Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I have considered placing actuator as below; EnergyManagementSystem:Sensor, Occu_Schedule, !- Name 2864, !- Output:Variable or Output:Meter Index Key Name Occupancy Schedule Schedule Value; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I have considered placing actuator and sensors as below; EnergyManagementSystem:Sensor, Occu_Schedule, !- Name 2864, !- Output:Variable or Output:Meter Index Key Name Occupancy Schedule Schedule Value; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I have considered placing actuator and sensors as below; below;

EnergyManagementSystem:Sensor,
 Occu_Schedule, !- Name
 2864,           !- Output:Variable or Output:Meter Index Key Name   Occupancy Schedule
 Schedule Value;  !- Output:Variable or Output:Meter Name

Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I believe I can study the change of supply air temperature by changing the room set-point temperature, Agree? Not sure about Chilled water temperature. I have considered placing actuator and sensors as below;

EnergyManagementSystem:Sensor,
Occu_Schedule, !- Name
2864,           !- Output:Variable or Output:Meter Index Key Name   Occupancy Schedule
Schedule Value;  !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I believe I can study the change of supply air temperature by changing the room set-point temperature, Agree? Not sure about Chilled water temperature. I have considered placing actuator and sensors as below;

EnergyManagementSystem:Sensor,
Occu_Schedule, !- Name
2864,           !- Output:Variable or Output:Meter Index Key Name   Occupancy Schedule
Schedule Value;  !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Results are: Results are

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I believe I can study the change of supply air temperature by changing the room set-point temperature, Agree? Not sure about Chilled water temperature. I have considered placing actuator and sensors as below;

EnergyManagementSystem:Sensor,
Occu_Schedule, !- Name
2864,           !- Output:Variable or Output:Meter Index Key Name   Occupancy Schedule
Schedule Value;  !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Results are: Results are

Flow rate vs temp plots are:

image description

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I believe I can study the change of supply air temperature by changing the room set-point temperature, Agree? Not sure about Chilled water temperature. I have considered placing actuator and sensors as below;

EnergyManagementSystem:Sensor,
Occu_Schedule, !- Name
2864,           !- Output:Variable or Output:Meter Index Key Name   Occupancy Schedule
Schedule Value;  !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Results are: Results are

Flow rate vs temp plots are:

image description

Chilled water and Supply air temperatures parametric study

I would like to perform a parametric study of chilled water and supply air temperatures but unable to find them in my IDF. The idea is to put EMS sensors and actuators to change these two temperatures to find their relationship with energy consumption. I have used Chiller:Electric:EIR as my chiller model, do I have to consider Condenser outlet temperature as the chilled water supply temperature? Also, How can I set supply air temperature to my own values? I believe I can study the change of supply air temperature by changing the room set-point temperature, Agree? Not sure about Chilled water temperature. I have considered placing actuator and sensors as below;

EnergyManagementSystem:Sensor,
Occu_Schedule, !- Name
2864,           !- Output:Variable or Output:Meter Index Key Name   Occupancy Schedule
Schedule Value;  !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Actuator,
Chiller_set_point, ! Name
CHILLER CONDENSER OUTLET NODE, ! Component Name
System Node Setpoint, ! Component Type
Temperature Setpoint; ! Control Variable

EnergyManagementSystem:ProgramCallingManager,
Temp_69,  !- Name
EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
Temp_Control69;     !- Program Name 8

EnergyManagementSystem:Program,
Temp_Control69,     !- Name
IF Occu_Schedule > 0, 
SET Chiller_set_point = 6,               
ELSE,
SET Chiller_set_point = 3,
ENDIF;

But when I plot Condenser outlet by using Output:Variable,*,Chiller Condenser Outlet Temperature,hourly; !- HVAC Average [C], it always give me different results then I assign. Any ideas?

Results are: Results are

Flow rate vs temp plots are:

image description