central ac clg coil,       !- Heating Source Name
   0.001,                     !- Water Flow Rate {m3/s}
   ,                          !- Water Pump Power {W}
   0.2;                       !- Fraction of Pump Heat to Water
  • And finally I got these two water nodes connected with WaterHeater:Mixed

.

WaterHeater:Mixed,
res wh,                  !- Name
0.136274824222915,       !- Tank Volume {m3}
WH Setpoint Temp,        !- Setpoint Temperature Schedule Name
2,                       !- Deadband Temperature Difference {deltaC}
99,                      !- Maximum Temperature Limit {C}
Cycle,                   !- Heater Control Type
5500.06477392209,        !- Heater Maximum Capacity {W}
0,                       !- Heater Minimum Capacity {W}
0,                       !- Heater Ignition Minimum Flow Rate {m3/s}
0,                       !- Heater Ignition Delay {s}
Electricity,             !- Heater Fuel Type
0.8,                     !- Heater Thermal Efficiency
,                        !- Part Load Factor Curve Name
0,                       !- Off Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- Off Cycle Parasitic Fuel Type
0,                       !- Off Cycle Parasitic Heat Fraction to Tank
0,                       !- On Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- On Cycle Parasitic Fuel Type
0,                       !- On Cycle Parasitic Heat Fraction to Tank
Outdoors,                !- Ambient Temperature Indicator
,                        !- Ambient Temperature Schedule Name
,                        !- Ambient Temperature Zone Name
Model Outdoor Air Node,  !- Ambient Temperature Outdoor Air Node Name
0.704227539803499,       !- Off Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- Off Cycle Loss Fraction to Zone
0.704227539803499,       !- On Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- On Cycle Loss Fraction to Zone
,                        !- Peak Use Flow Rate {m3/s}
,                        !- Use Flow Rate Fraction Schedule Name
,                        !- Cold Water Supply Temperature Schedule Name
Node 13,                 !- Use Side Inlet Node Name
Node 14,                 !- Use Side Outlet Node Name
1,                       !- Use Side Effectiveness
DesuperheaterOut,        !- Source Side Inlet Node Name
DesuperheaterIn,         !- Source Side Outlet Node Name
1,                       !- Source Side Effectiveness
Autosize,                !- Use Side Design Flow Rate {m3/s}
Autosize,                !- Source Side Design Flow Rate {m3/s}
1.5,                     !- Indirect Water Heating Recovery Time {hr}
IndirectHeatPrimarySetpoint,  !- Source Side Flow Control Mode
,                        !- Indirect Alternate Setpoint Temperature Schedule Name
General;                 !- End-Use Subcategory

Water system energy results:

Model1

  • Baseline : 13.21
  • Desuperheater : 6.07

Model2

  • Baseline : 11.09
  • Desuperheater : 119.2

I looked into the reports of Model2, and made some plots:

image description

the “DESUPERHEATER:Water Heater Heating Energy J” and “WATER HEATER:Water Heater Source Side Heat Transfer Energy J” were surprisingly not reported as the same. They look like this (0601-0607).

image description

The results are so weird. I attached my models below, they're sitting in the google drive link below ready for you to review. If anyone knows where it went wrong, please let me know. Thanks very much!!

Folder Link

Models and results folder

Unreasonable results for water heating desuperheater

Previously, I modeled a water system with desuperheater in Model 1 which gave happy results (about half water heating energy saving). Now I need to integrate this technology into another model( Model2) with exactly the same approach. However, the Model 2 results showed about 10X more water heating energy usage than its baseline, which is unreasonable.

The approach I used to model desuperheater is quite straightforward, I'd like to elaborate as following:elaborate:

  • I created a constant temperature schedule of 55C (setpoint is 52.6667C)52.6667C) as desuperheater setpoint, which requires a little bit higher than water heater setpoint to be activated.

.

Schedule:Constant,
  desuperheaterStp,        !- Name
  Temperature,             !- Schedule Type Limits Name
  55;                      !- Hourly Value
  • I used Coil:WaterHeating:Desuperheater object, the snippet was like

.

Coil:WaterHeating:Desuperheater,
   Desuperheater,             !- Name
   ,                          !- Availability Schedule Name
   desuperheaterStp,          !- Setpoint Temperature Schedule Name
   2,                         !- Dead Band Temperature Difference {deltaC}
   0.25,                      !- Rated Heat Reclaim Recovery Efficiency
   50,                        !- Rated Inlet Water Temperature {C}
   35,                        !- Rated Outdoor Air Temperature {C}
   60,                        !- Maximum Inlet Water Temperature for Heat Reclaim {C}
   ,                          !- Heat Reclaim Efficiency Function of Temperature Curve Name
   DesuperheaterIn,           !- Water Inlet Node Name
   DesuperheaterOut,          !- Water Outlet Node Name
   WaterHeater:Mixed,         !- Tank Object Type
   water heater,              !- Tank Name
   Coil:Cooling:DX:SingleSpeed,  !- Heating Source Object Type
   central ac clg coil,       !- Heating Source Name
   0.001,                     !- Water Flow Rate {m3/s}
   ,                          !- Water Pump Power {W}
   0.2;                       !- Fraction of Pump Heat to Water
  • And finally I got these two water nodes connected with WaterHeater:Mixed

.

WaterHeater:Mixed,
res wh,                  !- Name
0.136274824222915,       !- Tank Volume {m3}
WH Setpoint Temp,        !- Setpoint Temperature Schedule Name
2,                       !- Deadband Temperature Difference {deltaC}
99,                      !- Maximum Temperature Limit {C}
Cycle,                   !- Heater Control Type
5500.06477392209,        !- Heater Maximum Capacity {W}
0,                       !- Heater Minimum Capacity {W}
0,                       !- Heater Ignition Minimum Flow Rate {m3/s}
0,                       !- Heater Ignition Delay {s}
Electricity,             !- Heater Fuel Type
0.8,                     !- Heater Thermal Efficiency
,                        !- Part Load Factor Curve Name
0,                       !- Off Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- Off Cycle Parasitic Fuel Type
0,                       !- Off Cycle Parasitic Heat Fraction to Tank
0,                       !- On Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- On Cycle Parasitic Fuel Type
0,                       !- On Cycle Parasitic Heat Fraction to Tank
Outdoors,                !- Ambient Temperature Indicator
,                        !- Ambient Temperature Schedule Name
,                        !- Ambient Temperature Zone Name
Model Outdoor Air Node,  !- Ambient Temperature Outdoor Air Node Name
0.704227539803499,       !- Off Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- Off Cycle Loss Fraction to Zone
0.704227539803499,       !- On Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- On Cycle Loss Fraction to Zone
,                        !- Peak Use Flow Rate {m3/s}
,                        !- Use Flow Rate Fraction Schedule Name
,                        !- Cold Water Supply Temperature Schedule Name
Node 13,                 !- Use Side Inlet Node Name
Node 14,                 !- Use Side Outlet Node Name
1,                       !- Use Side Effectiveness
DesuperheaterOut,        !- Source Side Inlet Node Name
DesuperheaterIn,         !- Source Side Outlet Node Name
1,                       !- Source Side Effectiveness
Autosize,                !- Use Side Design Flow Rate {m3/s}
Autosize,                !- Source Side Design Flow Rate {m3/s}
1.5,                     !- Indirect Water Heating Recovery Time {hr}
IndirectHeatPrimarySetpoint,  !- Source Side Flow Control Mode
,                        !- Indirect Alternate Setpoint Temperature Schedule Name
General;                 !- End-Use Subcategory

Water system energy results:

Model1

  • Baseline : 13.21
  • Desuperheater : 6.07

Model2

  • Baseline : 11.09
  • Desuperheater : 119.2

I looked into the reports of Model2, and made some plots:

image description

the “DESUPERHEATER:Water Heater Heating Energy J” and “WATER HEATER:Water Heater Source Side Heat Transfer Energy J” were surprisingly not reported as the same. They look like this (0601-0607).

image description

The results are so weird. I attached my models below, they're sitting in the google drive link below ready for you to review. If anyone knows where it went wrong, please let me know. Thanks very much!!

Folder Link

Models and results folder

Unreasonable results for water heating desuperheater

Previously, I modeled a water system with desuperheater in Model 1 which gave happy results (about half water heating energy saving). Now I need to integrate this technology into another model( Model2) with exactly the same approach. However, the Model 2 results showed about 10X more water heating energy usage than its baseline, which is unreasonable.unreasonable. I am using E+ v9.1.0.

The approach I used to model desuperheater is quite straightforward, I'd like to elaborate:

  • I created a constant temperature schedule of 55C (setpoint is 52.6667C) as desuperheater setpoint, which requires a little bit higher than water heater setpoint to be activated.

.

Schedule:Constant,
  desuperheaterStp,        !- Name
  Temperature,             !- Schedule Type Limits Name
  55;                      !- Hourly Value
  • I used Coil:WaterHeating:Desuperheater object, the snippet was like

.

Coil:WaterHeating:Desuperheater,
   Desuperheater,             !- Name
   ,                          !- Availability Schedule Name
   desuperheaterStp,          !- Setpoint Temperature Schedule Name
   2,                         !- Dead Band Temperature Difference {deltaC}
   0.25,                      !- Rated Heat Reclaim Recovery Efficiency
   50,                        !- Rated Inlet Water Temperature {C}
   35,                        !- Rated Outdoor Air Temperature {C}
   60,                        !- Maximum Inlet Water Temperature for Heat Reclaim {C}
   ,                          !- Heat Reclaim Efficiency Function of Temperature Curve Name
   DesuperheaterIn,           !- Water Inlet Node Name
   DesuperheaterOut,          !- Water Outlet Node Name
   WaterHeater:Mixed,         !- Tank Object Type
   water heater,              !- Tank Name
   Coil:Cooling:DX:SingleSpeed,  !- Heating Source Object Type
   central ac clg coil,       !- Heating Source Name
   0.001,                     !- Water Flow Rate {m3/s}
   ,                          !- Water Pump Power {W}
   0.2;                       !- Fraction of Pump Heat to Water
  • And finally I got these two water nodes connected with WaterHeater:Mixed

.

WaterHeater:Mixed,
res wh,                  !- Name
0.136274824222915,       !- Tank Volume {m3}
WH Setpoint Temp,        !- Setpoint Temperature Schedule Name
2,                       !- Deadband Temperature Difference {deltaC}
99,                      !- Maximum Temperature Limit {C}
Cycle,                   !- Heater Control Type
5500.06477392209,        !- Heater Maximum Capacity {W}
0,                       !- Heater Minimum Capacity {W}
0,                       !- Heater Ignition Minimum Flow Rate {m3/s}
0,                       !- Heater Ignition Delay {s}
Electricity,             !- Heater Fuel Type
0.8,                     !- Heater Thermal Efficiency
,                        !- Part Load Factor Curve Name
0,                       !- Off Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- Off Cycle Parasitic Fuel Type
0,                       !- Off Cycle Parasitic Heat Fraction to Tank
0,                       !- On Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- On Cycle Parasitic Fuel Type
0,                       !- On Cycle Parasitic Heat Fraction to Tank
Outdoors,                !- Ambient Temperature Indicator
,                        !- Ambient Temperature Schedule Name
,                        !- Ambient Temperature Zone Name
Model Outdoor Air Node,  !- Ambient Temperature Outdoor Air Node Name
0.704227539803499,       !- Off Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- Off Cycle Loss Fraction to Zone
0.704227539803499,       !- On Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- On Cycle Loss Fraction to Zone
,                        !- Peak Use Flow Rate {m3/s}
,                        !- Use Flow Rate Fraction Schedule Name
,                        !- Cold Water Supply Temperature Schedule Name
Node 13,                 !- Use Side Inlet Node Name
Node 14,                 !- Use Side Outlet Node Name
1,                       !- Use Side Effectiveness
DesuperheaterOut,        !- Source Side Inlet Node Name
DesuperheaterIn,         !- Source Side Outlet Node Name
1,                       !- Source Side Effectiveness
Autosize,                !- Use Side Design Flow Rate {m3/s}
Autosize,                !- Source Side Design Flow Rate {m3/s}
1.5,                     !- Indirect Water Heating Recovery Time {hr}
IndirectHeatPrimarySetpoint,  !- Source Side Flow Control Mode
,                        !- Indirect Alternate Setpoint Temperature Schedule Name
General;                 !- End-Use Subcategory

Water system energy results:

Model1

  • Baseline : 13.21
  • Desuperheater : 6.07

Model2

  • Baseline : 11.09
  • Desuperheater : 119.2

I looked into the reports of Model2, and made some plots:

image description

the “DESUPERHEATER:Water Heater Heating Energy J” and “WATER HEATER:Water Heater Source Side Heat Transfer Energy J” were surprisingly not reported as the same. They look like this (0601-0607).

image description

The results are so weird. I attached my models below, they're sitting in the google drive link below ready to review. If anyone knows where it went wrong, please let me know. Thanks very much!!

Folder Link

Models and results folder

Unreasonable results for water heating desuperheater

Previously, I modeled a water system with desuperheater in Model 1 which gave happy results (about half water heating energy saving). Now I need to integrate this technology into another model( Model2) with exactly the same approach. However, the Model 2 results showed about 10X more water heating energy usage than its baseline, which is unreasonable. I am using E+ v9.1.0.

The approach I used to model desuperheater is quite straightforward, I'd like to elaborate:

  • I created a constant temperature schedule of 55C (setpoint is 52.6667C) as desuperheater setpoint, which requires a little bit higher than water heater setpoint to be activated.

.

Schedule:Constant,
  desuperheaterStp,        !- Name
  Temperature,             !- Schedule Type Limits Name
  55;                      !- Hourly Value
  • I used Coil:WaterHeating:Desuperheater object, the snippet was like

.

Coil:WaterHeating:Desuperheater,
   Desuperheater,             !- Name
   ,                          !- Availability Schedule Name
   desuperheaterStp,          !- Setpoint Temperature Schedule Name
   2,                         !- Dead Band Temperature Difference {deltaC}
   0.25,                      !- Rated Heat Reclaim Recovery Efficiency
   50,                        !- Rated Inlet Water Temperature {C}
   35,                        !- Rated Outdoor Air Temperature {C}
   60,                        !- Maximum Inlet Water Temperature for Heat Reclaim {C}
   ,                          !- Heat Reclaim Efficiency Function of Temperature Curve Name
   DesuperheaterIn,           !- Water Inlet Node Name
   DesuperheaterOut,          !- Water Outlet Node Name
   WaterHeater:Mixed,         !- Tank Object Type
   water heater,              !- Tank Name
   Coil:Cooling:DX:SingleSpeed,  !- Heating Source Object Type
   central ac clg coil,       !- Heating Source Name
   0.001,                     !- Water Flow Rate {m3/s}
   ,                          !- Water Pump Power {W}
   0.2;                       !- Fraction of Pump Heat to Water
  • And finally I got these two water nodes connected with WaterHeater:Mixed

.

WaterHeater:Mixed,
res wh,                  !- Name
0.136274824222915,       !- Tank Volume {m3}
WH Setpoint Temp,        !- Setpoint Temperature Schedule Name
2,                       !- Deadband Temperature Difference {deltaC}
99,                      !- Maximum Temperature Limit {C}
Cycle,                   !- Heater Control Type
5500.06477392209,        !- Heater Maximum Capacity {W}
0,                       !- Heater Minimum Capacity {W}
0,                       !- Heater Ignition Minimum Flow Rate {m3/s}
0,                       !- Heater Ignition Delay {s}
Electricity,             !- Heater Fuel Type
0.8,                     !- Heater Thermal Efficiency
,                        !- Part Load Factor Curve Name
0,                       !- Off Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- Off Cycle Parasitic Fuel Type
0,                       !- Off Cycle Parasitic Heat Fraction to Tank
0,                       !- On Cycle Parasitic Fuel Consumption Rate {W}
Electricity,             !- On Cycle Parasitic Fuel Type
0,                       !- On Cycle Parasitic Heat Fraction to Tank
Outdoors,                !- Ambient Temperature Indicator
,                        !- Ambient Temperature Schedule Name
,                        !- Ambient Temperature Zone Name
Model Outdoor Air Node,  !- Ambient Temperature Outdoor Air Node Name
0.704227539803499,       !- Off Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- Off Cycle Loss Fraction to Zone
0.704227539803499,       !- On Cycle Loss Coefficient to Ambient Temperature {W/K}
1,                       !- On Cycle Loss Fraction to Zone
,                        !- Peak Use Flow Rate {m3/s}
,                        !- Use Flow Rate Fraction Schedule Name
,                        !- Cold Water Supply Temperature Schedule Name
Node 13,                 !- Use Side Inlet Node Name
Node 14,                 !- Use Side Outlet Node Name
1,                       !- Use Side Effectiveness
DesuperheaterOut,        !- Source Side Inlet Node Name
DesuperheaterIn,         !- Source Side Outlet Node Name
1,                       !- Source Side Effectiveness
Autosize,                !- Use Side Design Flow Rate {m3/s}
Autosize,                !- Source Side Design Flow Rate {m3/s}
1.5,                     !- Indirect Water Heating Recovery Time {hr}
IndirectHeatPrimarySetpoint,  !- Source Side Flow Control Mode
,                        !- Indirect Alternate Setpoint Temperature Schedule Name
General;                 !- End-Use Subcategory

Water system energy results:

Model1

  • Baseline : 13.21
  • Desuperheater : 6.07

Model2

  • Baseline : 11.09
  • Desuperheater : 119.2

I looked into the reports of Model2, and made some plots:

image description

the “DESUPERHEATER:Water Heater Heating Energy J” and “WATER HEATER:Water Heater Source Side Heat Transfer Energy J” were surprisingly not reported as the same. They look like this (0601-0607).

image description

The results are so weird. I attached my models below, they're sitting in the google drive link below ready to review. If anyone knows where it went wrong, please let me know. Thanks very much!!

Folder Link

Models and results folder