We are modelling a core & shell office building for LEEDv4 with multiple shells in e-Quest.
1) The proposed model(design) has floor level AHU’s of type ‘PIU’ with terminal Fan powered boxes at the perimeter zones and terminal VAV boxes at interior core zones. Perimeter zones have hot water reheat. The reheat deltaT at core zones was manually set to zero because the core zones require only cooling. 2) The baseline model has floor level AHU’s of type ‘Variable Air Volume’ with reheat temperature given at the system level (not possible to give a reheat temperature at zone level). Results show that the baseline heating is way worse than the proposed( by 40%) which doesn’t seem right. Core zones in the baseline model have a heating demand (confirmed through SV-A summary report) which may be the reason for the increased heating energy use
Please advise if the system types selected are the right one’s for the Appendix G System 7 baseline model. And if it is right to have assigned a reheat at the system level which makes assigns a reheat for the core zones automatically in the baseline model